Japan Earthquake: Nuclear Plants at Fukushima Daiichi
In summary: RCIC consists of a series of pumps, valves, and manifolds that allow coolant to be circulated around the reactor pressure vessel in the event of a loss of the main feedwater supply.In summary, the earthquake and tsunami may have caused a loss of coolant at the Fukushima Daiichi NPP, which could lead to a meltdown. The system for cooling the reactor core is designed to kick in in the event of a loss of feedwater, and fortunately this appears not to have happened yet.
  • #10,362
Luca Bevil said:
They have to keep cooling the reactors. That should account for much of the remaining processing tons.
The 250,000 figure was until the end of the fiscal year, i.e. 31 March 2012, which is another 9 months. 500 t/d (for cooling) * 270 d = 135,000 t. That's almost exactly the difference between the 250,000 t total and the 121,000 t reported in the buildings and in storage tanks at the moment.
  • #10,363
tsutsuji said:
http://www.yomiuri.co.jp/science/news/20110629-OYT1T00850.htm and http://www.tepco.co.jp/nu/fukushima-np/images/handouts_110629_02-j.pdf : The water treatment facility was stopped at 2:53 PM after an alarm signalling a leak at the site bunker building (1) rang. It had been also stopped for flushing and adsorption tower replacement between 10:45 AM and 2:13 PM. The reason why the alarm rang is under investigation.
(1) the orange box on http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110627_01-e.pdf
tsutsuji said:
http://www.asahi.com/national/jiji/JJT201106290077.html : The facility was started again at 9:15 PM.
http://mainichi.jp/select/weathernews/news/20110630dde001040018000c.html A first try to start the facility had been made at 6:45 PM, but a spill occurred at the Areva facility as a result of a pump failing to start because it was set on "manual" instead of "automatic". The facility had to be stopped after 9 minutes and it took 2 hours and 20 minutes until it was started again. The spilled water did not leak outside of the building.
  • #10,364
This map of unit 4 sfp was cropped from a recently posted report, it appears to be based on knowledge I have not previously seen published. I wonder if the figures might signify something to somebody.
  • #10,365
tsutsuji said:
http://www.chunichi.co.jp/s/article/2011062990203609.html : On 30 June, Tepco plans to begin transferring the accumulated water from unit 6 into the megafloat barge.
http://www.jiji.com/jc/c?g=soc_30&k=2011063000601 mentions water from unit 5 too, while saying that most of the transfer concerns ground water that seeped into unit 6's basement. The amount is 8000 tons, and the transfer will take 3 or 4 months. The radiation is 0.034 Bq/cm³ for each of the 134Cs and 137Cs contaminants, as a result of a zeolite or other purification process. The megafloat starts being used because the temporary storage tanks which had been used until now have become nearly full.
It is the first time that I hear about this "zeolite or other" purification process in the context of unit 5 and unit 6's accumulated water problem.
http://www.tepco.co.jp/en/press/corp-com/release/11062911-e.html a press release about a report to NISA concerning the amounts of contaminated water treated so far at the Kurion-Areva facility, and the processing plans until the end of September.
  • #10,366
Assuming the diagram is aligned like a map, with North at the top, the top center would be where the gate to the reactor pit is. Does anybody know where the skimmer surge tank is located on that diagram?
I am counting 1330 fuel assemblies giving off some amount of decay heat. One set of fuel elements for units 2-5 is 548. The 10 rows of 2 columns of 3x10 assemblies on the bottom left are 600 of them.
The dark red ones must the the assemblies unloaded after the shutdown on 29 Nov 2010, since these would have decayed the least and would still be giving off most of the heat.
Some of the dark blue ones (same as pool diagram background colour) must be holding the ~200 fresh fuel assemblies that are also supposed to be in the #4 SFP, originally due to be loaded this summer when the shroud replacement was supposed to be finished.
All the blue fields in the 10 3x10 clusters down the middle add up to 200. So these might be fresh ones. That also makes sense because these fuel rods were the next ones due to be loaded into the core, so in the middle they're already aligned with the open reactor pit.
  • #10,367
0.034 Bq/cm³ is 34 Bq/l or a total of 68 Bq/l for all cesium. I believe the Japanese legal limit for cesium in drinking water for adults is 200 Bq/l, to put this in perspective.
  • #10,368
tonio said:
- Assessment of the present ground water table (and thus flow speed) is probably unreliable as it is disturbed by these extractions and in a phase of adjustment (i.e. increasing flow speed), probably even if the extractions were halted after the tsunami.
As far as I understand they have so far emptied the unit #5 and #6 sub-drain pits once but have not done it for the units #1 - #4.
The total amount for #5 and #6 was 950 m3 + 373 m3 = 1,323 m3.
http://www.nisa.meti.go.jp/english/press/2011/06/en20110630-1-2.pdf
(page 12 and 13)
Also the groundwater level is probably higher near #5 and #6 because TEPCO had to divert water near #5 and #6 before crisis:
Before the crisis, streams beneath reactors No. 5 and 6 were pumped to divert water, a process that hasn't been conducted since the quake.
http://online.wsj.com/article/SB10001424052748703922504576273930625967622.html
So based on this information I would guess the situation could be quite good actually. The sub-drain water underneath #5 and #6 is low-level contaminated so even if they have more water in the sub-drain pits there it's less contaminated.
The sub-drain water underneath #1 - #4 is more heavily contaminated but there is less water there. I think they must have some kind of mechanism (automatic or manual) to observe the level of water in the sub-drain pits - and because they have not yet emptied the #1 - #4 pits it probably means that those pits are not full yet.
If one calculates that the max capacity of sub-drain pits for a single unit is somewhere near 1,000 tons (based on the 950 tons emptied from the unit #5), there would be max 4,000 tons of contaminated sub-drain water to be emptied from the units #1 - #4.
The situation gets worse if lots of contaminated water from turbine/reactor buildings has been able to go below sub-drain systems. Nobody knows if the sub-drain systems are still functioning as they are supposed to. One could also ask if the sub-drain systems are designed to hold radioactive water. Why are the cesium levels decreasing in the #1 - #4 sub-drain pits? Where has all that cesium gone?
Some clean water from the mountains or clean rainwater could dilute with the contaminated sub-drain water and make the cesium levels go down. But in the case of the #1 - #4 units I think there has been so much contamination at some point that it would be very odd to see the cesium levels to go to N.D. = not detectable?
  • #10,369
The water levels in unit 1 reactor building basement over a month are provided on
http://www.nisa.meti.go.jp/english/press/2011/06/en20110611-1-5.pdf (28 May -10 June)
http://www.nisa.meti.go.jp/english/press/2011/06/en20110629-1-4.pdf (8-28 June)
Do we have a clear idea why this level is finally stabilizing with oscillations between OP 4300 mm and OP 4600 mm ?
Is this a result of a balance between water leaking in and leaking out ?
Tepco doesn't seem to have plans to process water from unit 1 if you judge by the absence of a hose linking unit 1 to the Kurion-Areva facility on the diagram page 3 of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110627_01-e.pdf
Page 3 of http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110629e13.pdf the 80 m³ mentioned for unit 1 as "change from last report" are small in comparison with other units.
Does it mean that 100% of the 3.5 m³/h injected into unit 1 evaporate into the atmosphere or seep into the ground water ?
How can we explain the difference between unit 1 and unit 2 as regards the quantities of water accumulating in the turbine building basements, while the injected amount in the reactor is the same (3.5 m³/h now) ?
Is the leaking water from unit 1 streaming underground into unit 2's turbine building ?
  • #10,370
Both the published videos from the pool have been shot with a camera positioned at top center of the map, so top of the map is most likely south or west. A huge cylindrical object can be seen in the second video from the pool, it's position is in the lower right corner of the map.
http://gyldengrisgaard.dk/fuku_docs/unit4_sfp_map.gif
  • #10,371
I assume so, yes. If you look at the reported reactor water levels, they change very little, if you can believe the readings. It's either in the ground or in the air.
If you look at the temps, the reactors are still easily hot enough to evaporate a decent volume of the water, and the rest just leaks out.
http://www.ianbradshaw.co.uk/multimedia/fukushima/tepco.html
I.
  • #10,372
MadderDoc said:
This map of unit 4 sfp was cropped from a recently posted report ...
Which recently posted report, please? Later on a few posts you refer to 2 videos of SFP4, do you have links for those also, please? The one with the large cylindrical object I have seen, and I thought that was from the first video we were treated to from SFP4. Was there another one previous to that?
  • #10,373
The map is from a DOE report which is attached to the end of this NRC testimony
(the link was posted on the Unit 3 thread recently, however perhaps not here on the big thread):
http://pbadupws.nrc.gov/docs/ML1114/ML11147A075.pdf
Yes there was a previous video, dated April 28th, It shows the area corresponding to the upper right corner of the DOE map:
http://www.tepco.co.jp/en/news/110311/images/110428_1.zip
The second video showing most of the remaining and larger part of the pool, including the cylindrical object, dated May 8th:
http://www.tepco.co.jp/en/news/110311/images/110508_2.zip
  • #10,374
I agree after looking at http://www.youtube.com/watch?v=unvcryGXNv4" (110508). Since the video was probably taken using the "kirin" (giraffe), which is usually parked at the south of unit 4 for easy access to the SFP located at that end of the building, the top of the map most likely is the south side, making the bottom north. The large round object in the bottom right is then at the north west.
The items shown as circles with a cross in them, arranged in their own racks near the camera position (middle top) and near the round object in the chart look like BWR control rods on the video (at 00:32-00:37).
I had not heard of control rods being parked in SFPs, but given how much radiation they are exposed to, it is possible and maybe they are also there as a precaution against criticality. Perhaps the boron becomes saturated with neutrons and needs replacing every now and then, while the steel could become radioactive, hence the underwater storage like the old shroud.
Could the large round object be the skimmer surge tank? The only picture I've seen of its top shows it to be round.
  • #10,375
Those are control blades. Indeed, the boron gets depleted and the steel gets activated.
  • #10,376
That should be the old shroud, I think.
  • #10,377
clancy688 said:
There always is the possibility that TEPCO, NISA and NSC didn't tell the whole truth and the release was significantly bigger than reported.
Hm, they revised the numbers again and at least me didn't notice...
http://www.kantei.go.jp/foreign/kan/topics/201106/pdf/attach_04_2.pdf" of the official reports gives us 840.000 TBq (converted) for the airborne releases of Units 1-3.
But no indication as for which timeframe.
  • #10,378
They note on P3 that they calculate the total fission products released 'during the term of the analysis', which appears to be about 1 week, judging by the time lines on the charts. Presumably that covers the bulk of the emissions.
  • #10,379
A diagram they released as part of the explanation for injecting water into reactor 4 & the storage pit, which I believe is linked to some days ago in this thread, showed a core shroud in the dryer storage pit/pool area, not in the spent fuel pool.
  • #10,380
The daily Kurion-Areva facility trouble :
http://sankei.jp.msn.com/affairs/news/110630/dst11063022440037-n1.htm (and http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110630_05-e.pdf ) : On 30 June the decontamination facility was stopped for flushing between 10:46 AM and 1:35 PM. The facility was restarted but after one hour it had to stop again because of an alarm signalling that gasses are unable to evacuate through the exhaust stack at the Areva facility.
http://www.nikkei.com/news/headline...19481E1E2E2E19A8DE1E2E2E4E0E2E3E39797E0E2E2E3 The facility started again at 6:50 PM (30 June).
The same http://www.nikkei.com/news/headline...19481E1E2E2E19A8DE1E2E2E4E0E2E3E39797E0E2E2E3 also says that the heat exchanger for unit 3's spent fuel pool has started running at 6:33 PM (30 June).
  • #10,381
I noticed the 840,000 TBq estimate at the time, but I don't think I noticed that it was new, I forgot that the previous adjustment was from 370,000 to 770,000 rather than straight to 840,000. Press reports certainly mention 770,000 but I can't actually work out which document had this figure in.
As for timescales, I became very interested in how these sorts of estimates were done, the estimated timing of the largest releases, and the fact that the analysis which showed emissions by each reactor had reactor 2 as the main culprit. I did not have much joy learning more about NISA estimate methodology, but I had much more success with finding detail of how the NSC did their calculations. NSC are the ones who came out with the 630,000 TBq figure in April, at a time that NISA only estimated 370,000 TBq.
The following document, which I have mentioned at least once before in this thread and which is in Japanese, seems to contain a wealth of information about how they estimate contamination, far more than we usually get. Its from an NSC meeting (meeting 31). Computer translation does not do a perfect job of revealing the details in their full glory, but give it a try and you should at least see what I mean. There are a few tables and charts there too which require almost no translation to understand. And the one on the very last page shows a timeline of release magnitude which really helps to get a sense of the picture they have established when collecting data and doing their analysis of what happened.
http://www.nsc.go.jp/anzen/shidai/genan2011/genan031/siryo4-2.pdf
  • #10,382
I still don't understand why there is only 350mm in unit 4 skimmer surge tank, it was always 4500-6500mm and was changing when they were injecting water from concrede pump, but 2 days ago it started decreasing very quick to 350mm now, also they didnt change anything in pipes, look here: http://www3.nhk.or.jp/daily/english/30_03.html
But TEPCO hasn't been as successful with the No.4 reactor's spent fuel pool. A hydrogen explosion in March damaged water pipes that are connected to it. The company is reviewing its installation plan.
Workers entered the 5th floor of the No.4 reactor building on Wednesday for the first time since the explosion to see if other pipes can be used instead.
  • #10,383
I can think of a few possibilities.
When they used concrete pump trucks, they would go for days without pumping anything, and then pump lots over many days until they saw the skimmer surge level go back up, which is an indication that the pool has been filled to a certain high level that causes overflow to skimmer.
It is possible that now they have a different system, they are injecting water more steadily over time, at a rate that keeps the pool a t a certain level that is high enough, but not so high as to overflow into skimmer tank. Robbed of fresh supplies of water, the skimmer tank eventually reaches lows we have not seen before.
Also possible that they change that state of system that skimmer tank is part of, in a way that causes water to leave the skimmer tank at a faster rate.Unclear whether this has ever been the case at this pool or any of the other reactor pools, but we have seen skimmer levels at some other pools fall to levels that we weren't used to seeing, think this has happened at least once or twice. To put this point another way, there have been times when we see skimmer levels not really changing much at some pools for long lengths of time, and then suddenly decrease quite rapidly for a number of days. Probably easier to spot this phenomenon with a pool such as the one at reactor 1 which has been considered to be far more under control than the one at 4.
  • #10,384
But unit 2 skimmer surge tank is ~3000mm
there was no change in water system:
and here is plot, sst water level from 6/15 to today:
[PLAIN]http://img714.imageshack.us/img714/6221/erwero.jpg
  • #10,385
There has been a change. They could not use the system they wanted to due to pipe damage, and an even more recent survey of building reveals that a valve they want to use is covered in debris. However, this has not stopped them from starting up a different temporary solution. They posted a document about this system which we talked about in this thread, and judging from the wording of status updates they have ben using it for a while now.
eg:
http://www.tepco.co.jp/en/press/corp-com/release/11061902-e.html
From 4:05 pm to 7:23 pm on June 18, the injection of fresh water to spent fuel pool of Unit 4 was implemented using temporary water injecting system (hydrazine was also injected from 4:29 pm and completed at 6:33 pm on same day)
However it is unclear to me whether they are now reporting every time they put water in the pool using this method, if they just put it in during brief periods of time, or more continuously. I am a little bit behind reading the status updates but I don't remember hearing anything about this very recently, say within the last 5 days.
edited to add link to document showing this alternative system:
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110616_03-e.pdf
  • #10,387
Question
TEPCO just published this new data today
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110630e11.pdf
this is what i think it all amounts to:
June 29 at the Main Gate of Fukushima Daiichi
the radiation levels were
2.3 mega becquerels (counts per sec.) per cubic centimeter in the air for Iodine-131
5.0 mega becquerels (counts per sec.) per cubic centimeter in the air for Cesium-134
3.0 mega becquerels (counts per sec.) per cubic centimeter in the air for Cesium-137
is my take on this correct, are my numbers what TEPCO data says?
note, the complete document it here (appendixes at bottom of page)
http://www.tepco.co.jp/en/press/corp-com/release/11063009-e.html
  • #10,388
causeceleb said:
Question
I am not sure which document you're referring to but MegaBecquerels (10E6) can't be correct. Radioactivity in the air has been in the order of MicroBecquerels (10E-6) all the time
  • #10,389
i'm talking about this document:
so, then, if i change all of my "megas" to "micros" does everything else look right?
  • #10,390
here's the correction:
2.3 micro becquerels (counts per sec.) per cubic centimeter in the air for Iodine-131
9.5 micro becquerels (counts per sec.) per cubic centimeter in the air for Cesium-134
9.3 micro becquerels (counts per sec.) per cubic centimeter in the air for Cesium-137
  • #10,391
but i still don't get it. i thought one becquerel was one disintegration;
how can i have .000003 disintegration (counts per second)
what is a 3 millionth of a disintigration?
what is a 3 millionth of a count per second?
  • #10,392
I don't know if anybody noticed, but when they were taking readings some distance away from the plant after opening reactor 2 doors, a value in one location was quite a bit higher than before. I thought this may cause them to take more readings, but no other data emerged to show any bad changes as a result of opening reactor 2 building, so I assumed there was some other explanation for this higher reading.
Anyway it seems they investigated reasons why a reading in that locations changed, and reported on their findings:
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110630e3.pdf
Reasons include someone forgetting to send the people doing the testing a detailed map, so they measured 100m away from where previous measurement had been done. And they didnt get out of the car to do reading at night, they just stuck their arm out of the window, which affected the reading quite a bit. Reason given for not getting out of car was 'to reduce the risk of animal encounters etc.'!
  • #10,393
What about one disintegration per 300000 seconds per mL?
  • #10,394
then you are saying that TEPCO is saying that there is next to zero radioactivity (these
three isotopes) at the main gate?
  • #10,395
causeceleb said:
but i still don't get it. i thought one becquerel was one disintegration (1 count per sec);
how can i have .000003 of a disintegration (.000003 counts per second)?
It is my understanding that such measurements are taken over a larger area than 1 cm³ and over a bigger timeframe than one second.
So for example you take 1 m³ air and count all disintegrations over a period of twelve hours. Afterwards you recalculate those results into easier to understand numbers, e.g. Bq/cm3.
What you finally get is more or less a disintegration probability. The probability that there'll be a disintegration in one cm³ air is 0.0003% every second.
  • Nuclear Engineering
46K
51
419K
17K
259K
15K
11K