Good morning Gentlemen (and Ladies),
I'm looking for some help from you HV experts out there.
I have had an event where it is believed that a flooded transformer connection box induced a fault on to a 33kV 3phase transmission line, and the fault current was enough for the repulsive forces generated were enough to twist the 3 lines together.
The initial event was for 2 cycles (50hz) and did not cause protection to trip.
The fault current induces was capures on a trace and lasted 300mS, showing phases A & B initial contact and phase C approx 180mS into the event.
Criteria:
Now we have spent the last couple of days doing calcs based on every theory and formulae we can think of, and have results that range form induced forces of 30kg/m2 to over 1300N per linear meter.
My gut feeling says that this isn't enough force over a 300mS period to cause this to happen, but I need to prove it - one way or another
And none of us have ever heard of this type of event ever occurring in the real world (although we could find evidence of very heavy duty DC cables in an arc furnace snaking on the floor and having to be tied down).
So what I'm asking is:
Has anyone out there ever experienced this phenomenon?
Do you have any reports / evidence / pics / etc?
Can anyone provide a definate answer to the induced forces? And provde the maths behind it... :)
I can post pics if I can work out how, but I am happy to send to anyone who asks.
Thanks in advance.
Shane
I'm looking for some help from you HV experts out there.
I have had an event where it is believed that a flooded transformer connection box induced a fault on to a 33kV 3phase transmission line, and the fault current was enough for the repulsive forces generated were enough to twist the 3 lines together.
The initial event was for 2 cycles (50hz) and did not cause protection to trip.
The fault current induces was capures on a trace and lasted 300mS, showing phases A & B initial contact and phase C approx 180mS into the event.
Criteria:
- 33kV 3 phase no neutral
- Fault current - measured at approx 10kA per phase
- Initial fault - across all 3 phases 1.5 - 2 cycles
- Secondary fault - approx 180mS between A & B and C joined in for a further 120mS before trip
- Duration between fault 1 and 2 - 1.7 seconds
- Conductors: approx 100 meters in length (over 2 spans - 1 centre pole - centre pole is around a bend and the line translates from horizontal to vertical to horizontal at this centre pole), 16mm steel core aluminium, ACB at each end.
- Weather - Cold (12 deg C), Medium rain, Minimal wind
- No other external influences in the lines can be discovered.
Now we have spent the last couple of days doing calcs based on every theory and formulae we can think of, and have results that range form induced forces of 30kg/m2 to over 1300N per linear meter.
My gut feeling says that this isn't enough force over a 300mS period to cause this to happen, but I need to prove it - one way or another
And none of us have ever heard of this type of event ever occurring in the real world (although we could find evidence of very heavy duty DC cables in an arc furnace snaking on the floor and having to be tied down).
So what I'm asking is:
Has anyone out there ever experienced this phenomenon?
Do you have any reports / evidence / pics / etc?
Can anyone provide a definate answer to the induced forces? And provde the maths behind it... :)
I can post pics if I can work out how, but I am happy to send to anyone who asks.
Thanks in advance.