Calculating KVA delivered on 3 phase feed
In summary, KVA is a unit of apparent power and is important to calculate on a 3 phase feed because it helps determine the maximum amount of power that can be delivered without causing overload or damage. To calculate KVA, the voltage, current, and power factor of the system are needed and the formula is KVA = (Voltage x Current x √3) / 1000. KVA represents both real and reactive power, while kW represents only real power. KVA can be higher than kW because it includes both types of power. Factors such as voltage, current, and power factor can affect the KVA delivered on a 3 phase feed, as well as other factors such as temperature, harmonics, and power quality
evang
For a building powered by a 3-phase feed, I need to estimate the amount of power available to 120v & 208v loads in the building.
If the feed delivers 200A at 600v, is this 200A per phase (meaning 360 KVA total) or a third of that?
TIA.
you have not clearly mentioned supply voltage. from where the 600v comes into picture?
assuming phase to ground voltage as 120 (phase to phase voltage 208) and load current as 200A
Power = 3 * 120V * 200A
= 72000 VA
= 72 KVA
Correct, the voltage supplied to the building is 600v per phase.
200A is the max current available on the 600v feed.
FAQ: Calculating KVA delivered on 3 phase feed
What is KVA and why is it important to calculate it on a 3 phase feed?
KVA stands for kilovolt-ampere and it is a unit of apparent power. It is important to calculate KVA on a 3 phase feed because it helps determine the maximum amount of power that can be delivered to a load without causing overload or damage to the system.
How do you calculate KVA delivered on a 3 phase feed?
To calculate KVA on a 3 phase feed, you need to know the voltage, current, and power factor of the system. The formula is KVA = (Voltage x Current x √3) / 1000. The √3 represents the square root of 3, which is a constant for 3 phase systems.
What is the difference between KVA and kW?
KVA represents the total amount of power in a system, both real and reactive power. kW, on the other hand, only represents the real power or the actual amount of power being used to do work. KVA is important for sizing equipment and determining the capacity of a system, while kW is important for measuring energy consumption.
Can KVA be higher than kW?
Yes, KVA can be higher than kW. This is because KVA includes both real and reactive power, while kW only represents real power. In systems with high levels of reactive power, the KVA may be significantly higher than the kW.
What factors can affect the KVA delivered on a 3 phase feed?
The KVA delivered on a 3 phase feed can be affected by factors such as the voltage level, the current level, and the power factor. Changes in any of these factors can result in a change in the KVA delivered to a load. Other factors such as temperature, harmonics, and power quality can also impact KVA.