Solar series battery charging problem

In summary, the conversation discusses the use of large 12v solar panels wired in series to produce 24v and connected to a 24v charge controller and two 12v batteries wired in series for 24v. However, there is an issue with this configuration, as one battery tends to fail while the other remains partially charged. The cause of this is believed to be the charging in a cascading fashion, resulting in unequal charging of the batteries. The solution proposed is to connect the common between two solar panels on the roof and tie it to the common (+/-) post that tie the two batteries together, allowing both batteries to charge simultaneously. The conversation also touches on the importance of periodically doing an equalization charge to avoid battery failure
  • #1
BernieM
281
6
I have a large array of solar panels, which are 12v panels. I have wired them two each in series to produce 24v at the array and carry that to a 24v charge controller which then connects to two 12v batteries wired in series for 24v, to power a 24 volt inverter.

But I have observed a problem with this configuration. The problem is that while the system is still charging up the battery bank, if I separate two batteries and measure the voltage on them, the first in series (from the + connection end) will be fully charged at 12.6v and the second will be less. For example, when my voltage on the array shows 28v during charge, two batteries separated and tested for voltage may show one to be 12.6v and the second one at 10.8v. This means to me that one of the batteries is being overcharged while the other battery is not yet charged. It usually results in the first battery of the pair failing. Never the 2nd one.

I am not certain but I get the feeling that the cause of this is that the power coming into charge the batteries must pass through each cell to get to the next? Whatever the cause of this is, it causes battery failure as the first battery in line in the series configuration gets overcharged while the 2nd battery is still charging to get up to full potential.

After consideration of this problem recently, I wondered if it might not be better to carry the common between two solar panels on the roof and tie it to the common (+/-) post that tie the two batteries together. In this way both batteries would see 12v from the array and charge simultaneously, rather in a cascade fashion. The solar controller would still control the charging of the array as both the + and - of the array go through it, so when it turns off, there would only be the common leg connected directly to the solar array, hence no path for power to bypass the charge controller. Likewise the inverter would not change it's connection and would still see 24 volts.

I would like to understand the cause of the difference in voltage (is it really due to charging in a cascade fashion?) I know that it is not a bad battery issue, as I have twenty 265Ah batteries in the bank (10 banks of two batteries each) and all batteries show the same voltage when tested. So it's not just a battery going bad.
 
Engineering news on Phys.org
  • #2
https://electronics.stackexchange.com/questions/14174/charging-lead-acid-batteries-in-series said:
1down voteIt is normal to charge lead-acid batteries in series. As they are used, the cell voltages will change, which is why they are not charged in parallel. If they were charged in parallel, the one with the high voltage wouldn't get much current, and the one with the low voltage would get too much current.

With the cells in series, they all get the same amount of current, and all get approximately the same amount of charge. Since they will not charge and discharge exactly the same, the battery voltage and level of charge will gradually drift apart.

To handle this, it is common to periodically do an "equalization" charge, where you overcharge the string slightly to bring up the charge of the undercharged cells. You do this because lead-acid batteries handle overcharge better than they handle undercharge.

You have done that, and at least one of the cells has gassed. Check the fluid level, and next time charge to a slightly lower voltage. Only do equalization every couple of months. If some of the cells fail, it will not be possible to charge the battery fully. When that happens, it is time to throw out the battery.
 
  • Like
Likes scottdave
  • #3
So you are saying that the one reading the higher voltage tends to fail first?
What happens if you switch positions of those two batteries?
 
  • #4
scottdave said:
So you are saying that the one reading the higher voltage tends to fail first?
What happens if you switch positions of those two batteries?

Nope, the undercharged battery will fail first due to "sulphation" of the plates.

(BTW we are talking about lead-acid batteries, correct? And you have checked the water level in all cells, correct?)

Swapping position won't help, because both get the same current in series.

The better charge controllers have a built-in "equalization" cycle for exactly this reason. Check yours, you may have it but not know about it.

If you don't have it, then you periodically (30-60 days) need to separate the batteries and put them through an equalization charge at 12v, not 24v as a maintenance procedure. My charger's equalization cycle brings each battery to 15.2 volts for 60 minutes, once every 30 days. You need to check the water levels frequently.
 
  • #5
scottdave said:
So you are saying that the one reading the higher voltage tends to fail first?
What happens if you switch positions of those two batteries?

Yes. The higher voltage battery is the one that always fails. Never the lower voltage one. I never let my array fall below 24 volts (1/2 charged.) So you see one battery is at full charge (12.6v) the other is at less than 1/2 charge (10.8v) while system voltage shows 1/2 charge or greater (24.5v). Originally I believed it was too much charging current so added more battery banks to cut down the amount of current per bank. (Please note that the voltages given are examples, and not actual measurements, they are just to illustrate the problem.)

It seems that the first cell in the first battery (the battery that has it's + terminal connected to the array) fails always. Swapping batteries around gets rid of the problem, but handling 200 pound batteries isn't any fun ( I have to physically swap the batteries position due to the wiring. All wires are equal length to a central point where all connect to the power so that there is no difference in potential that any bank sees from the rest.)

I equalize the batteries regularly (once or twice a month at 32v for 2-4 hours.) These are 7-10 year batteries that are failing in under 2 years. Not good. Very expensive problem to have. I have had 4 die now. I saw this same problem occur with golf cart batteries on a friends' array that was set up for 12v. So he had two 6v golf cart batteries in series. Same exact issue.

I am not a novice when it comes to solar, as I live off grid and have lived off grid now for 2 years with solar being my sole source of power. I do regular maintenance.

The array is about 5KW of panels and there is about 100 amps @ 24v coming in from the panels at max.
 
  • #6
BernieM said:
I have twenty 265Ah batteries in the bank (10 banks of two batteries each)
Do i understand you have ten 24 volt 'banks' wired in in parallel ? Do you equalize them one at a time or all in parallel?

Do you have any 12 volt loads connected across just one of the two batteries that's in series comprising a 'bank' ??
The only other wire on "the common (+/-) post that tie the two batteries together" should be a high impedance voltmeter..
 
  • #7
BernieM said:
These are 7-10 year batteries that are failing in under 2 years.

What is the failure mechanism? Cracked plates are most often caused by low water levels.

BernieM said:
I equalize the batteries regularly (once or twice a month at 32v for 2-4 hours.)

That is almost an excessive amount of equalizing. I would expect that to evaporate away lots of water.

Are the batteries flooded or AGM or gel cell?

If flooded:
How often do you pull the caps to check water level? I recommend once per equalizing cycle. That is quite a chore if you have 120 cells..
Do you have a watering system that distributes water to all cells without the need to pull the caps to check?

If gel cell:
The max charging voltage for a flooded battery is 14.2, for a gel cell 13.8, for an AGM (don't know).
The max voltage for gel cells is very sensitive to temperature. If the gel cells are at 120F or more when charging, failure is likely.
 
  • #8
jim hardy said:
Do i understand you have ten 24 volt 'banks' wired in in parallel ? Do you equalize them one at a time or all in parallel?

Do you have any 12 volt loads connected across just one of the two batteries that's in series comprising a 'bank' ??
The only other wire on "the common (+/-) post that tie the two batteries together" should be a high impedance voltmeter..

20 Flooded Cell batteries in 10 banks of two each. In other words, pairs of batteries wired together for 24 volts, the pairs wired in parallel.
The only load is the inverter itself.

anorlunda said:
What is the failure mechanism? Cracked plates are most often caused by low water levels.
That is almost an excessive amount of equalizing. I would expect that to evaporate away lots of water.

Are the batteries flooded or AGM or gel cell?

If flooded:
How often do you pull the caps to check water level? I recommend once per equalizing cycle. That is quite a chore if you have 120 cells..
Do you have a watering system that distributes water to all cells without the need to pull the caps to check?

If gel cell:
The max charging voltage for a flooded battery is 14.2, for a gel cell 13.8, for an AGM (don't know).
The max voltage for gel cells is very sensitive to temperature. If the gel cells are at 120F or more when charging, failure is likely.
Batteries are 8D's
Due to the low amount of current, I have very little water loss. At peak each bank gets at max 12 amps or so. That is why I equalize them a bit longer and more often.
I have to manually add water, but as there is never much water loss, it hasn't been a problem.
I use Trojan's guide on voltage for charging, which is 28.2 - 29.4 volts, I use 28.8v as the high voltage setting on my charge controller.

When a battery fails, I can charge it to full voltage but soon after disconnecting from the charging source, after the surface charge is gone, the voltage will go to 11.8v where it then stays. It will not stay at 12.6v. To me this means a half cell problem (full cell failure would be 1.6v) which I believe may be a short internally, but I can not understand by what mechanism this would happen on all batteries regardless of type. As I said this same thing happens on 6 volt golf cart batteries as well. I came to the belief that too much current was passing through the first cell, but at 10-12 amps, with this large of batteries I couldn't see that being enough to do this kind of damage.
 
  • #9
Four failures out of twenty batteries, i think you said.

Are they close together ? Batteries in parallel need to be about the same temperature. Are they all in the shade?
All about same age? We're not discussing recycled batteries, are we ?
 
  • #10
BernieM said:
So you see one battery is at full charge (12.6v) the other is at less than 1/2 charge (10.8v) while system voltage shows 1/2 charge or greater (24.5v). (Please note that the voltages given are examples, and not actual measurements, they are just to illustrate the problem.)
...
...
I equalize the batteries regularly (once or twice a month at 32v for 2-4 hours.) .

Your frustration is understandable - it is quite an expensive investment.

If possible, could you provide a couple more bits of information:

1) You say the 12.6v and 10.8v are illustrative voltages. Are the "actual" measurements in the same ball park? If not, any chance you could relate figures from actual voltages you measured?

2) Have you ever equalized a pair of batteries exhibiting the problem, individually - i.e. not as a pair. So each battery equalized at around 15v - 16v?
 
  • #11
jim hardy said:
Four failures out of twenty batteries, i think you said.

Are they close together ? Batteries in parallel need to be about the same temperature. Are they all in the shade?
All about same age? We're not discussing recycled batteries, are we ?
Using a mix of batteries (age / model / temperature) is best avoided. Not a pleasant prospect to change them all at one time if that's much sooner than they're guaranteed for.
I wonder if it could be worth while checking the wiring between the batteries in detail? Sounds a bit daft but it wouldn't cost any money to measure voltage drops between adjacent + and - terminals etc..
 
  • Like
Likes jim hardy and OmCheeto
  • #12
We're the failures sudden or gradual?
Do you keep records that can be used to plot trends?

The Trojan Battery Company promotes their reputation for making superior batteries. Contact them and ask if they would be willing to do a complete post mortem on one of the failed batteries. They may even be willing to send someone to look over your entire installati M.

If the cause is sulphation, then it might even be recoverable.

Here is a paper that claims to present a fault tree causal analysis of lead acid battery failure.
http://journal.esrgroups.org/jes/papers/4_2_2.pdf
 
  • Like
Likes jim hardy, sophiecentaur, OmCheeto and 1 other person
  • #13
sophiecentaur said:
I wonder if it could be worth while checking the wiring between the batteries in detail? Sounds a bit daft but it wouldn't cost any money to measure voltage drops between adjacent + and - terminals etc..
Like that idea .

I've been wracking my brain too. Old troubleshooter instinct , plus i have OCD tendencies.

When you're baffled it's helpful to try baseless random measurements and see if anything peculiar shows up. Ever watch a veterinarian poke gently at a puppy until it yips?

Bernie separates his cells to check for failure.
Pick a pair that's been having trouble. Don't disconnect them, just measure... What is voltage across each when being charged? And when loaded? Check the AC component too by switching the dmm to AC. Feel one with each hand - are they same temperature?
.........................

Since i knoiw nothing about your installation.
Is that inverter's input filtered ? Reason i ask is
Old fashioned SCR inverters take huge gulps of current at twice line frequency.
Large capacitors adjacent inverter are necessary to keep them out of the battery bank.
I once had to add capacitors to old fashioned SCR inverters to tame our battery voltage. They modulated it at twice line frequency , imposing peak to peak ripple about 75% of battery voltage . We placed 1 microfarad per milliamp of inverter current, about 60,000 μf, at input terminals of each inverter .

PWM inverters draw high frequency current pulses. Are his filtered ?
What about that charge controller output? Is it pwm too?
Reason i mention that is , knowing nothing about his physical battery wiring layout i wonder if it has substantial inductance?
If so it's possible some battery pairs carry the lion's share of the high frequency current. High frequency pulses heat the electrolyte lowering cell voltage, perhaps starving other battery pairs on float..

upload_2017-6-22_9-45-18.png

https://tspace.library.utoronto.ca/...3/Sritharan_Thuwaragan_201206_MASc_Thesis.pdf

While he's checking DC, measurements of the AC ripple across several batteries might give a clue.
Draw a physical map and write them on it looking for a pattern.
But the meter will have to have frequency response out to inverter's and charger's pwm frequencies. Old fashioned Simpson 260 using "output" jack is good to about 40 khz. Check your dmm book...

Yes it's a long shot . But looking into it might lead to some other shorter shot.

Necessity may be the mother of invention but desperation is at least its good uncle.

old jim
 
Last edited:
  • Like
Likes Tom.G and sophiecentaur
  • #14
Very weird.
@BernieM , can you tell us what the average daily depth of discharge is?
At 50%, a 2 year lifespan is standard for flooded lead acid.
I'm still scratching my head as to why the order of the batteries makes a difference. It makes absolutely no sense.
And your one paragraph is rather incomprehensible:

BernieM said:
After consideration of this problem recently, I wondered if it might not be better to carry the common between two solar panels on the roof and tie it to the common (+/-) post that tie the two batteries together. In this way both batteries would see 12v from the array and charge simultaneously, rather in a cascade fashion.

"carry the common"?
"cascade fashion"?

Can you doodle a schematic for me. I've had a lifelong difficulty with language, but, I've found that a picture is sometime worth more than a thousand words.

Thanks!
 
  • Like
Likes jim hardy
  • #15
OmCheeto said:
I've had a lifelong difficulty with language,
The appropriate 'language' for describing this sort of problem is Pictures. I am confused by written descriptions, too.
 
  • Like
Likes OmCheeto
  • #16
sophiecentaur said:
The appropriate 'language' for describing this sort of problem is Pictures. I am confused by written descriptions, too.

I saw someone post one day; "I don't understand pictures, nor equations. Just tell me what the problem is!"
I'm quite the opposite, and the lady who posted that has a PhD, so I just assumed I was stupid.
 
  • #17
jim hardy said:
Four failures out of twenty batteries, i think you said.

Are they close together ? Batteries in parallel need to be about the same temperature. Are they all in the shade?
All about same age? We're not discussing recycled batteries, are we ?

All batteries are the same age and two different brands, but same specs and type. Four failures out of 24 batteries originally, I now have 20 left. They are about 2 years old at this point.

mccv said:
Your frustration is understandable - it is quite an expensive investment.

If possible, could you provide a couple more bits of information:

1) You say the 12.6v and 10.8v are illustrative voltages. Are the "actual" measurements in the same ball park? If not, any chance you could relate figures from actual voltages you measured?

2) Have you ever equalized a pair of batteries exhibiting the problem, individually - i.e. not as a pair. So each battery equalized at around 15v - 16v?

They are not recycled batteries. They came out of a 12v solar power system that someone was upgrading and were 1 year old when I got them. I tested them all and they all tested about the same on a load tester. They are two different brands but have the same specifications. Both brands have failed, so failure is not due in my opinion to a difference between the brands.

There is about an inch of space between batteries. They are housed in a small room on the porch which is covered and at lower temperature than outside currently (it's hot here but these failures have happened when it's cold too, so it isn't heat related.) I also have temperature compensation on the charge controller and the sensor is near the batteries. Difference in temp from top batteries to lower batteries is about 3c max when it's hot outside. That's the best I can do with where I live and the conditions I have to deal with here.

1) --- 12.6v and 11.8v. I put one of the failed batteries on a stand alone solar charging station with 250 watts available to charging. After a month of charging cycles with no usage on it, it still would drop to 11.8v and stay there after fully charging up.

2)--- I also ran some equalizing cycles on it during that time. I was baffled by the problem and was trying to figure it out myself. I even went so far at the end to put a bit of hydrochloric acid in it to dissolve the sulfate (hydrochloric dissolves lead sulfate but does not dissolve pure lead and after a while will dissipate, leaving the cell as chlorine gas.) This changed nothing either. So I was relatively certain at this point that it was not a sulfation issue, though obviously I could be wrong.

OmCheeto said:
Very weird.
@BernieM , can you tell us what the average daily depth of discharge is?
At 50%, a 2 year lifespan is standard for flooded lead acid.
I'm still scratching my head as to why the order of the batteries makes a difference. It makes absolutely no sense.
And your one paragraph is rather incomprehensible:
"carry the common"?
"cascade fashion"?

Can you doodle a schematic for me. I've had a lifelong difficulty with language, but, I've found that a picture is sometime worth more than a thousand words.

Thanks!
These are considered 7 year batteries as I recall. If one keeps depth of discharge less than 50%, one should be able to nearly double the life span. The life span of a battery is considered to be the number of full discharge cycles the battery can tolerate without failing. So a 50% discharge would take 2 discharges to that depth to equal one complete discharge. This is how I run my setup, I do not allow it ever to get below 50% (24v.)

When I said 'carry the common' I meant to connect the common connection between two solar panels on the roof, where they are joined in series, and connect that directly to the battery's common connection, where they join in series. In this way each battery would have a separate solar panel circuit charging it. Simplest model would be two batteries, each with their own solar panel to charge them, then joining the two batteries in series. In this way there would be 24v across the batteries as well as 24 volts across the solar panels, yet each battery would only see 12v passing through it's terminals.

What I mean by cascade fashion (and I will make no illusions that I understand battery physics here) is that I visualize all the power to charge both batteries having to pass through the first cell, the current moving to the next cell, will be less than the first cell sees as the first cell has used up some power in charging, and on and on through to the last cell of the second battery. Perhpas this is an incorrect picture of how it works (and I am sure someone will correct me if it is) but I see it that the + terminal sees all the incoming power to charge both batteries, where the + terminal at the second battery sees only half of that due to the power dropped in the first battery to charge it. That's what I meant by cascade fashion. Though the voltage potential is the same across both batteries, the amount of current would not be as I see it.
I have another small array that I put in place that is 12v and I don't see this problem there.
 
Last edited:
  • #18
jim hardy said:
Like that idea .

I've been wracking my brain too. Old troubleshooter instinct , plus i have OCD tendencies.

When you're baffled it's helpful to try baseless random measurements and see if anything peculiar shows up. Ever watch a veterinarian poke gently at a puppy until it yips?

Bernie separates his cells to check for failure.
Pick a pair that's been having trouble. Don't disconnect them, just measure... What is voltage across each when being charged? And when loaded? Check the AC component too by switching the dmm to AC. Feel one with each hand - are they same temperature?
.........................

Since i knoiw nothing about your installation.
Is that inverter's input filtered ? Reason i ask is
Old fashioned SCR inverters take huge gulps of current at twice line frequency.
Large capacitors adjacent inverter are necessary to keep them out of the battery bank.
I once had to add capacitors to old fashioned SCR inverters to tame our battery voltage. They modulated it at twice line frequency , imposing peak to peak ripple about 75% of battery voltage . We placed 1 microfarad per milliamp of inverter current, about 60,000 μf, at input terminals of each inverter .

PWM inverters draw high frequency current pulses. Are his filtered ?
What about that charge controller output? Is it pwm too?
Reason i mention that is , knowing nothing about his physical battery wiring layout i wonder if it has substantial inductance?
If so it's possible some battery pairs carry the lion's share of the high frequency current. High frequency pulses heat the electrolyte lowering cell voltage, perhaps starving other battery pairs on float..

View attachment 205901
https://tspace.library.utoronto.ca/...3/Sritharan_Thuwaragan_201206_MASc_Thesis.pdf

While he's checking DC, measurements of the AC ripple across several batteries might give a clue.
Draw a physical map and write them on it looking for a pattern.
But the meter will have to have frequency response out to inverter's and charger's pwm frequencies. Old fashioned Simpson 260 using "output" jack is good to about 40 khz. Check your dmm book...

Yes it's a long shot . But looking into it might lead to some other shorter shot.

Necessity may be the mother of invention but desperation is at least its good uncle.

old jim

Voltage is equal across the batteries while not disconnected from each other. After disconnecting, one will show a lower voltage, the other a higher voltage, but the voltage across both will be whatever they were charged to as a pair.

There is no source of a/c here as I am off grid 20 miles from a city, nearest power lines are 5 miles from here, no generators on the system, etc. Sources of high freq a/c would be a microwave oven, a computer (which isn't always on) and a tv perhaps.

I have been using a 8KW/32KW true sine wave inverter. It has been a great inverter and gone through a lot of tough tests over the last couple years and has performed excellently. It's made by Powerjack. It's split phase 220/110.

The old charge controller I used was PWM, recently I have put on a relay type that can handle 300 amps. Kind of dumb but it doesn't shut down when it gets too hot. Before I had issues when the amperage going through the controller got high and temps were high. I have almost finished an underground building to put the batteries, inverter and charge controller into guarantee that the batteries don't see any high temps. Currently they can get up to about 95F for short periods (a few hours at the end of a day.)
 
  • #19
BernieM said:
These are considered 7 year batteries as I recall.
Everything has an "advertised" "rated" lifespan if kept within its normal operating parameters.
I think the first battery in my first car lasted 20 years, even though it was probably rated for about 5. Not sure. That was nearly a half century ago.
If one keeps depth of discharge less than 50%, one should be able to nearly double the life span.
Not sure where you heard that. It's not true. You should stop listening to whomever told you that.

ps. It's partially true, but in a hand-wavy, really bad maths kind of way.

pps. Are you still living in the Mojave desert in Arizona? Sorry to be so nosy, but I checked out your profile, in an effort to figure out your battery's environment, saw that it was blank, and checked out some of your posts.:redface:
 
  • #20
OmCheeto said:
I saw someone post one day; "I don't understand pictures, nor equations. Just tell me what the problem is!"
I'm quite the opposite, and the lady who posted that has a PhD, so I just assumed I was stupid.
Meh. Take heart , my friend.
We picture thinkers are in good company.

Here's a longer extract from Einstein's answer:

"(A) The words or the language, as they are written or spoken, do not seem to play any role in my mechanism of thought. The psychical entities which seem to serve as elements in thought are certain signs and more or less clear images which can be "voluntarily" reproduced and combined. There is, of course, a certain connection between those elements and relevant logical concepts. It is also clear that the desire to arrive finally at logically connected concepts is the emotional basis of this rather vague play with the above-mentioned elements. But taken from a psychological viewpoint, this combinatory play seems to be the essential feature in productive thought--before there is any connection with logical construction in words or other kinds of signs which can be communicated to others.

(B) The above-mentioned elements are, in my case, of visual and some of muscular type. Conventional words or other signs have to be sought for laboriously only in a secondary stage, when the mentioned associative play is sufficiently established and can be reproduced at will.

(C) According to what has been said, the play with the mentioned elements is aimed to be analogous to certain logical connections one is searching for.

(D) Visual and motor. In a stage when words intervene at all, they are, in my case, purely auditive, but they interfere only in a secondary stage, as already mentioned.

(E) It seems to me that what you call full consciousness is a limit case which can never be fully accomplished. This seems to me connected with the fact called the narrowness of consciousness (Enge des Bewusstseins)"

From "A Mathematician's Mind,... Princeton University Press, 1945." in Ideas and Opinions.
BernieM said:
I have been using a 8KW/32KW true sine wave inverter. It has been a great inverter and gone through a lot of tough tests over the last couple years and has performed excellently. It's made by Powerjack. It's split phase 220/110.

They do have a following. It's a pretty good bet they do draw some sort of pulsing current
this guy adds a 18 microhenry inductor to reduce idle current draw.
http://www.anotherpower.com/board/index.php?topic=902.0

BernieM said:
Voltage is equal across the batteries while not disconnected from each other. After disconnecting, one will show a lower voltage, the other a higher voltage, but the voltage across both will be whatever they were charged to as a pair.
That is very confusing. They're not all joined in the middle, are they? All those common +/- junctions tied together? Something's got to be holding voltage equal.
Sounds to me like internal battery failure but I'm at a loss as to what causes it. You've described what should be a quite good system.


BernieM said:
I use 28.8v as the high voltage setting on my charge controller.
divided by 12 cells = 2.4 volts per cell
Sounds like you are doing everything right.

Gotta be something very simple or something very esoteric.

That huge inverter has to draw pulsating current. Were this mine I'd look at the AC ripple across every one of my batteries with inverter running and with it off, objective being to see if they're sharing it equally. If your dmm has a frequency button, check that, too.
Fortunately it's high frequency so if it's there it will be easier to filter than was my 120 hz. A few good high current oil filled 'SCR commutation' capacitors right across its input terminals might do the trick. This CDM Cornell-Dubilier one's good for 60 amps rms.
Wish i knew how to measure the ripple current your inverter draws. Most clamp arounds I've seen are only good to 2 khz or less.

upload_2017-6-22_13-36-57.png


you might get away with less expensive aluminum electrolytics, depending on what frequency you find.
http://www.cde.com/resources/catalogs/AEappGUIDE.pdfWishing you Good Luck
and when you solve this one i hope you'll enlighten us.

old jim
 
  • #21
OmCheeto said:
Everything has an "advertised" "rated" lifespan if kept within its normal operating parameters.
I think the first battery in my first car lasted 20 years, even though it was probably rated for about 5. Not sure. That was nearly a half century ago.

Not sure where you heard that. It's not true. You should stop listening to whomever told you that.

ps. It's partially true, but in a hand-wavy, really bad maths kind of way.

pps. Are you still living in the Mojave desert in Arizona? Sorry to be so nosy, but I checked out your profile, in an effort to figure out your battery's environment, saw that it was blank, and checked out some of your posts.:redface:

Yes I live in the Mojave desert west of Phoenix, where yesterday it was 121F here. So my battery bank and solar are hugely important and the difference between life and death literally, as I live remote, 1/2 hour drive from nearest town. If power goes out here it could get really serious (though I do have a generator for backup, which I nearly never run.)

If you just go to a good search engine and search for 'depth of discharge vs battery life' you will find plenty of corresponding articles and webpages that confirm the same thing, including some that are reputable.

jim hardy said:
Meh. Take heart , my friend.
We picture thinkers are in good company.

They do have a following. It's a pretty good bet they do draw some sort of pulsing current
this guy adds a 18 microhenry inductor to reduce idle current draw.
http://www.anotherpower.com/board/index.php?topic=902.0That is very confusing. They're not all joined in the middle, are they? All those common +/- junctions tied together? Something's got to be holding voltage equal.
Sounds to me like internal battery failure but I'm at a loss as to what causes it. You've described what should be a quite good system.



divided by 12 cells = 2.4 volts per cell
Sounds like you are doing everything right.

Gotta be something very simple or something very esoteric.

That huge inverter has to draw pulsating current. Were this mine I'd look at the AC ripple across every one of my batteries with inverter running and with it off, objective being to see if they're sharing it equally. If your dmm has a frequency button, check that, too.
Fortunately it's high frequency so if it's there it will be easier to filter than was my 120 hz. A few good high current oil filled 'SCR commutation' capacitors right across its input terminals might do the trick. This CDM Cornell-Dubilier one's good for 60 amps rms.
Wish i knew how to measure the ripple current your inverter draws. Most clamp arounds I've seen are only good to 2 khz or less.

View attachment 205912

you might get away with less expensive aluminum electrolytics, depending on what frequency you find.
http://www.cde.com/resources/catalogs/AEappGUIDE.pdfWishing you Good Luck
and when you solve this one i hope you'll enlighten us.

old jim

The post about that PowerJack inverter is old. I discussed this with the engineer/inventor/owner of Powerjack in China, and he says that all of the issues in that post have been dealt with several years back. I find very little not to like about it, especially considering it's ability to output 4x it's rated output for up to 2 minutes (instead of 15 seconds) without shutting down to protect itself or frying itself. Many times while my system was pretty much under full load I have fired up a big power hungry table saw and ran it for a minute or so while I did something I needed to do in a hurry, and the inverter didn't whine about it. I have two of them, one as a backup, and the backup is a year older. It has a few idiosynchrasies that the newer one doesn't, and a more recent model I bought for a friend and his house, is even better. So they are continuously improving their inverter.

I have an o-scope and have checked the output of the inverter out and it's really clean and a very true sine wave, that's really stable. I have never checked the input of the inverter for a/c on the scope, though I did check it with my meter with no a/c shown on the batteries. I put the meter on Freq and did a check and it shows .001 which is the default display so it's not detecting any a/c up to 3khz (range of this meter.)

I am suspecting that it might be a combination of not a high enough amount of current during equalization and battery electrolyte stratification. It's the only thing that makes sense to me. I guess I can disconnect 1/2 of the array during equalization and see if that increase of current per battery changes anything. I should be able to tell right away by disconnecting two of the batteries and measure the voltages on them after equalization. If they don't read the same voltage then I still have the problem, if they do read the same then it's fixed. So I guess that's my next step.
 
  • #22
I need to make a clarification here. I see that part of the confusion is what is happening before a battery failure and then after the failure. So let me put it like this:
Ignore the charge controller and just imagine I have two 12 volt solar panels connected in series to produce 24v at the array. This in turn connects directly to two 12v batteries, likewise connected in series. As it should be.

At any time, if I measure the battery voltage across the two batteries it will show, of course, the system voltage, which will reflect the solar input and load. If I disconnect the two batteries from each other so they are no longer in series, and measure the voltage of each, they will both have the same voltage.
But when a problem occurs, if I disconnect the two batteries, one will show a lower voltage than the other. The lower voltage battery will always be the battery that connects into the system at the negative terminal (battery #2 in the series.) But at this point neither battery is failed. Both will charge fully and keep the charge if charged separately. I have found that I can delay this problem if I swap them out physically so that the battery that had it's negative terminal connected to the array is now the one that connects to the positive of the array and vice versa.

When a failure finally occurs however, the failure is the battery that had it's positive terminal connected to the array. At this point when I read the voltage of it, it will be .8v lower than fully charged, regardless of how I try equalizing or charging it thereafter.

So it seems to me that if sulfation was the cause, it should be the battery that spends more time in a discharged state before the failure, (battery #2,) not the one that is constantly at a higher voltage (battery #1.) That's why I rule out sulfation. The only difference between why one has a higher charge state than the other in my mind is current. That all the current to charge both the batteries must pass through the first battery (the one with the positive connection to the array) where the positive terminal on the second battery is carrying only half the current of the first one, because of the power used in charging the first battery on its way to the second. Although both batteries see the same voltage, the first battery sees double the current than the second one. If I have that wrong let me know.

So it is the current that I feel that has a role in this but I don't know how it plays a role.
 
  • #23
BernieM said:
If I have that wrong let me know.
Yes i think you have it wrong, your words do not describe behavior of electricity.
Two 'things' that are in series have the same exact current through them. They can have different voltages, though.

Only way for them to have different current is for a leakage path around one of them to appear.
That might be spilt electrolyte on top of the battery that bridges its terminals
or something connected to that +/- junction between a pair which you've already said isn't there
or a hole in the case of a battery through which current gets from the electrolyte to a conductive battery rack or something.
One's imagination can run away.
BernieM said:
because of the power used in charging the first battery on its way to the second. Although both batteries see the same voltage, the first battery sees double the current than the second one. If I have that wrong let me know.

This is a decent little writeup
http://batteryuniversity.com/learn/article/serial_and_parallel_battery_configurations
Batt_U_Series.jpg


Thought experiment:
Imagine yourself very small and seated at the observation point with a "charge counter", a hand held gizmo that increments by one count every time a single quantum of positive electric charge moves past your observation point in the direction of the arrow.
When it increments 6.24 X 1018 times a second that's one amp of current flowing.
Look up "Coulomb".
Since the charge of one electron is known to be about 1.6021766208(98)×10−19 C,[7] 1 C can also be considered the charge of roughly 6.241509×1018 electrons
An amp is one Coulomb per second flowing past a point. It's that simple.

Observe those charges can't get out the top or bottom of the battery string because of the insulation..
So,
All the charges that go in the left end must come out the right end, traversing all four cells.. You could observe anyplace in the series string and get the same current.
That's why things in series have same current. It's their voltage that can differ.

not talking down here, just it's important to get the basic definitions nailed down straight early on. Saves a lot of unlearning later.

Rethink your sulfation conclusion?old jim
 
  • #24
jim hardy said:
a hand held gizmo that increments by one count every time a single quantum of positive electric charge moves past your observation point in the direction of the arrow.

Of course , some folks consider current to be movement of negative charges because usually it's electrons that carry them.
Hence the old conundrum of "Conventional Current"(positive charges in motion) versus "Electron Current"(negative charges in motion).
They work identically and give the numerical same answer, just on your drawings your current arrows point in opposite directions .

old jim
 
  • #25
http://journal.esrgroups.org/jes/papers/4_2_2.pdf was a link provided in an earlier post in this thread. In it it shows an electronic model of the cells in a battery. If you will notice the R's are in series in it. Current drops when it passes through a resistance. So there is no way that the same amount of current that enters the battery may get past to the next cell having passed through a resistor, stated simply. Start with whatever current you want on either side and move through and calculate it out. Current drops through each resistive load. Not true? Or another way to put it would be that each cell consumes power, which means if you have a fixed amount of power entering the battery, as power is consumed in charging a cell, there is less power available at the next cell. How can you consume electrons and do work with them, and not reduce the overall volume of electrons with a fixed input of electrons to begin with?
 
  • #26
BernieM said:
Current drops through each resistive load. Not true?
Not true. Current may split into multiple branches (parallel circuits), but it never drops across anything. Check out Kirchhoff's voltage and current laws.
 
  • #27
Asymptotic said:
Not true. Current may split into multiple branches (parallel circuits), but it never drops across anything. Check out Kirchhoff's voltage and current laws.

You took what I said out of context. I said that in a series resistor configuration which is the model of the internal electronic equivalence of a battery presented in the paper I referenced in my last post, that current drops with each additional resistor. I was not talking about parallel resistance circuits, only series.

Part of the problem is how you view the model. The sum of the resistances in a circuit in series will limit the total amount of power flowing into the circuit, like one larger resistor would. Rtotal= R1+R2+... Rx. So R total is the total resistance and at a given voltage means that a fixed amount of current will flow through this circuit. But where is the current used? By the resistors and it is dissipated as heat. So all the current enters the circuit at point A and when it encounters the first resistor, power is used and so there is less current flowing on to the second resistor where more power is used, and less then to flow to the next resistor, where it is used, etc. So when you say that the current is fixed, yes, the total current is fixed by the sum of the resistances. But internally in the circuit how much current will be flowing at any point will be determined by how much current was used in work before that point.
 
  • #28
BernieM said:
Current drops through each resistive load. Not true?

Not true. Basic definition of current is charge flowing past a point.
BernieM said:
How can you consume electrons and do work with them, and not reduce the overall volume of electrons with a fixed input of electrons to begin with?
You don't consume electrons, or charge. They're sort of analogous to matter.
The charge carries energy in proportion to its 'voltage' (more correctly its potential) which is sort of analogous to pressure. You don't lose matter when it flows through a pipe, just its pressure drops.
British textbooks still used the term "Pressure" for voltage when i was in high school.

Some basic definitions for you, and i hope you'll use Google to find articles that suit your learning style.
I'm sure you know all these concepts just you're using the wrong words for some of them
so you'll be misunderstood when you try to communicate your thoughts
and you might get your mental pictures confused, too i don't know for i can't see them...

The terms are hard to remember at first because they're all named after dead physicists,
further the international naming committees have to divvy up the names among countries so no politicians feel slighted.
Once you've tied the names to the physical concepts it makes sense.
I'm so bad with names it took me a long time. I remember struggling.

It all starts with Coulombs (after Charles Coulomb, a Frenchman).
Remember what is a Coulomb from above - equivalent to charge of about 6.24X1018 electrons.

Energy = ability to do work. SI unit of energy is Joule(English physicist),
the work done by pushing with a force of one Newton(You know him) for a distance of one meter.
A Newton is a small but readily perceptible force.
To put Newtons and Joules in more familiar terms, a Quarter Pounder burger weighs roughly one Newton. So a Joule will lift a Quarter Pounder against gravity roughly a yard(which is almost a meter). Not a lot of energy. Memory aid - imagine Dr Joule and Isaac Newton eating at MacDonald's.

Power = rate of doing work. You can rub your palms together and feel the heat being generated(work being done) by that Force X Distance. One Joule per second is one Watt(Scottish). Not a lot of power but you can feel it.

So how does charge do work?
You know like charges repel and opposites attract. That's the "electric field " between them. Simply moving them through that field involves work.
To push them against it requires work, to let them move with it delivers work.
That work shows up as an increase or decrease of the 'voltage' those charges possesses .(more correctly ' potential' they possess)
Remember what is a Coulomb(French) - a certain number of individual charges,
and that an Ampere(also French) is one Coulomb per second passing an observation point

One Joule per Coulomb is one Volt(after Volta, Italian). Every Coulomb of charge carries along with it some potential energy that can do some work. That's its potential, closely akin to its voltage. Raising its potential raises its voltage, lowering it lowers...
As Coulombs flow through a battery that's supplying a load they acquire energy from the chemicals in the battery. As they flow toward the load they carry along that energy. When they flow through the load they give up that energy. Then they return to the battery , for another round trip.
When the battery is being charged Coulombs get 'energized' by your solar panel and give that energy up to the chemicals inside the battery.

Rate at which energy gets moved is then
(Joules per Coulomb) X (Coulombs per second) = Volts X Amps = Watts .
Begorra, Sacre Bleu, Voila, Blimey !

So-
i think you have criss-crossed terms Current and Voltage somewhere between your mental picture and what you typed.
Reason i went on for so long is to try and help straighten out your conversion from mental picture to words.

Google will find much better tutorials for you.

Please don't be offended.

old jim
 
Last edited:
  • #29
BernieM said:
But where is the current used? By the resistors and it is dissipated as heat.
BernieM said:
when it encounters the first resistor, power is used and so there is less current flowing on to the second resistor where more power is used, and less then to flow to the next resistor, where it is used, etc

That tells me you're not using the term in its accepted sense.

Current doesn't get used, Potential is what gets used.

Your mental picture might be fine i don't know

but potential is closely akin to potential energy and it's energy that gets consumed not current ..

Current is same everywhere in a series circuit. Just like hydraulic fluid in a pipe.
 
  • #30
BernieM said:
so there is less current flowing on to the second resistor where more power is used, and less then to flow to the next resistor, where it is used, etc.
This reads really wrong. Whatever you may mean to say, what you have written implies that the current somehow gets less and less units way round a circuit. This is just not the case, Every Amp out of the + battery terminal, returns through the - terminal. You have to distinguish between the meanings of the terms Current, Charge, Potential difference and Power and follow 'the rules'- even when attempting a 'friendly' and chatty explanation of the way a circuit operates.
 
  • Like
Likes jim hardy
  • #31
sophiecentaur said:
You have to distinguish between the meanings of the terms Current, Charge, Potential difference and Power and follow 'the rules'- even when attempting a 'friendly' and chatty explanation of the way a circuit operates.

Amen,
and i was too lax above . it was in interest of brevity.

my old standby
Laviosier, quoting de Condillac
https://web.lemoyne.edu/giunta/EA/LAVPREFann.HTML
"We think only through the medium of words. --Languages are true analytical methods. --Algebra, which is adapted to its purpose in every species of expression, in the most simple, most exact, and best manner possible, is at the same time a language and an analytical method. --The art of reasoning is nothing more than a language well arranged. ....
... the sciences have made progress, because philosophers have applied themselves with more attention to observe, and have communicated to their language that precision and accuracy which they have employed in their observations: In correcting their language they reason better."
not bad thinking for 1780, eh ?
Though i'd make it read
We think exchange our thoughts only through the medium of words.
 
Last edited:
  • #32
Well I am not going to belabor this any longer. It's possible I have gotten things mixed up in this discussion, as to which is fixed, i.e., current or voltage. But don't forget a battery cell is an electrochemical reaction and a cell is not a carbon resistor. One has to capture 2 electrons to reverse the process to charge a cell as I recall. The earlier comment made in one of the posts was that you have X coulombs of electrons flowing in the circuit, a coulomb of course being a fixed quantity of electrons. When you have electron capture, you have to be subtracting from the total number of electrons flowing once capture occurs.

Regardless, this is a real problem evidenced by the dead batteries.
However, I think this could be a power density issue. And that's why I went to stratification. If the electrolyte is stratified, the current density flowing through the electrolyte will be higher where the electrolyte is stronger, less current flowing through the weaker electrolyte. So there would be a gradient from top to bottom of the battery in each cell. Any lead plates conducting current will see the lower portion of the plate with a much higher current density compared to the upper portion of that plate. If I put say 10000amps charge on a battery, the post would evaporate. At lower amperages it would melt, and so forth and at zero amps of course no damage. By reducing the area over which the current is entering the electrolyte, or increasing the the current densities in one area, one would effectively have a higher current density and may be degrading the plate starting from the bottom and as it falls to the bottom of the case, works on up. At least that's the theory I had come up with. Wrong or right it seems to me to make the most sense. This is what I was tending toward in the conclusion that I made earlier. I guess it's time to cut a few batteries open.
 
  • #33
BernieM said:
But don't forget a battery cell is an electrochemical reaction and a cell is not a carbon resistor. One has to capture 2 electrons to reverse the process to charge a cell as I recall. The earlier comment made in one of the posts was that you have X coulombs of electrons flowing in the circuit, a coulomb of course being a fixed quantity of electrons. When you have electron capture, you have to be subtracting from the total number of electrons flowing once capture occurs.

nope. That's the source of your confusion.
See
http://ecee.colorado.edu/ecen4517/materials/Battery.pdf
BernieM said:
However, I think this could be a power density issue.

Could be.

Might also be a ripple current issue. I don't know if it is, but good troubleshooting rules out the possibilities one at a time.
Industry papers on effect of ripple on batteries confirm it heats the electrolyte and to an extent the plates too. It shortens battery life.
The heating is easily measured. Do your batteries get warmer when running that inverter from them?
http://www.cdtechno.com/pdf/ref/41_2131_0212.pdf
upload_2017-6-23_19-49-56.png

http://www.battcon.com/PapersScanned1999/GernerPaper1999.pdf
upload_2017-6-23_19-51-1.png



http://www.ecmweb.com/ops-amp-maintenance/get-know-your-battery

Ripple current — Excessive ripple will cause internal heating of batteries. Ideally, ripple current should be less than 5A for every 100Ah. However, ripple current says more about the state of the charger than the battery. Ripple current does not provide any information about SOC, capacity, or SOH.

You ought to look at your inverter's current draw with your oscilloscope if only to rule put the ripple issue .

However - all that said

Yours is not the only inverter of its type out there. Were this an inverter issue the brand would have a reputation as a "Battery Killer".
Which leads me to think it's a battery issue.

Where did you get your batteries?
BernieM said:
They are not recycled batteries. They came out of a 12v solar power system that someone was upgrading and were 1 year old when I got them. I tested them all and they all tested about the same on a load tester. They are two different brands but have the same specifications.
http://www.cres.gr/kape/publications/photovol/batt-bar.pdf
A techno-economical analysis showed that the use of vehicle batteries should be avoided in PV applications.
Daily cycling of two SLI batteries resulted in more than 70% capacity loss after 160 cycles.
Are yours deep cycle or plain old starting(SLI) batteries?

I don't know what's going on. That's all i can think of to check.

Let us know what your autopsy on a battery finds ?
Photos always help. Might be a battery guru in the house.

old jim
 
Last edited:
  • #34
BernieM said:
...
I guess it's time to cut a few batteries open.
You might want to google the hazards of working with sulfuric acid first.
 
  • #35
OmCheeto said:
At 50%, a 2 year lifespan is standard for flooded lead acid.
BernieM said:
If one keeps depth of discharge less than 50%, one should be able to nearly double the life span. The life span of a battery is considered to be the number of full discharge cycles the battery can tolerate without failing. So a 50% discharge would take 2 discharges to that depth to equal one complete discharge. This is how I run my setup, I do not allow it ever to get below 50% (24v.)
That's good...
Never below 70% charged (30%discharged) might be better ?

http://pvcdrom.pveducation.org/BATTERY/charlead.htm
image032.gif

Relationship between battery capacity, depth of discharge and cycle life for a shallow-cycle battery.

Have you said whether yours are shallow cycle or deep ?
How deep did previous owner cycle them ?
 

Similar threads

  • Electrical Engineering
Replies
11
Views
386
  • Electrical Engineering
Replies
10
Views
951
  • Electrical Engineering
Replies
3
Views
608
Replies
8
Views
1K
  • Electrical Engineering
Replies
7
Views
1K
Replies
8
Views
1K
Replies
28
Views
3K
  • Electrical Engineering
Replies
17
Views
1K
  • Electrical Engineering
Replies
3
Views
1K
Replies
5
Views
1K
Back
Top