In summary: ThanksIn summary, the problem involves a heater and three jacketed reactors being heated by water from the heater. The heater size needs to be determined to handle all three reactors at full load, and the reactors can be treated as heat exchangers. The appropriate pipe sizes for the main water supply and return lines should be determined by calculating the pressure losses in each section, including the heater, and using that to determine the pump head and flow rate.
  • #1
theone!
2
0
The problem involves a a heater and three jacketed reactors. The reactors are heated by water supplied by the heater.

Determine the heater size(in kW) required for this service if the heater is to be
sized so that it is large enough to handle all three reactors when they operate at full load


do I just treat the jacketed vessels like heat exchangers;

##\dot Q=U A_s \Delta T## with ##\frac{1}{U A_s}=\frac{1}{h_i A_i} + \frac{ln(D_o/D_i)}{2 \pi k L} + \frac{1}{h_o A_o}##

and then multiply ##\dot Q## by 3 to get the heater size?

Determine the appropriate pipe sizes for the main water supply and return lines.
the system. There should be two different pipe sizes: one for the main supply/return line and another for the lines connecting the reactors to the main supply lines.

is this just an application of

## \frac{p_1}{y} + \frac{V_1}{2g} + z_1 = \frac{p_2}{γ} + \frac{V_2}{2g} + z_2 + \frac{V_2}{2g} [ \frac{fL}{D} + K ]##

and I should solve for the diameter?
 

Attachments

  • Untitled.png
    Untitled.png
    6.6 KB · Views: 403
  • Untitled2.png
    Untitled2.png
    31.6 KB · Views: 441
Physics news on Phys.org
  • #2
The device I'm using to type this on doesn't allow me to see your equations correctly so I haven't been able to check those but..

The problem statement appears to gives you enough info to work out the power consumed by each reactor... You have the flow rate and the temperature drop and can look up the specific heat capacity of water. Multiply by three and you have the power that the heater would need to deliver.

I can't help with the pipe sizing sorry.
 
  • Like
Likes theone!
  • #3
CWatters said:
The device I'm using to type this on doesn't allow me to see your equations correctly so I haven't been able to check those but..

The problem statement appears to gives you enough info to work out the power consumed by each reactor... You have the flow rate and the temperature drop and can look up the specific heat capacity of water. Multiply by three and you have the power that the heater would need to deliver.

I can't help with the pipe sizing sorry.

thanks!

about the pipe diameters, I think I have the equation to get them but it looks like I need the flow rate of the water. (The only flow rate info I'm given is the max allowable flow rate of 50 USGPM through the jacket)

Another question of the project asks me to "determine the required pump head and flow rate for your design"

So I was wondering if I should pick some pump, plot the system curve and pump curve, get the operating pump head and flow rate at the intersection, and then use that flow rate to get the diameters?
 
  • #4
I never studied this but...

The problem statement describes the pipework. It looks like there is a main supply and return which will carry 3 x 50usgpm plus branch pipes to each reactor that will carry 1 x 50usgpm each.

Its not my field but I imagine you need to make a drawing and mark it up with the flow rates and calculate the pressure losses in each section. Calculate the pressure loss around the loop including that in the heater (gives you the pump head required). That and the flow rate should allow you to work out the pump power? I think!
 
  • #5
theone! said:
The problem involves a a heater and three jacketed reactors. The reactors are heated by water supplied by the heater.

Determine the heater size(in kW) required for this service if the heater is to be
sized so that it is large enough to handle all three reactors when they operate at full load


do I just treat the jacketed vessels like heat exchangers;

##\dot Q=U A_s \Delta T## with ##\frac{1}{U A_s}=\frac{1}{h_i A_i} + \frac{ln(D_o/D_i)}{2 \pi k L} + \frac{1}{h_o A_o}##

and then multiply ##\dot Q## by 3 to get the heater size?

Determine the appropriate pipe sizes for the main water supply and return lines.
the system. There should be two different pipe sizes: one for the main supply/return line and another for the lines connecting the reactors to the main supply lines.

is this just an application of

## \frac{p_1}{y} + \frac{V_1}{2g} + z_1 = \frac{p_2}{γ} + \frac{V_2}{2g} + z_2 + \frac{V_2}{2g} [ \frac{fL}{D} + K ]##

and I should solve for the diameter?
Hey, so did you end up solving the problem with the P&ID? Is there any chance you can share it?
 

Related to Help with a problem to design a vessel

1. What is the purpose of the vessel design?

The purpose of the vessel design is to determine the optimal shape, size, and materials for a vessel that will meet the requirements of its intended use.

2. What factors should be considered when designing a vessel?

The design of a vessel should take into account factors such as the type of material needed for the vessel, the size and shape of the vessel, the intended use of the vessel, and any potential environmental conditions that may affect the vessel's performance.

3. How do you determine the appropriate materials for a vessel design?

The materials for a vessel design should be chosen based on their strength, durability, and compatibility with the vessel's intended use. It is important to consider factors such as weight, corrosion resistance, and cost when selecting materials.

4. What methods can be used to test the effectiveness of a vessel design?

There are several methods for testing the effectiveness of a vessel design, including computer simulations, scale models, and physical testing. These methods can help to identify potential flaws or weaknesses in the design and allow for adjustments to be made before the vessel is built.

5. How can the design of a vessel be optimized for efficiency?

To optimize the efficiency of a vessel, it is important to consider factors such as hydrodynamics, weight distribution, and energy consumption. Advanced design techniques, such as computational fluid dynamics, can be used to analyze and improve the vessel's performance in these areas.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
2
Replies
45
Views
7K
  • Mechanical Engineering
Replies
15
Views
1K
  • Sci-Fi Writing and World Building
2
Replies
52
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
3K
  • Mechanical Engineering
Replies
2
Views
3K
  • Mechanical Engineering
Replies
1
Views
2K
Replies
5
Views
2K
  • Introductory Physics Homework Help
Replies
11
Views
25K
Back
Top