I've been looking at the level measurement data from the Fukushima plants during the accident, and wondering if the somewhat suspicious behaviour is due to clogging of the impulse tubes ore some other malfunction, or if the measurement is arranged in such a way that it does not measure the core level in this kind of situation.
Being only familiar with the ASEA BWRs with the internal recirculation pumps, I've been looking at the GE documentation on the jet pump type BWR:s ( http://www4.ncsu.edu/~doster/NE405/Manuals/BWR6GeneralDescription.pdf ) trying to comprehend how the level measurement system works in these reactors. However, no information on that particular detail is given in that (otherwise wonderful) documentation.
Is there someone who could help an ignoramus by sharing the following information:
If my thinking is correct, the location of the lower impulse pipe (above or below the core shroud shelf) determines whether the level to be measured is the actual core level (=the level inside the shroud) or the level in the annular region between the diffuser pipes. This should make no difference as long as the level is above the top of the diffuser pipes (which is the state the plant is supposed to be in), but if the level falls below the top of the diffuser pipe, then it is important to know which level we are actually seeing in the measurement results.
Being only familiar with the ASEA BWRs with the internal recirculation pumps, I've been looking at the GE documentation on the jet pump type BWR:s ( http://www4.ncsu.edu/~doster/NE405/Manuals/BWR6GeneralDescription.pdf ) trying to comprehend how the level measurement system works in these reactors. However, no information on that particular detail is given in that (otherwise wonderful) documentation.
Is there someone who could help an ignoramus by sharing the following information:
- Is the level measurement based on impulse pipe-type pressure transmitters and a pressure sensor?
- If so, is the location of the lower impulse pipe above or below the core shroud support shelf?
If my thinking is correct, the location of the lower impulse pipe (above or below the core shroud shelf) determines whether the level to be measured is the actual core level (=the level inside the shroud) or the level in the annular region between the diffuser pipes. This should make no difference as long as the level is above the top of the diffuser pipes (which is the state the plant is supposed to be in), but if the level falls below the top of the diffuser pipe, then it is important to know which level we are actually seeing in the measurement results.