Motor fan pulley sizing for HVAC

In summary, you designed a motor fan system with a 7" driver pulley and a 10" curved fan. The system draws 13.24 kW at the specified rpm. If the fan draws more than 13.24 kW at the specified rpm, something is wrong with the fan. You need to speak to the consultant to make sure the calculations were done correctly.
  • #1
Muhammad Hasan
6
0
Hi Everyone!
I designed a motor fan system pulley system. So, basically, the motor is of 15 kw with a driver pulley of 7" dia. And through a v-belt I attached a backward curved fan with a 10" dia pulley on the shaft. My fan shaft power is 13.24 kw. This selection was given to me by the software.
Now the problem was that when I assembled this all, my current was coming out to be 48 amps. So, I had to reduce motor pulley size to 6" and amperage reduced to 24 amps. Still, my motor rating was at 22.3 amps. And when I reduced the dia, the rpm changed and hence the flow rate changed.
My motor is 15 kw 3 phase 380v motor. ABB 15 kw motor.
 
Engineering news on Phys.org
  • #2
If the fan draws 13.24kW at Frpm and the motor is rated at 15kw at Mrpm then the pulley ratio must be selected to convert Mrpm to Frpm.

If you set it up like that and it still draws too much current then something is wrong with the fan. It's drawing more than 13kw at the specified rpm.

You don't mention the rated rpm for either so I can't check the ratio.
 
  • #3
CWatters said:
If the fan draws 13.24kW at Frpm and the motor is rated at 15kw at Mrpm then the pulley ratio must be selected to convert Mrpm to Frpm.

If you set it up like that and it still draws too much current then something is wrong with the fan. It's drawing more than 13kw at the specified rpm.

You don't mention the rated rpm for either so I can't check the ratio.
Rated Motor RPM is 1466 and Fan RPM is 1014.
you mean i should change the fan??
 
  • #4
Muhammad Hasan said:
My fan shaft power is 13.24 kw. This selection was given to me by the software.
Are you sure? Your motor is telling you the shaft power was 30 kW. What did you tell the selection software? What is the system configuration?

One common cause of higher than expected shaft power is lower than expected static pressure...
 
  • Like
Likes Asymptotic
  • #5
russ_watters said:
Are you sure? Your motor is telling you the shaft power was 30 kW. What did you tell the selection software? What is the system configuration?

One common cause of higher than expected shaft power is lower than expected static pressure...
what do you mean by 30 kw?
upload_2018-11-14_19-27-43.png


This is the selection that the software gave me. I calculated the pulley diameters using the blower speed RPM and Motor RPM(1440).
 

Attachments

  • upload_2018-11-14_19-27-43.png
    upload_2018-11-14_19-27-43.png
    16.6 KB · Views: 1,602
  • #6
Muhammad Hasan said:
what do you mean by 30 kw?
48 amps at 380V and 90% efficiency is about 30 kW.
View attachment 233987

This is the selection that the software gave me. I calculated the pulley diameters using the blower speed RPM and Motor RPM(1440).
But where did you get the input data you told the selection software? Where did you get the airflow and static pressure?
 
  • #7
russ_watters said:
48 amps at 380V and 90% efficiency is about 30 kW.

But where did you get the input data you told the selection software? Where did you get the airflow and static pressure?
A consultant gave me!
 
  • #8
Muhammad Hasan said:
A consultant gave me!
just tell me something, i calculated sizes using simple RPM ratios. Is that calculation legit?? Or there some other process to calculate pulley dias?
 
  • #9
Muhammad Hasan said:
A consultant gave me!
...Then it would be a good idea to go back to the consultant and make sure it was sized and selected properly. And/or if you can measure the pressure and airflow, check to make sure they match the design.

[edit] Also make sure it is installed properly. I've heard of contractors installing a fan and testing it before attaching the ductwork. You can't do that.
 
  • Like
Likes Asymptotic, jrmichler and CWatters
  • #10
Muhammad Hasan said:
just tell me something, i calculated sizes using simple RPM ratios. Is that calculation legit??
Yes, your pulley sizing procedure was correct.
 
  • #11
+1

Muhammad Hasan said:
Rated Motor RPM is 1466 and Fan RPM is 1014.

That's a ratio of 1466/1014 = 1.45:1

10"/7" is a ratio of 1.43:1 which is close enough.

So yes the original pulley ratio should have worked fine.

I agree you need to speak to the consultant and ask why his fan appears to be drawing too much power. Perhaps a factor of 2 missing somewhere in his calculations?
 
  • Like
Likes russ_watters
  • #12
I might be wrong but I think have found part of the problem...

Fan.png


If the OUTPUT of the fan is 13.24kW and the efficiency is 65.8% then the INPUT power to the fan is..

= 13.24 * 100/65.8
= 20kW

That still does not explain why it is drawing 30kW but check with the consultant.

EDIT: What is the motor efficiency with a 33% overload (5kW/15kW=33%)? If the efficiency drops a lot then that might account for some of the other 10kW ?
 

Attachments

  • Fan.png
    Fan.png
    15.9 KB · Views: 1,288
Last edited:
  • #13
See post #9.

I believe that post #12 is incorrect - the 'software' picked a 15 KW motor - 'Efficiency' is accounted for in the 13.24KW. A rough calc of an ideal blower supports that notion.

As an experiment, you can restrict the inlet or outlet - you'll almost certainly see the current drop. You can determine the pressure difference across your fan with a piece of clear tubing and some water (hillbilly U-tube manometer). Those measurements and a fan curve (available from the manufacturer, if you don't already have one) will set you free. You are almost certainly (as Russ suggests) overflowing your blower.
 
  • Like
Likes russ_watters and jrmichler
  • #14
Their fan curves are different from what I'm used to seeing:
upload_2018-11-14_13-42-36.png

If I'm correctly interpreting the fan curve, the fan shaft power will be 30 Kw at 1000 shaft RPM at about 45,000 m^3 per hour. That flow rate is larger than the fan is designed for. Also, the fan catalog specifies a 95% efficiency when designing belt drives, and also a 1.1 safety factor on the motor size.

Is the fan connected to the completed ductwork? Also @Dullard is correct about restricting inlet or outlet. And the clear tubing manometer he suggests, while it may be cheap appearing, is completely accurate. It is accurate enough to be used as a calibration standard for mechanical gauges.
 

Attachments

  • upload_2018-11-14_13-42-36.png
    upload_2018-11-14_13-42-36.png
    54.3 KB · Views: 1,183
  • Like
Likes russ_watters
  • #15
That curve shows what the data table claims:
approx 13 KW @ .95Kpa / 27K m3/Hr
 
  • Like
Likes russ_watters
  • #16
CWatters said:
I might be wrong but I think have found part of the problem...

View attachment 234007

If the OUTPUT of the fan is 13.24kW and the efficiency is 65.8% then the INPUT power to the fan is..

= 13.24 * 100/65.8
= 20kW
I don't know about their terminology, but a quick calc tells me the air power is 7.2 kW. 13.2 looks like motor drive shaft power.
 
  • #17
Yes I've just done the same and got 7.4kW for the air power. That gives a fan efficiency of 100 * 7.4/13.2 = 56%. So not sure how they get 65.9%.
 
  • #18
I get what you all are saying but, what I don't understand is that why is the software selecting that Fan and Motor combination?

Furthermore, I am using TICA AHU software for designing! Any suggestion on a better software for designing AHUs?

I have also attached the Fan curve and selection done by the software! please have a look and help me out.
Thanks Everyone.
 

Attachments

  • AHU-01_FanCurveReport.pdf
    405.4 KB · Views: 239
  • AHU-01_TechnicalReport.pdf
    474.6 KB · Views: 325
  • #19
Muhammad Hasan said:
I get what you all are saying but, what I don't understand is that why is the software selecting that Fan and Motor combination?
The design engineer enters the required airflow, static pressure, altitude, and various desired configuration elements and the software lists fans and motors that will meet the specified requirements, and from that list the design engineer picks one.
 
  • #20
Perhaps one of the other contributors to this thread could comment on the data in the filter section in the TICA report. The air velocity in that section is listed as 0.15m/s where as the velocity out of the fan is 18m/s. Presumably the filter is much larger in diameter than the duct... From the flow rate and volume I calculated the duct has an area of about 0.4sqm (70cm Diameter). To drop the velocity to 0.15m/s wouldn't the filter have to be 40sqm? Is this actually lots of small filters around the building?
 
  • #21
I'm a bit puzzled by the "FanCurveReport." The 'design point' appears to require 925 RPM - I'm not sure where 1014 came from. The fan/system curve intercept will occur high/right of the plotted design point. The power gets high out there, based on the 'blank' curve in post # 14.
 
  • Like
Likes CWatters

Related to Motor fan pulley sizing for HVAC

1. What is the purpose of a motor fan pulley in HVAC systems?

A motor fan pulley is a critical component in HVAC systems that helps to regulate the speed and airflow of the fan. It is responsible for transferring power from the motor to the fan and controls the rotation speed of the fan. The size of the motor fan pulley directly affects the speed and efficiency of the fan, making it an important factor in HVAC design and installation.

2. How do you determine the correct size for a motor fan pulley in HVAC systems?

The size of the motor fan pulley is determined by the required airflow and the speed of the fan. This calculation is based on the fan's CFM (cubic feet per minute) and the motor's RPM (revolutions per minute). The correct size is then selected based on the relationship between these two factors, as well as the size and capacity of the motor and fan.

3. What are the consequences of using an incorrect size for a motor fan pulley in HVAC systems?

If the motor fan pulley is too small, it can result in the fan not being able to generate enough airflow, leading to poor air circulation and decreased efficiency. On the other hand, if the pulley is too large, the fan will spin too fast, resulting in excessive noise, increased energy consumption, and potential damage to the motor.

4. Can a motor fan pulley be adjusted or changed after installation?

Yes, a motor fan pulley can be adjusted or changed after installation. However, this should only be done by a trained professional with an understanding of the impact on the overall HVAC system. Changing the size of the motor fan pulley can affect the performance and efficiency of the fan, so it should be done carefully and with proper calculations.

5. Are there any other factors to consider when sizing a motor fan pulley for HVAC systems?

In addition to CFM, RPM, and motor and fan size, there are other factors that may affect the sizing of a motor fan pulley. These include the type and size of the ductwork, the layout of the HVAC system, and the specific requirements of the building or space being cooled or heated. It is important to take all of these factors into consideration when determining the correct size for a motor fan pulley in HVAC systems.

Similar threads

  • Mechanical Engineering
Replies
13
Views
2K
  • Mechanical Engineering
2
Replies
63
Views
5K
Replies
3
Views
3K
  • Mechanical Engineering
Replies
14
Views
2K
  • Mechanical Engineering
Replies
8
Views
2K
Replies
3
Views
4K
  • Mechanical Engineering
Replies
4
Views
2K
Replies
2
Views
1K
Replies
5
Views
1K
Replies
1
Views
4K
Back
Top