Calculating 208V Power: 3 Methods Explained

  • Thread starter trikkydik
  • Start date
  • Tags
    Power
In summary: It was replaced by 3 phase power in the early 20th century.In summary, the conversation discusses the calculation of power for a 208V/30A 2 pole breaker with 10A being fed to each phase. Three methods are mentioned, with method 1 being the correct way to calculate power for single phase systems. The conversation also touches on the topic of two phase systems, with some confusion over whether they exist or not. It is ultimately determined that two phase systems were used in the past but have been replaced by three phase systems in modern times.
  • #1
trikkydik
4
1
Need some help here, as things get a little blurry with the phase angles and everything.
But here's my question:

I have a 208V/30A 2 pole breaker, feeding 10A to each phase. i need to calculate power.
I have 3 methods and need to know which one is correct.

1.) 208V x 10A = 2080 Watts (total power used by both phases)

2.) (208V x 10A) for 1 phase + (208V x 10A) for the other phase = 4160 Watts for both phases

3.) (120V x 10A) for 1 phase + (120V x 10A) for the other phase = 2400 Watts for both phasesOMIT POWER FACTOR AND ANYTHING ELSE PLEASE. I would like to eliminate confusion, because coefficients are easy to understand. and please just answer my question directly.
 
Engineering news on Phys.org
  • #2
You have either a single phase system (2 wires) or a three phase system (3 wires). There is no such thing as a two phase system.

Method 1 is the way to calculate power for single phase systems.
 
  • Like
Likes russ_watters
  • #3
I was little confused by your statement "there is no such thing as a two phase system"

But i think i get what you mean. Even though the circuit has 2 hots, it is still considered single phase.

Is that correct?
 
  • #4
trikkydik said:
I was little confused by your statement "there is no such thing as a two phase system"

But i think i get what you mean. Even though the circuit has 2 hots, it is still considered single phase.

Is that correct?
Yes, that's correct.
 
  • #5
It depends. If you have a resistor across the 208 volt pair then it is 10 A x 208 V. But, you may have a resistor from each hot to ground. This is not the same on a 208 wye system which I suspect you have.
 
  • #6
Averagesupernova said:
It depends. If you have a resistor across the 208 volt pair then it is 10 A x 208 V. But, you may have a resistor from each hot to ground. This is not the same on a 208 wye system which I suspect you have.

Ay here we go again. Soon someone will mention neutral and cause @sophiec@hoophy to melt down. :oldsmile:
 
  • #7
anorlunda said:
Ay here we go again. Soon someone will mention neutral and cause @sophiec@hoophy to melt down. :oldsmile:
Good one! :smile:
 
  • #8
  • #9
D_Arsonval said:
I would be confused by a statement saying "...there is no such thing as a two phase system..." as well.

For I've worked on two phase electric motors in my past.

John

Google it for something to do: https://en.wikipedia.org/wiki/Two-phase_electric_power

True, but a motor is not a power distribution system.

The key idea is that the currents do not disappear. Current supplied by the source must be returned to the source. That is Kirchoff's Current Law applied to a system.

In a single phase system, we have two wires. Current comes from the source through one wire, and returns via a second wire. Two wires, one phase.

In a three phase system, the currents in the three phases are shifted 120 degrees relative to each other, so that when they are combined, the three add up to zero. Thus no return wire is needed. Three phases, three wires.

Clever people can invent hundreds of other combinations of wires and phase shifts and give them many names. (Earth returns excluded.) Here are just a handful of them.

1-Phase, 2-Wire 120 V with neutral 120 – US 3Y-208
1-Phase, 2-Wire 230 V with neutral 230 – EU, Others 3Y-400
1-Phase, 2-Wire 208 V (No neutral) – 208 US 3D-240
1-Phase, 2-Wire 240 V (No neutral) – 240 US 3D-240
1-Phase, 3-Wire 120/240 V 120 240 US 3Y-208
3-Phase, 3-Wire 208 V Delta (No neutral) – 208 US 3D-240
3-Phase, 3-Wire 230 V Delta (No neutral) – 230 Norway 3D-240
3-Phase, 3-Wire 400 V Delta (No neutral) – 400 EU, Others 3D-400
3-Phase, 3-Wire 480 V Delta (No neutral) – 480 US 3D-480
3-Phase, 3-Wire 600 V Delta (No neutral) – 600 US, Canada none1
3-Phase, 4-Wire 208Y/120 V 120 208 US 3Y-208, 3D-240
3-Phase, 4-Wire 400Y/230 V 230 400 EU, Others 3Y-400, 3D-400
3-Phase, 4-Wire 415Y/240 V 230 415 Australia 3Y-400, 3D-400
3-Phase, 4-Wire 480Y/277 V 277 480 US 3Y-480, 3D-480
3-Phase, 4-Wire 600Y/347 V 347 600 US, Canada 3Y-600
3-Phase 4-Wire Delta 120/208/240
Wild Phase 120,
208 240 US 3D-240
3-Phase 4-Wire Delta 240/415/480
Wild Phase 240,
415 480 US 3D-480
3-Phase Corner-rounded Delta 208/240 – 240 US 3D-240
3-Phase Corner-Grounded Delta 415/480 – 480 US 3D-480Some are called two phase, so in that respect you are correct But in the end, they must reduce to one of the two above. Either there is a wire for return current (sometimes called the neutral :oldsurprised: ), or the currents add to zero.

http://www.ccontrolsys.com/w/Two_Phase_Electrical_Service said:
Residential electric service in the United States (120/240 VAC) is sometimes called two-phase service but this is NOT correct. It is only single-phase, since both line voltages are derived from a single phase of a distribution transformer with a center tapped neutral and are 180° out of phase with each other.

Two-phase service is an obsolete style of electrical power distribution where two phases are provided that are 90° out of phase with each other. There were two line wires and one neutral, so two-phase service was commonly a two-phase three-wire service.

Another variation used four line wires and one neutral for a two-phase five-wire service. This was sometimes incorrectly called four-phase five-wire service.

We are not aware of any two-phase service still in use.
 
  • #10
Don't let anyone in the center of Philadelphia know their two phase system produced by the Scott T transformer connection doesn't exist.
They may become confused as well.

Always enjoying the forum.

John
 
  • #11
D_Arsonval said:
Don't let anyone in the center of Philadelphia know their two phase system produced by the Scott T transformer connection doesn't exist.
They may become confused as well.

Always enjoying the forum.

John

OK, if they're still using that, I must be wrong about two phase. The Scott T transformer was invented in 1890.
 
  • #12
2 phase has existed in the past and may well exist today but I cannot be sure. I never knew until a few years ago that there was such a thing as true 2 phase.
 
  • #13
The typical US residential service is often called "split phase".
 
  • #14
LOL this thread is so funny. I am glad i was able to stir up an old debate.

And thank you so much for everyone's inputs.
 
  • #15
trikkydik said:
Need some help here, as things get a little blurry with the phase angles and everything.
But here's my question:

I have a 208V/30A 2 pole breaker, feeding 10A to each phase. i need to calculate power.
I have 3 methods and need to know which one is correct.

1.) 208V x 10A = 2080 Watts (total power used by both phases)

2.) (208V x 10A) for 1 phase + (208V x 10A) for the other phase = 4160 Watts for both phases

3.) (120V x 10A) for 1 phase + (120V x 10A) for the other phase = 2400 Watts for both phasesOMIT POWER FACTOR AND ANYTHING ELSE PLEASE. I would like to eliminate confusion, because coefficients are easy to understand. and please just answer my question directly.
A question well stated is half answered
and yours falls just short of well stated.

What is that 208 volt breaker's feed coming from ? And what kind of a load is it connected to ?

If its feed comes from a residential type distribution transformer , which is 230 volt single phase centertapped,
and it's reading just 208 today instead of 230 for some reason you didn't tell us about ,
then the best answer from the three you proposed is (1) .
But
If it's fed from a 208/120 three phase distribution transformer , like they use for motels and such
where 208 volts is phase to phase voltage for big loads like airconditioners
and 120 volts is phase to neutral voltage for lights and receptacles,
then the best answer will depend on what the breaker feeds.
It will be either:
(1), if the breaker connects to 208 volt loads
or
(3), if the breaker connects to 120 volt loads.

(2) is out, barring something really weird...

So - is this a single phase panel where we'd expect to find not 208 volts but 230 ?
Or is is a 3 phase panel where we'd expect 208 volts ?

In other words,
Does all the current entering through one pole return through the other pole or is there a neutral you didn't mention ?
Had you said 230 volts not 208 i'd have assumed single phase residential...

Lastly, if you want to calculate power, you CANNOT omit power factor.
To get Watts, you must multiply the product Volts X Amps by Power Factor.

old jim
 

FAQ: Calculating 208V Power: 3 Methods Explained

1. What is the formula for calculating 208V power?

The formula for calculating 208V power is P = V x I, where P represents power in watts, V represents voltage in volts, and I represents current in amps.

2. What are the 3 methods for calculating 208V power?

The 3 methods for calculating 208V power are using the formula P = V x I, using the formula P = I^2 x R, and using the formula P = V^2 / R. These methods involve different variables and can be used depending on the information available.

3. Can the power be calculated if only voltage is known?

Yes, the power can still be calculated if only voltage is known. The formula to use in this case is P = V^2 / R, where R represents the resistance in ohms.

4. How does power change if current increases in a 208V circuit?

If the current increases in a 208V circuit, the power will also increase. This is because power is directly proportional to current, according to the formula P = V x I.

5. Is there a difference in calculating power for AC and DC circuits?

Yes, there is a difference in calculating power for AC and DC circuits. For AC circuits, the formula P = V x I x cos(θ) is used, where θ represents the phase angle between voltage and current. For DC circuits, the formula P = V x I can be used since there is no phase angle to consider.

Similar threads

Back
Top