Active power of three-phase system

In summary, the homework statement is to find the active power of a three-phase system. The equivalent impedance and active power for each resistor is found by reducing the circuit to one phase.
  • #1
gruba
206
1

Homework Statement


Find active power of the given three-phase system.
[itex]U_{RS}=U_{ST}=U_{TR}=220\sqrt 3 V[/itex]
[itex]R=\omega L=\frac{1}{\omega C}=10\Omega[/itex]

2. The attempt at a solution
After reducing the circuit to one phase (see attachments), equivalent impedance is [itex]\underline{Z_e}=\sqrt{101}e^{-j84,3^{o}}[/itex].

[tex]U_{RS}=U_{ST}=U_{TR}=U_{L}=\sqrt{3}U_R\Rightarrow U_R=220 V\Rightarrow \underline{U_R}=220e^{-j\pi/3}\Rightarrow \underline{I_R}=\frac{220}{\sqrt{101}}e^{j54,3^{o}}[/tex]

Active power of each resistor is given by

[tex]P_1=P_2=P_3=\mathfrak{R}(\underline{U_L}\underline{I_R^{*}})=\sqrt 3 U_RI_R\cos\angle(\underline{U_L}\underline{I_R})\Rightarrow P=3P_1[/tex]

[tex]\cos\angle(\underline{U_L}\underline{I_R})\approx 0.099\Rightarrow P_1\approx 825.88 W\Rightarrow P=2477.64W[/tex]

Is this correct?
 

Attachments

  • circuit.PNG
    circuit.PNG
    1.5 KB · Views: 456
  • circuit_2.PNG
    circuit_2.PNG
    930 bytes · Views: 499
Physics news on Phys.org
  • #2
Can you show your calculations for the equivalent impedance?
 
  • #3
gneill said:
Can you show your calculations for the equivalent impedance?

From circuit_2, [itex]\underline{Z_e}=X_C+(\frac{R}{3} || X_L)[/itex] where [itex]X_C=-j\frac{1}{\omega C},X_L=j\omega L[/itex].

[tex]\underline{Z_e}=3-j9[/tex]

I think this is the correct impedance.

Question: Expect calculations, are the equations for powers, impedance, voltage and current in my original post set correctly?
 
Last edited:
  • #4
ATTEMPT EDITED (errors in calculation):

After reducing the circuit to one phase (see attachment):Equivalent impedance is [itex]\underline{Z_e}=X_C+(R/3 || X_L)=-j10+(3+j)=3-j9[/itex]
[tex]U_{RS}=U_{ST}=U_{TR}=U_L=\sqrt{3}U_R\Rightarrow \underline{U_R}=220e^{-j\pi/6}\Rightarrow \underline{I_R}=\sqrt{90}e^{-j71.56^{o}}[/tex]

Active power of each resistor is given by:
[tex]P_1=P_2=P_3=\mathfrak(\underline{U_R}\underline{I_R^{*}})=\sqrt{3}U_RI_R\cos\angle(\underline{U_L}\underline{I_R})[/tex]
[tex]\cos\angle(\underline{U_L}\underline{I_R})\approx 0.75\Rightarrow P_1=165\sqrt{270}W\Rightarrow P=3P_1=495\sqrt{270}W[/tex]

Question: Could someone check if equations are set correctly?
 
  • #5
Your equivalent impedance looks right now.

How did you determine the potential across the resistor? In your equivalent circuit the capacitor is in series with the parallel combination of the resistor and inductor. Note that, since in a perfectly symmetric Y configuration the branches are essentially independent, you can ignore the phase angle of the source for a given branch if you're just looking for the real power in its load. Thus you have:

upload_2016-4-4_8-10-16.png


I put the magnitude of the voltage across the resistor at about 73 V, so whatever method you use to find it should find something similar.
 
  • Like
Likes gruba
  • #6
How did you determine the potential across the resistor?

Why do we need voltage across the resistor?

Total active power is given by [tex]P=3P_1=3\sqrt{3}U_RI_R\cos\angle(\underline{U_L}\underline{I_R})[/tex]

To use this equation, we need to draw phase diagram and find [itex]\angle(\underline{U_L}\underline{I_R})[/itex] which is [itex]\approx 41.4^{o}[/itex].
 
  • #7
You don't necessarily need the voltage across the resistor. But it's a simple way to get to the power dissipated since P = V2/R. You should end up with a power (for one branch) of about 732/(10/3), or about 1600 W.

In your previous attempt you wrote: ## \underline{I_R}=\sqrt{90}e^{-j71.56^{o}}##, but that looks more like the branch impedance value than the branch current.
 
  • Like
Likes gruba
  • #8
In your previous attempt you wrote: ## \underline{I_R}=\sqrt{90}e^{-j71.56^{o}}##, but that looks more like the branch impedance value than the branch current.

You are right, it should be [itex]\underline{I_R}=\frac{220}{\sqrt{90}}e^{j41.56^{o}}[/itex].

But applying the formula [itex]P=3P_1=3\sqrt{3}U_RI_R\cos\angle(\underline{U_L},\underline{I_R})[/itex] doesn't give the result you get
(I think that your result is correct, just don't know why it is not the same using complex domain).
 
  • #9
It must have something to do with the definitions of, or values of, your variables. Let's try a slightly different approach and see how it works out (It's a good idea to be able to check your work using different methods).

If the branch source voltage is U = 220 V and the branch impedance is Z = (3 - j9) Ω, then the branch current is:

##I = \frac{U}{Z} = \frac{220}{3 - j9} = \left(\frac{22}{3} + j22 \right)~A##

Then the complex power is p = VI* , so that:

##p = (220~V) \left(\frac{22}{3} - j22 \right) ~A = \left( \frac{4840}{3} - j4840 \right)~ VA ##

The active power is the real component of the complex power, so P1 = 4840/3 W.

What values are you using for UR and IR?edit: Fixed typo in power calculation (current value).
 
Last edited:
  • Like
Likes gruba
  • #10
What values are you using for UR and IR?

I used [itex]U_R=220V,I_R=\frac{220}{\sqrt{90}},\cos\angle(\underline{U_L},\underline{I_R})=0.75[/itex].
 
  • #11
I have an idea of where your problem lies. I think you're applying a power formula for a Y-connected source with a Δ-connected load. That would explain the presence of the √3 before the voltage variable, converting the Y source voltage to a Δ line-to-line source.

In this case you've already combined the loads into a single Y-connected load, and the given line-to-line voltage to a Y-source of 220 V, so the formula won't apply. What you have is:

upload_2016-4-4_14-48-41.png
 
  • Like
Likes gruba
  • #12
Thanks for detailed explanations.
 

FAQ: Active power of three-phase system

1. What is the active power of a three-phase system?

The active power of a three-phase system is the real power that is consumed by the load and is converted into useful work such as mechanical energy or heat. It is measured in watts (W) and is denoted by the symbol P.

2. How is the active power calculated in a three-phase system?

The active power in a three-phase system can be calculated by multiplying the line voltage (V) by the line current (I) by the power factor (PF) and by the square root of three (√3), as shown in the formula: P = V x I x PF x √3. The unit for active power is watts (W).

3. What is the difference between active power and apparent power in a three-phase system?

Active power is the real power that is consumed by the load and is converted into useful work, while apparent power is the total power that is supplied to the load, including both real and reactive power. Apparent power is measured in volt-amperes (VA) and is denoted by the symbol S.

4. How does the power factor affect the active power in a three-phase system?

The power factor (PF) is a measure of how efficiently the load utilizes the supplied power. A higher power factor means that more of the supplied power is being converted into useful work, resulting in a higher active power. A lower power factor means that more of the supplied power is being wasted, resulting in a lower active power.

5. Why is it important to measure and maintain the active power in a three-phase system?

Measuring and maintaining the active power in a three-phase system is important because it allows for efficient use of power and helps to prevent wastage. This can result in cost savings for the consumer and also helps to reduce the strain on the power grid. Additionally, a balanced and stable active power can help to increase the lifespan of electrical equipment and prevent power outages.

Similar threads

Replies
6
Views
2K
Replies
33
Views
3K
Replies
2
Views
2K
Replies
2
Views
1K
Replies
4
Views
1K
Replies
2
Views
5K
Back
Top