3x230V grids without neutral -- What countries use it?

  • Thread starter Merlion
  • Start date
  • Tags
    Neutral
In summary: That's roughly equivalent to a 10kV line. Somebody has to come and fix it ASAP. It's called an IT-system. That also means that high impedance grounding must exist at the supply side either via one leg of the transformer or an artificial neutral point.In summary, Norway has a three-phase grid with a ground connection at the center of the delta. There is no need for RCDs because the grid is grounded at the transformer. The center wire is live and the other two are live-neutral.
  • #1
Merlion
9
1
Does anybody here happen to know which countries have 3x230V grids without neutral. I know that this exists in some areas in France and Belgium. Was told Norway as well, not sure? Any other?

Thanks
 
Engineering news on Phys.org
  • #2
Try a google search for:
3 phase supply voltage by country
 
  • #3
Norway is correct, but the power companies are starting to introduce 4-lead distribution, also called 400V distribution (the classic 3x230V is a delta connection, the 4-lead is a star distribution).
 
  • #4
Svein said:
(the classic 3x230V is a delta connection).
I presume you have RCDs in Norway. Does that mean that 1 leg is connected to ground?
 
  • #5
Merlion said:
I presume you have RCDs in Norway. Does that mean that 1 leg is connected to ground?
No. Check out https://en.wikipedia.org/wiki/Three-phase_electric_power. The article contains a drawing:
220px-The_basic_3-phase_configurations.svg.png

And a short notice: "There are two basic three-phase configurations: wye (Y) and delta (Δ). As shown in the diagram, a delta configuration requires only 3 wires for transmission but a wye (star) configuration may utilise a fourth wire. The fourth wire, if present, is provided as a neutral and is normally grounded. The "3-wire" and "4-wire" designations do not count the ground wire used above many transmission lines, which is solely for fault protection and does not carry current under non-fault conditions."
 
  • #6
That surprises me. Seems extremely dangerous to me as these lines float with respect to ground, meaning they can be at any potential including a leak, capacitive or inductive coupling from a 10kV primary for example. Furthermore RCDs are no longer functional in such configuration.
 
  • #7
  1. The center of the delta is grounded at the local supply transformer (5kV-230V).
  2. Every house must provide a local safety ground connection. It is not connected to any of the supply wires.
  3. Both wires are considered "live".
  4. I do not know exactly what an RCD does, but from about the year 2000, every fuse in the fuse cabinet must include a Ground Fault Interrupter circuit. A GFCI works by measuring the current leaving one side of a power source (the so-called "live" or "hot wire"), and comparing it to current returning on the other (the "neutral" side). (cited from https://simple.wikipedia.org/wiki/GFCI). Thus, the potential on the wires relative to ground is completely irrelevant.
 
  • #8
There's some "inconsistencies" here.

1. Delta windings don't have a center, that's the nature of the problem
2. That's the case in most parts of the world but has only meaning if the supply side is grounded as well. A return path via the Earth must exist for earthing to be functional
3. Understandably
4. Aaah, you make use of a GFCI. Difference with a RCD is that the latter trips in case of a ground failure. A GFCI only tells you the problem is there. Someone has to come and fix it ASAP. It's called an IT-system. That also means that high impedance grounding must exist at the supply side either via one leg of the transformer or an artificial neutral point.

Interesting to know. Finland is probably is probably the only part of the world where this is used in the public sphere other than hospitals. Got to visit that place :-)
 
  • #9
Merlion said:
Delta windings don't have a center, that's the nature of the problem
Yes, but the supply transformers do not have to be in a delta configuration in order to supply three-phase delta. They may just as well be in a wye configuration and then it is easy to ground the center.
Merlion said:
A GFCI only tells you the problem is there.
Well, it trips when the imbalance is >15mA (or 10mA, I do not recollect).
 

FAQ: 3x230V grids without neutral -- What countries use it?

1. What is a "3x230V grid without neutral"?

A 3x230V grid without neutral is an electrical power system that operates with three phases and a voltage of 230 volts, but does not have a neutral connection. This means that there are three power lines, each carrying 230 volts, but there is no fourth neutral line.

2. How does a "3x230V grid without neutral" differ from a traditional power grid?

A traditional power grid has three phases and a neutral line, whereas a 3x230V grid without neutral does not have a neutral line. This can affect the way the electrical system is grounded and the way that electricity is distributed.

3. Which countries use a "3x230V grid without neutral"?

This type of power grid is commonly used in European countries such as Germany, France, and Italy. It is also used in some parts of Asia, such as Japan and South Korea.

4. Why do some countries use a "3x230V grid without neutral"?

This type of power grid is used in countries that have a history of using 3-phase power systems without a neutral connection. It is also commonly used in countries where the grid was built before the concept of a neutral connection was introduced.

5. Are there any advantages to using a "3x230V grid without neutral"?

One advantage is that it can be more cost-effective to build and maintain a 3x230V grid without neutral compared to a traditional power grid. It can also be more reliable in areas with a lot of lightning strikes, as there is no neutral line to attract lightning. However, it may not be as safe as a traditional power grid as there is no neutral line to help balance the load and protect against voltage fluctuations.