Calculate Phase Voltage On Unbalanced Load if Neutral Disconnected

In summary, the neutral wire in a star-connected system becomes disconnected and the voltage between the star points and neutral wire is unknown.
  • #1
blueboxcat
3
0

Homework Statement


An Unbalanced 3-phase star connected load has the details as below.
Line Voltage=400V
Voltage R-N = 230V 0°
Voltage B-N = 230V +120°
Voltage W-N= 230V -120°

Impedance R-N = 100+J36
Impedance B-N = 102+J0
Impedance W-N = 50+J0


A.) Determine the neutral current(im confident in this)

B.) Determine the voltage between the star point and neutral wire if the neutral wire(Vn-o) becomes disconnected. (Im not sure how to do this)



Homework Equations





The Attempt at a Solution


I calculated neutral current.

converted all impedances to polar to calculate current

Ir=Vph/Zr=230V 0° / 106.28ohm 19.8° = 2.1641A -19.8°
Ib=230V 120° / 102ohm 0° = 2.25A 120°
Ic=230V 240° / 50ohm 240° = 4.6A 240°

Converted these to Rectangular hen Added them together to determine neutral current

Ir=2.16A -19.8°=2.0361-J0.733
Ib=2.25A 120° =-1.125+J1.95
Iy=4.60A 240° =-2.3-J3.98

(2.0361-J0.733)+(-1.125+J1.95)+(-2.3-J3.98) = -1.3889-J2.7631 = 3.09A -116.69°

Now i do not know how to approach question b.) Determine the voltage between the star point and neutral wire if the neutral wire(Vn-o) becomes disconnected.
 
Physics news on Phys.org
  • #2
blueboxcat said:
Now i do not know how to approach question b.) Determine the voltage between the star point and neutral wire if the neutral wire(Vn-o) becomes disconnected.
Draw the schematic without the neutral wire. If you take the junction of the voltage sources as the reference node (Neutral), there's one other node and it happens to be the one you're interested in. Write the nodal equation and solve for the potential of that node.
 
  • #3
Im having trouble understanding your explanation, if i make the star point the reference node, where is this other node? are you able to demonstrate to me how to solve it?
 
Last edited:
  • #4
blueboxcat said:
Im having trouble understanding your explanation, if i make the star point the reference node, where is this other node? are you able to demonstrate to me how to solve it?
Sorry, we can't provide solutions to homework, only help, hints, clarifications, etc.

You have star-connected sources and star-connected loads. In the 4-wire system the Neutral wire joins the node where the sources come together to the node where the loads come together. Here you are asked to remove that Neutral wire and determine the potential difference between these now separate nodes. Looks like an ideal case for nodal analysis.

Here's your circuit with the neutral wire still in place:
attachment.php?attachmentid=58527&stc=1&d=1367841201.gif
 

Attachments

  • Fig1.gif
    Fig1.gif
    3.6 KB · Views: 2,561
  • #5
Hey, I am not confident in node voltage analysis as I am only in my first month of power engineering. Though i do intend to look into it. I found a similar problem in a book at the library and found the solution, are you able to confirm if this is correct or not?

Vn-o= ((Vr x Yr)+(Vy x Yy)+(Vb x Yb)) / (Yr + Yy + Yb)

Yr = 1/100+j36 = 1/106.28 , 19.8° = 9.41 , -19.8°
Yb = 1/102+J0 = 1/102, 0° = 0.009804 , 0°
Yw = 1/50+ J0 = 1/50 , 0° = 0.02 , 0°

Vn-o = ((230 , 0° x 9.41 , -19.8) + (230 , -120° x 0.02) + (230 , 120° x 0.009804 , 0°)) / ((8.85-J3.19)+(0.009804) + (.02)

Vn-o = (2161.7652 , -19.88°) / (9.4356 , -19.76)

Vn-o = 229.11V -12°

Im doubting whether my answer is correct because it is incredibly close to the supply phase voltage(230v) . But I am thinking this could also be a coincidence. Are you able to tell me if I am wrong and if so, where i have went wrong? Thank you
 
  • #6
blueboxcat said:
Hey, I am not confident in node voltage analysis as I am only in my first month of power engineering. Though i do intend to look into it. I found a similar problem in a book at the library and found the solution, are you able to confirm if this is correct or not?

Vn-o= ((Vr x Yr)+(Vy x Yy)+(Vb x Yb)) / (Yr + Yy + Yb)
The above formula is correct. Do you understand where it comes from (how to derive it)? You won't have the library at your disposal at exam time...
Yr = 1/100+j36 = 1/106.28 , 19.8° = 9.41 , -19.8°
Yb = 1/102+J0 = 1/102, 0° = 0.009804 , 0°
Yw = 1/50+ J0 = 1/50 , 0° = 0.02 , 0°
Recheck the value I've indicated in red; Looks waaay too big.
Vn-o = ((230 , 0° x 9.41 , -19.8) + (230 , -120° x 0.02) + (230 , 120° x 0.009804 , 0°)) / ((8.85-J3.19)+(0.009804) + (.02)

Vn-o = (2161.7652 , -19.88°) / (9.4356 , -19.76)

Vn-o = 229.11V -12°

Im doubting whether my answer is correct because it is incredibly close to the supply phase voltage(230v) . But I am thinking this could also be a coincidence. Are you able to tell me if I am wrong and if so, where i have went wrong? Thank you
Fix the value I've indicated and redo your math. The result should be less than 100V.

I'd suggest looking up and reviewing the nodal analysis technique. It's usefulness will come up again and again in electrical systems.
 

FAQ: Calculate Phase Voltage On Unbalanced Load if Neutral Disconnected

1. How do I calculate phase voltage on an unbalanced load if the neutral is disconnected?

In order to calculate the phase voltage on an unbalanced load, you will need to use the formula V = IR, where V is the voltage, I is the current, and R is the resistance. In an unbalanced load, the current and resistance will vary between the different phases. You will need to measure the current and resistance for each phase and plug those values into the formula to calculate the phase voltage for each phase.

2. Why is it important to calculate phase voltage on an unbalanced load?

Calculating phase voltage on an unbalanced load is important because it helps to determine the voltage drop and power loss in each phase. This information is crucial for maintaining the stability and efficiency of the electrical system.

3. What are the potential consequences of not calculating phase voltage on an unbalanced load?

If phase voltage on an unbalanced load is not properly calculated, it can lead to unequal distribution of power and voltage drops in different phases. This can cause damage to electrical equipment and may result in power outages or other electrical failures.

4. What factors can cause an unbalanced load?

An unbalanced load can be caused by a variety of factors, such as unequal distribution of electrical loads, faulty wiring or connections, or a malfunctioning electrical device. It can also be caused by power surges or fluctuations in the electrical supply.

5. How can I prevent an unbalanced load and the need to calculate phase voltage?

To prevent an unbalanced load, it is important to properly distribute electrical loads across different phases and regularly check for any faulty wiring or connections. Installing voltage regulators or using power factor correction techniques can also help to prevent an unbalanced load. However, it is always important to monitor and calculate phase voltage on an unbalanced load to ensure the stability and efficiency of the electrical system.

Back
Top