50Hz and 60Hz supply neutral line question

In summary, the circuit is OK, but the resolution is too low to be sure. The bit that counts is in that box on the left. It could have a label "In here, a miracle occurs" or it could be a sophisticated switch mode inverter.
  • #1
petefa
3
1
TL;DR Summary
inverter and transformers
Hi,

I have a question, I think the answer is no you can't do it, but I want to know why.

First mains supply - 3phase N + E (50hz)
Connected to this first supply is an inverter that gives out a 3 phase 415vac @60hz (no neutral) second supply.
The 60hz inverter output feeds 3 independent tapped transformers connected to the neutral of the first supply (50hz).

What would happen with one end of these transformer winding connected to second supply (60hz) with the other end of the transformer winding connect to the 50hz first supply neutral?Thanks
Pete
 
Engineering news on Phys.org
  • #2
You blow all of the fuses and/or shut the inverter down. You can't connect AC power distribution if the frequencies don't match exactly. Although I might be misunderstanding you circuit. Always draw a schematic (and show it to us for the best answers). I think you'll see a transformer winding at 60Hz in parallel with a transformer winding driven at 50Hz, which means the voltages will be out of phase and draw lots of current.
 
  • Like
Likes petefa
  • #3
@petefa , what specifically are you trying to accomplish? There may be a non-dangerous way to accomplish it.
 
  • #4
Hi,
Thank you all for getting back to me.
This is what is being proposed.
 

Attachments

  • inverter.PNG
    inverter.PNG
    9.6 KB · Views: 178
  • #5
The N and PE input are common to the entire system.
3PH+N+PE 50 Hz feeds a VFD that produces 415 V 3PH 60 Hz.
The 3PH output at 60 Hz drives the taps on three separate auto transformers, that are referenced to the common N. The three transformers provide the 3PH 60Hz output.

I see no immediate problem.
 
  • Like
Likes DaveE and sophiecentaur
  • #6
DaveE said:
You can't connect AC power distribution if the frequencies don't match exactly.
It all depends what you stick in between them. A DC link is not uncommon where phases of the systems each end can't be relied on so a change of frequency is not out of the question, albeit possibly a bit more complicated.
petefa said:
Hi,
Thank you all for getting back to me.
This is what is being proposed.
From what I can see the circuit look OK but the resolution is too low to be sure.
However, t he bit that counts is in that box on the left. It could have a label "In here, a miracle occurs" or it could be a sophisticated switch mode inverter. There's no reason why the appropriate sides of the three 60Hz phases shouldn't be connected to Earth or a common conductor called Neutral and give a 60Hz 3phase output. That neutral can happily be connected to the Earth / Neutral of the incoming Power supply. Why not? Just don't try to connect any two of the other six terminals together!
 
  • #7
No. I mean what is your application? I do not mean what is your solution.

Is there a 60 Hz device you want to use in a 50 Hz country? If yes, then please provide some details. What kind of device? How much power?
 
  • #8
sophiecentaur said:
It all depends what you stick in between them.
LOL, OK, the less common interpretation of connected. Yup, you can put stuff between AC sources.
 
  • #9
anorlunda said:
No. I mean what is your application? I do not mean what is your solution.

Is there a 60 Hz device you want to use in a 50 Hz country? If yes, then please provide some details. What kind of device? How much power?
Hi,
It's a UK testing supply to connect 10.5kw 208v 60hz water heating machines to. it's mainly resistive, (heaters) with a control circuit and control solenoids. Switched mode PSU, all components rated 50-60hz.

I wanted to know if you could mix the 50hz and 60hz supplies on the neutral line, as it's an inverter suppling the second supply.

Could there be interference as the inverter output isn't a true sine wave?
I think we will need a sine former or a reactor.
 
  • #10
petefa said:
I wanted to know if you could mix the 50hz and 60hz supplies on the neutral line, as it's an inverter suppling the second supply.
There is no problem having a common neutral for the 50 Hz and 60 Hz parts.
All protective Earth's are connected together. All neutrals are connected together. You make no connection between PE and N, that is done in the meter box.
You do not need the three transformers if you use a 3PH Variable Frequency Drive as the inverter. The VFD will have a neutral output terminal, and you can program the VFD to produce 208 volt at 60 Hz, or anything else in that ballpark you might want. With a resistive load the VFD will produce three sinewaves with regulated voltages, largely independent of the input.
 
  • Like
  • Informative
Likes berkeman and petefa

FAQ: 50Hz and 60Hz supply neutral line question

What is the difference between 50Hz and 60Hz supply?

The main difference between 50Hz and 60Hz supply is the frequency at which the alternating current (AC) flows. 50Hz supply has a frequency of 50 cycles per second, while 60Hz supply has a frequency of 60 cycles per second. This difference in frequency affects the performance and efficiency of electrical devices.

Why do some countries use 50Hz supply while others use 60Hz supply?

The choice of using 50Hz or 60Hz supply is based on historical and economic reasons. In the early development of electricity, different regions and countries adopted different standards for their power grids. Some countries have stuck with their original standard, while others have switched to a different frequency for various reasons.

How does the neutral line play a role in 50Hz and 60Hz supply?

The neutral line is an important part of an electrical circuit as it provides a return path for the current to flow back to the source. In 50Hz and 60Hz supply, the neutral line is the reference point for the alternating current to flow. It is connected to the ground to ensure the safety of the electrical system and prevent electric shocks.

Can devices designed for 50Hz supply be used in a 60Hz supply and vice versa?

In most cases, devices designed for 50Hz supply can be used in a 60Hz supply and vice versa. However, there may be some differences in the performance and efficiency of the device. It is important to check the device's specifications to ensure it is compatible with the frequency of the power supply.

How does the frequency of the power supply affect the operation of electrical devices?

The frequency of the power supply can affect the operation of electrical devices in various ways. For example, devices designed for 50Hz supply may run at a slower speed in a 60Hz supply, and vice versa. It can also affect the heating and cooling of devices, as well as the efficiency of motors and other electrical equipment.