Calculate KVA Rating for 12kW Load at 0.8 Lag

In summary, the conversation is about determining the kva rating of an alternator required to drive a 12kw load with a power factor of 0.8 lag. The formula for apparent power is used to calculate the kva rating, which is found to be 15kva. The question is then specified to be a multiple choice question with the correct answer being 15kw, as per the trigonometric reasoning behind the 'power triangle'.
  • #1
tobiascarter
5
0
Hi there,

Can some one assist me as to how to answer this question...

An alternator is connected to a 12kw load and operating at a power factor of 0.8 lag. what is the kva rating of the alternator required to drive the load?

i don't know what formula to use so Any help would be great. cheers
------------------------------
 
Physics news on Phys.org
  • #2
What limits the power output of your alternator?
 
  • #3
it doesn't say? this is why i don't understand? is it asking what the apparent power value is? if so...
Apparent pwr= true power/ power factor

is true power 12kw?
if so...

12000/0.8= 15000va
=15kva

does that seem right?
 
  • #4
You've been givena 'trick' quesiotn. The limiting factor in a simple alternator is the current. Current generates heat. Heat causes things to fail. How does the current change with the power factor for a linear load? When the load is linear the current and voltage are still sinusoidal.
 
  • #5
thanks for the responses, but the last one lost me. I am very ammature when it comes to this stuff.

Its actually a multiple choice question with the answers being...
a)15kw
b)apparent power
c)2w
d)3000w
e)11000va

my guess is apparent power. and i think (a) is there to trick you, as the above calculation comes to 15kva

what do you think?

thanks again
 
  • #6
Sorry to throw you in the wrong direction. 15kw is correct.
 
  • #7
If you can remember trigonometry, that is the reasoning behind maths that applies here, as per the 'power triangle' (attached).
 

Attachments

  • Power Triangle.JPG
    Power Triangle.JPG
    10.5 KB · Views: 496

FAQ: Calculate KVA Rating for 12kW Load at 0.8 Lag

What is a KVA rating?

A KVA (kilovolt-ampere) rating is a unit used to measure the apparent power of an electrical system. It takes into account both the voltage and current of the system, rather than just the current as in the case of watts.

How is the KVA rating calculated?

The KVA rating can be calculated by multiplying the voltage (in kilovolts) by the current (in amperes) of the system. This calculation takes into account both the real power (measured in watts) and the reactive power (measured in volt-amperes reactive) of the system.

What is the significance of a 0.8 lag for a load?

A 0.8 lag refers to the power factor of a load, which is a measure of how efficiently the electrical energy is being used. A power factor of 0.8 lag means that the load is using 80% of the available energy for useful work, with the remaining 20% being lost as reactive power.

How does a 12kW load affect the KVA rating?

Since the KVA rating takes into account both the real power and reactive power of a system, a 12kW load at 0.8 lag will have a higher KVA rating compared to a 12kW load at unity power factor (where all the energy is used for useful work). This is because the reactive power component also needs to be accounted for in the KVA calculation.

Why is it important to calculate the KVA rating for a load?

Knowing the KVA rating of a load is important for determining the capacity and sizing of electrical equipment such as transformers, generators, and circuit breakers. It also helps in understanding the overall efficiency of the system and identifying areas for improvement in power factor correction.

Back
Top