Homework Statement
calculate the capacitive reactance/ph such that the load power factor
is increased to 0.98 lag
Relevant Equations
1/2πfC or 1/ωt
the full question is:
The following phase schematic diagram (FIGURE 4) shows an 11 kV, 50 Hz, 3-phase, short line feeding a load. By calculation or constructing the phasor diagram (use a scale of 1 mm = 2 A) for the load current with VR as reference, determine the capacitive current and
• calculate the capacitive reactance/ph such that the load power factor is increased to 0.98 lag
• calculate the percentage reduction in line current with this value of capacitive reactance in circuit.

So far i have got to:

p.f.=1.9/3.2=0.59
Il=(3.2*10^6)/(√3*11*10^3*0.59 )=284∟-53.8
=167.7-j229.2

unsure which way to go next..
 

Attachments

  • Untitled.jpg
    Untitled.jpg
    43.5 KB · Views: 260
Physics news on Phys.org
  • #2
Hi JE93,

JE93 said:
So far i have got to:

p.f.=1.9/3.2=0.59
Il=(3.2*10^6)/(√3*11*10^3*0.59 )=284∟-53.8
=167.7-j229.2
I'm not liking the power factor that you've found. Can you justify your calculation?'

Try starting with a power triangle diagram. Which sides of the triangle represent the power values that you are given?
 
  • #3
gneill said:
Hi JE93,I'm not liking the power factor that you've found. Can you justify your calculation?'

Try starting with a power triangle diagram. Which sides of the triangle represent the power values that you are given?

Hi Gneill.

I got the power factor from doing the real divided by the reactive power which, would be 1.9mva/3.2mw.

looking at a power triangle where Z (impedance) is the hypotenuse and X (reactance) is the opposite side,
X=Zsin θ, so would this be:

167.7-j229.2 sin 53.8
presuming the p.f. is correct.

Thanks
 
  • #4
JE93 said:
Hi Gneill.

I got the power factor from doing the real divided by the reactive power which, would be 1.9mva/3.2mw.

looking at a power triangle where Z (impedance) is the hypotenuse and X (reactance) is the opposite side,
X=Zsin θ, so would this be:

167.7-j229.2 sin 53.8
presuming the p.f. is correct.
That is incorrect! The power factor will be the cosine of the angle subtended by the real and reactive power legs on the power triangle.

A power triangle has sides that represent powers only; no impedances. So in this case:

1603486410780.png

Edit: Corrected Power value typo in diagram.
 
Last edited:
  • #5
gneill said:
That is incorrect! The power factor will be the cosine of the angle subtended by the real and reactive power legs on the power triangle.

A power triangle has sides that represent powers only; no impedances. So in this case:

https://www.physicsforums.com/attachments/271434

I have re done this now using the power triangle above.
I realize now that I used the MVAr rather than the MVA for calculating the p.f.
Now i have:

s=√(P^2+Q^2 ) = 3.2MVA
2.3MW/3.2MVA=0.72
〖cos〗^(-1) 0.72=43.9° = θ

Would I now put the correct power factor into the previous equation, so:

Il=(3.2*10^6)/(√3*11*10^3*0.72 )=233.3∟-43.9° = 168.1-j161.8
 
  • #6
Note that I've corrected a typo in the power triangle that I posted in #4. I had switched the digits in the real power value. Sorry about that. The new figure is repeated here:
1603488434921.png


I would suggest going first for question part (a), finding the capacitive reactance required to achieve a load power factor of 0.98 . You can work from the power triangle! Add in a line that represents the apparent power for the desired power factor. Something like:
1603488729483.png

so that ##Q_o## is the starting reactive power and ##Q_d## the desired reactive power. You should be able to calculate a value for ##Q_d##, and hence find how much reactive power the capacitor will have to carry in order to bring the reactive power down to that level.
 
  • #7
gneill said:
Note that I've corrected a typo in the power triangle that I posted in #4. I had switched the digits in the real power value. Sorry about that. The new figure is repeated here:
View attachment 271443

I would suggest going first for question part (a), finding the capacitive reactance required to achieve a load power factor of 0.98 . You can work from the power triangle! Add in a line that represents the apparent power for the desired power factor. Something like:
View attachment 271444
so that ##Q_o## is the starting reactive power and ##Q_d## the desired reactive power. You should be able to calculate a value for ##Q_d##, and hence find how much reactive power the capacitor will have to carry in order to bring the reactive power down to that level.

Thanks

From re-doing the power triangle for a power factor of 0.98 I now have:

Qd= S*Sin θ = 3.2sin11.5 = 0.74MVAr

Where would I go from here to calculate the Capacitive Reactance, seem to be getting confused as the equations i know of to calculate Xc you need to know the capacitor value in farads.

Do i need to continue the way I have been going previously where:

p.f= 0.86
Il=(3.2*10^6)/(√3*11*10^3*0.86 )= 195.3∟-30.7° = 167.9-j99.7

p.f.=0.98
Il=(3.2*10^6)/(√3*11*10^3*0.98 )=171.4∟-11.5° = 167.9-j34.2

Thanks for the help
 
  • #8
Note that the value of S will be different for the "new" power factor. Also, I think you've miscalculated the original S value. I don't get 3.2 MVA for ##\sqrt{P^2 + Q^2}##.

It's simpler to find the desired Q via the power factor angle and the constant real power P, so

##Q_{new} = P \tan{\theta}##

where ##\theta## is the power factor angle.
 
  • #9
gneill said:
Note that the value of S will be different for the "new" power factor. Also, I think you've miscalculated the original S value. I don't get 3.2 MVA for ##\sqrt{P^2 + Q^2}##.

It's simpler to find the desired Q via the power factor angle and the constant real power P, so

##Q_{new} = P \tan{\theta}##

where ##\theta## is the power factor angle.

Sorry must have put it wrong, I worked it out to 3.72MVA

using P tan θ
3.2tan11.5 = 0.65
 
  • #10
That looks better.

So if the original reactive power Q was 1.9 MVAr and the desired Q is 0.65 MVAr, how much reactive power do you need to cancel out?
 
  • #11
gneill said:
That looks better.

So if the original reactive power Q was 1.9 MVAr and the desired Q is 0.65 MVAr, how much reactive power do you need to cancel out?
/
you would need 1.25MVAr to cancel out
 
  • #12
JE93 said:
/
you would need 1.25MVAr to cancel out
Right!

So the capacitor that's to be added across the load should provide that much reactive power. Can you think of a way to calculate the reactance (in Ohms) given that power requirement?
 
  • #13
gneill said:
Right!

So the capacitor that's to be added across the load should provide that much reactive power. Can you think of a way to calculate the reactance (in Ohms) given that power requirement?
could you just use simple ohms law?
but using V^2/P
so 1.25^2/3.2=0.48kΩ

thinking this maybe wrong though
 
  • #14
You want to consider only the reactive power here. You have a supply voltage of ##V_R## and with some reactance value ##X_c## create the necessary power value (1.25 MVAr). So that

##Q_c = \frac{V_R^2}{X_c}##

Find ##X_c##, the capacitor reactance.
 
  • #15
gneill said:
You want to consider only the reactive power here. You have a supply voltage of ##V_R## and with some reactance value ##X_c## create the necessary power value (1.25 MVAr). So that

##Q_c = \frac{V_R^2}{X_c}##

Find ##X_c##, the capacitor reactance.
Qc=V^2/Xc
1.25=11^2/Xc
Xc=11^2/1.25=96.8Ω
 
  • #16
Almost. What happened to the ##\sqrt{3}## applied to the 11 kV?
 
  • #17
gneill said:
Almost. What happened to the ##\sqrt{3}## applied to the 11 kV?
sorry,
That now gives me 167.7 Ω
 
  • #18
I don't think you're applying the ##\sqrt{3}## appropriately. Remember,

##V_R = \frac{11 kV}{\sqrt{3}}##
 
  • #19
11*10^3/√3=6350.8
6350^2/1.25*10^6 =32.3Ω
 
  • #20
That's it! So the required capacitive reactance will have a magnitude of 32.3 Ω . That's part (a) of your problem.

For part (b) it looks like you'll need the line currents before and after the correction is applied. What have you learned about finding the magnitude of the line current given the real power, voltage, and power factor?
 
  • Like
Likes JE93
  • #21
gneill said:
That's it! So the required capacitive reactance will have a magnitude of 32.3 Ω . That's part (a) of your problem.

For part (b) it looks like you'll need the line currents before and after the correction is applied. What have you learned about finding the magnitude of the line current given the real power, voltage, and power factor?

thanks for you help really appreciate it.

Looking back at it all, it shows using the power triangle was a massive help in working it all out. I just need to stop the silly little mistakes haha.
 
  • Like
Likes berkeman
  • #22
Yeah, the power triangle gives you a concrete visual that's easy to comprehend and keeps the various variables and their relationships sorted out.

You're welcome for the help! Keep practicing and it'll soon become much clearer and easier.
 
  • Like
Likes berkeman and JE93

Related to Calculating Capacitive Reactance

1. What is capacitive reactance?

Capacitive reactance is a measure of the opposition that a capacitor presents to an alternating current (AC). It is measured in ohms and is dependent on the frequency of the AC signal and the capacitance of the capacitor.

2. How do you calculate capacitive reactance?

The formula for calculating capacitive reactance is Xc = 1/(2πfC), where Xc is the capacitive reactance in ohms, f is the frequency in hertz, and C is the capacitance in farads.

3. What is the relationship between frequency and capacitive reactance?

The relationship between frequency and capacitive reactance is inverse. This means that as the frequency of the AC signal increases, the capacitive reactance decreases, and vice versa.

4. How does capacitive reactance affect the current in a circuit?

Capacitive reactance limits the flow of current in a circuit by creating a resistance to the AC signal. As the capacitive reactance increases, the current in the circuit decreases, and vice versa.

5. What are some practical applications of calculating capacitive reactance?

Calculating capacitive reactance is important in designing and analyzing circuits that use capacitors, such as in AC power systems, electronic filters, and audio equipment. It is also used in determining the power factor in electrical systems and in designing capacitive touchscreens and sensors.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
4
Views
2K
  • Introductory Physics Homework Help
Replies
1
Views
713
  • Engineering and Comp Sci Homework Help
Replies
4
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
4K
  • Introductory Physics Homework Help
Replies
8
Views
381
Back
Top