Lil background that may support the best answer to my question.
I'm a plant manager for a small landfill gas power generation facility 3.6MW, 2ea RICE CAT 3520'S, which are paralleled to the grid. I believe my site is experiencing utility power quality issues that are effecting genset stability. Some known facts is the site is at the end of the utility distribution line in a rural area. The bus or utility frequency seems to deviate even with the genset offline more than other sites I operated in the past, for example 59.97-60.3ish, I'm not so sure if this swing is acceptable or not, and this swing moves relative fast - within minutes.
Also when the site gensets load increases the generator/line voltage increases, our generators are 4160v with a step up transformer to line voltage of 12480v, generator voltage increases up to 200-250v from nominal start voltage most of the time. Reactive Power also seems to erratic at times, we run a PF .99 and put out about 250vars from each genset.
My background is mechanical so before I start making phone calls to our power purchasers (utility company) I like to have the decent knowledge on what might be contributing this issues, and not sound like a complete idiot. We have multiple devices monitoring our generator and line power quality and I'm seeing the same issues, so its highly unlikely its instrumentation. We also recently load banked our gensets to see the gensets stability and no anomalies were found. Because the gensets are unstable at load we are experiencing cylinder detonation due to unusual loading and unloading of engine.
I have exhausted all my tricks with tuning the switchgear VAR/load PID loops along with engine governor system and generator voltage regulator gain settings, and unfortunately the local CAT techs have less technical knowledge in this department then I do.lol
Any insight will be greatly appreciated
I'm a plant manager for a small landfill gas power generation facility 3.6MW, 2ea RICE CAT 3520'S, which are paralleled to the grid. I believe my site is experiencing utility power quality issues that are effecting genset stability. Some known facts is the site is at the end of the utility distribution line in a rural area. The bus or utility frequency seems to deviate even with the genset offline more than other sites I operated in the past, for example 59.97-60.3ish, I'm not so sure if this swing is acceptable or not, and this swing moves relative fast - within minutes.
Also when the site gensets load increases the generator/line voltage increases, our generators are 4160v with a step up transformer to line voltage of 12480v, generator voltage increases up to 200-250v from nominal start voltage most of the time. Reactive Power also seems to erratic at times, we run a PF .99 and put out about 250vars from each genset.
My background is mechanical so before I start making phone calls to our power purchasers (utility company) I like to have the decent knowledge on what might be contributing this issues, and not sound like a complete idiot. We have multiple devices monitoring our generator and line power quality and I'm seeing the same issues, so its highly unlikely its instrumentation. We also recently load banked our gensets to see the gensets stability and no anomalies were found. Because the gensets are unstable at load we are experiencing cylinder detonation due to unusual loading and unloading of engine.
I have exhausted all my tricks with tuning the switchgear VAR/load PID loops along with engine governor system and generator voltage regulator gain settings, and unfortunately the local CAT techs have less technical knowledge in this department then I do.lol
Any insight will be greatly appreciated