Calculating phase currents from line currents in an unbalanced delta
  • Thread starter mrcavemen
  • Tags
    Delta
mrcavemen
In an unbalanced delta system, I can calculate the line currents given the phase currents.
However, I seem to be unable to go the other direction and cannot find sufficient resources to do so.
Looking at the phasor diagrams it seems like this should be possible, but my math (or understanding of it) is failing me.
Is it possible to calculate this? For simplicity we can assume a pure resistive system.
I believe the information you are missing, is that the sum of the line currents, is zero.
Likes Babadag
I think your problem here is that if you just do KCL you get a set of 3 equations and 3 unknowns that is singular. This indicates that there is more than one possible solution.
@Baluncore is correct, the line currents SHOULD sum to zero. IRL, check that first, just to verify that your data fits your model. This means that you can ignore one of them, let's say ##I_C## since ##I_C = -(I_A+I_B)##. This will allow you to simplify your model, as I've done below.
My approach would be to use superposition to get a set of equations and work from there. I've started it below, but I'm way too busy today to actually finish it. Let me know how this works out for you.
I think the genesis of the multiplicity is that you could have a circulating current in the loads. Suppose you have a solution to the phase currents. If you just add another constant term to each phase current (with the polarity in my schematic), that would also be a solution, since it would have no effect on the line currents.
So, you could also choose to stipulate the the phase currents sum to zero. This is a more restrictive question than you originally asked (a passive load condition). This would give you a 4th equation to add to KCL. This is really the same as just adding a KVL equation for the only loop in the network. I suspect this is what @Baluncore really meant above. Again, I haven't done it (at least in the last 5 years or so). Let me know if that works.
Likes Baluncore
Given these conventions I tried to calculate iba and icb.
But I seem to have taken a wrong step somewhere as my end result is incorrect. I think its already in the first steps:
iba|IA=0 = IB +icb
iba|IB=0 = iac - IA
+= IB +icb + iac - IA
icb|IA=0 = iba -IB
icb|IB=0 = IC - iac -> -IA -IB - iac
+= iba - iac -IA
Referring to the two unlabeled nodes in the schematic of post #3 (it's not too hard to figure out which is which), if you knew the voltage at each, and the impedance of each leg of the delta, would you be able to calculate the current in each phase? Do you know how to calculate the voltage at each node?
I thought the OPs original problem statement was an unbalanced system with known line currents. Of course it's easier if he has more data. I don't think he does in this context.
Your schematic in post #3 showing phase impedances misled me into thinking we were trying to solve a problem where the phase impedances were known.
They may be useful if you want to use KVL, but shouldn't be necessary. They should go away in the solution.
I would use KCL and perform a nodal analysis. You schematic in post #3 is instantly solvable if the 3 impedances are known. The two node voltages are obtained and from those, the 3 phase currents follow.
The 3PH line voltages are assumed fixed in magnitude and phase.
The impedance of the phases are assumed fixed, but unequal.
Each phase impedance is subjected to a differential line voltage.
A vector current flows through each phase.
Those phase current vectors are subtracted to get the line current vectors.
Is the problem here, reversing that process, while not knowing the differing impedances of the different phases ?
yes, I don't know the difference impedances of the different phases.
In polar form, I assumed Ia< 0°, for here I can calculate the angles of Ib and Ic (given that their sum is 0).
Given
IA = iac - iba
IB = iba -icb
IC = icb - iacthe phases voltages should be in line with the phase currents, so I thought I could get the impendances by substituting the current:
IA = Uac/Zac -Uba/Zba
IB = Uba/Zba - Ucb/Zcb
IC = Ucb/Zcb - Uac/Zac
Uba, Ucb and Uac have an offset of 120°
Given that IA+IB+IC = 0, I thought I could calculate the angle between the voltages and the line currents.
From there, given that the resistors are pure resistors, the phase currents are in phase with the phase voltages, so I could then get the phase currents from there...
But unfortunately, I don't think it's possible to calculate the angle, as I think there are many solutions that would fit :\
Yes. My previous model with current sources isn't right in this regard. Just because we know the line currents, we can't draw it as a high impedance source. Those should be voltage sources.
Still too lazy to try and solve it myself, LOL.
Given
IA = iac - iba
IB = iba -icb
Do you know the line currents AND voltages, or just the line currents?
Since the line voltages are low impedance, this has become three separate problems.
You can calculate any phase current from two line voltages and that phase impedance.
You can calculate line currents from phase currents without any problem.
Unfortunately, you cannot go back again because there are an infinite number of solutions. If you arbitrarily specify any one phase current, there is a simple consistent solution for the other two phase currents.
To solve the problem requires you define a relationship between the phase currents, but they are independent problems, and cannot be separated, because the impedance of the phases are unrelated in the unbalanced model.
This is true for unbalanced complex impedances and for unbalanced resistive loads.
The 3PH line voltage and phase is assumed to be ideal.
The line impedance is assumed to be zero.
Yes. You need one more piece of information. A phase current or a phase impedance.
mrcavemen, are you still paying attention to this thread? There's more to be said which you might find useful.
mrcavemen, you can proceed like this.
Using your definitions:
Given
IA = iac - iba
IB = iba -icb
IC = icb - iac
The conversions for phase to line currents, and back again can be done with simple
matrix multiplications like this:
As an example if we have phase currents of 1,2,-3 amps, the conversion gives line
currents of -1,5,-4 amps. And converting those line currents back to phase
currents gives 1,2,-3 amps. This example is using DC currents, but it all works
with complex currents.
Either one phase impedance, or one phase current must be known, before you can reverse the process. By claiming that you can recover the unbalanced phase currents, from the line currents, you are pulling three rabbits out of a matrix of hats.
I want to know how you perform that trick.
' Given phase impedance, compute phase currents, then line currents
' reverse the process to recover the phase currents
' line X is connected to phases B and C, opposite phase A
' line Y is connected to phases C and A, opposite phase B
' line Z is connected to phases A and B, opposite phase C
' topology: currents flow counter-clockwise in the delta, A to B to C
' currents flow towards the supply generator in X, Y and Z
' declare state variables
Complex Xv, Yv, Zv ' line voltages
Complex Xi, Yi, Zi ' line currents
Complex Av, Bv, Cv ' phase voltages
Complex Az, Bz, Cz ' phase impedances
Complex Ai, Bi, Ci ' phase currents
' initial line voltages
Double Vrms, Vpk, phase
Vrms = 230 ' neutral to any phase
Vpk = Vrms * Sqr( 2 )
' phasors
phase = 0
Xv = Type( Vpk * Cos( phase ), Vpk * Sin( phase ) )
phase = + TwoPi / 3
Yv = Type( Vpk * Cos( phase ), Vpk * Sin( phase ) )
phase = - TwoPi / 3
Zv = Type( Vpk * Cos( phase ), Vpk * Sin( phase ) )
' phases voltages are line differences
Av = Yv - Zv
Bv = Zv - Xv
Cv = Xv - Yv
' generate random phase impedances
Randomize
Az = Type(200 * Rnd, 100 * ( Rnd - 0.5) )
Bz = Type(200 * Rnd, 100 * ( Rnd - 0.5) )
Cz = Type(200 * Rnd, 100 * ( Rnd - 0.5) )
' phase currents
Ai = Av / Az
Bi = Bv / Bz
Ci = Cv / Cz
' line currents
Xi = Ci - Bi
Yi = Ai - Ci
Zi = Bi - Ai
' now we are ready to go backwards
' we know
' Xi = Ci - Bi
' Yi = Ai - Ci
' Zi = Bi - Ai
Ai = Type( 2, -1 ) ' assume something new for Ai
Bi = Type( 0, 0 ) ' blind trial, hide original
Ci = Type( 0, 0 ) ' blind trial, hide original
' then compute Ai, in a circular argument
Ci = Ai + Yi
Bi = Ci + Xi
Ai = Bi + Zi
' now, Ai is whatever was assumed a few lines back
' there are an infinity of solutions.
I'm pretty unclear on the value of finding a solution if you can't know that it's the solution.
Not if you define "the" solution as the one that includes no circulating current.
As DaveE said in post #4:
"I think the genesis of the multiplicity is that you could have a circulating current in the loads. Suppose you have a solution to the phase currents. If you just add another constant term to each phase current (with the polarity in my schematic), that would also be a solution, since it would have no effect on the line currents."
If you have any solution, adding an arbitrary constant term to each phase current gives another solution--hence there are an infinite number of solutions. But there is only one solution that includes no circulating current. The sum of the squares (the Euclidean norm) of the individual currents of that solution is the minimum possible.
Why do you deny the existence of circulating currents in reactive AC systems ?
I don't deny them. Some systems may have circulating currents, some may not.
If a particular case of the 3 phase system we're discussing has some circulating currents, that fact will not be able to be determined by considering the line currents. The line currents are not affected by any circulating currents, and if the line currents are calculated by multiplying the vector of phase currents by the appropriate transformation matrix, the result obtained will not be affected by any circulating currents. The transformation matrix does not "see" the circulating currents.
If you're trying to calculate the phase currents from the line currents, you won't get a solution that includes circulating currents because they can't be known from the line currents. You can get a solution for the case where there are no circulating currents; this is a useful result and it's the best you can do because there's no way to know what any circulating currents might be just by knowing the line currents.
But if you calculate the phase currents by any method, it's certainly true that another solution is obtained by adding a constant to each phase current (in the right polarity), so we have an infinite number of solutions. This doesn't mean that no useful result can be obtained; it's useful to know what the no-circulating-current result is.
I can recover the minimum norm vector of the phase currents, and in many (even most?) real circuits the circulating currents should be a relatively small fraction of the non-circulating currents. There will be effort in the design and operation of the circuit to minimize circulating currents because they're energy wasters! So it's likely the the minimum norm solution is close to the actual phase currents.
We have an underdetermined system: https://en.wikipedia.org/wiki/Underdetermined_system
The rank of the augmented system is equal to the rank of the coefficient matrix, so the system has an infinitude of solutions. How can we find the one solution out of the infinitude that has the smallest norm (size)?
Use the singular value decomposition (SVD): https://en.wikipedia.org/wiki/Singular_value_decomposition
That article describes how to find the pseudoinverse of the coefficient matrix which I used in post #19 to find the smallest norm solution.
The SVD can also show what can be added to the minimum norm solution to get another solution. In this case our solution be characterized as a 3 element vector. The SVD will give us another 3 element vector such that any multiple of that vector can be added to the minimum norm solution vector, and that result will still satisfy the system.
We can see just from the physics of this circuit that adding equal values to each phase current gives a valid solution. It is to be expected that the math would show that same thing, which we could know from the SVD in some other situation where the physics didn't provide our intuition with the vector whose multiples can be added to any solution vector giving another solution vector.
As an aside, I've been using a DC circuit in my examples because the arithmetic is easier. I've also used the phrase "circulating currents" but the physics of a DC version of this circuit can't really have circulating currents although the math is consistent as though there were such a thing. Maybe we could have "virtual" circulating currents. :smile:
Lol. You are opening up a real can of worms here potentially. Borders on a thread we had not quite a year ago concerning the Walter Lewin paradox. Loops of resistive wire wrapped are a transformer core, that sort of thing. And the ability or inability to make measurements.
You've misconstrued the last sentence of my post. It's strictly for humor. Unfortunately I couldn't find a specifically tongue-in-cheek emoji.😞
Another view.
Computation of line currents from phase currents, is discrete differentiation, around the delta.
Computation of phase currents from line currents, is discrete integration, around the star.
What will be the constant of integration ?
Baluncore said:
Another view.
Depends of what kind of solution you want. Do you want the unique solution where there is no circulating current?
I want to be able to optimise the solution to a problem, by transforming forward and backward consistently, without underestimating the circulating current.
  • #31
It's not possible to calculate (know) what the circulating current is (if there is any) by just knowing the line currents; as DaveE said in post #4, any circulating current has no effect on the line currents.
  • #32
Y'all are really confusing me with this talk of circulating currents. Help, please explain what you mean explicitly.
The OP's problem is clearly not fully defined, so we say it has a multiplicity of solutions. However, I think it can also be thought of as a multiplicity of problems, each with a unique real world solution. Let's look at some specific examples.
To save me some typing, lets define ##V_{XY} \equiv -V_{YX} \equiv V_X - V_Y##
Given that ##I_A = -1##, ##I_B = 5##, ##I_C = -4##
We have the solution in post #19 of ##i_{ac}=1##, ##i_{ba}=2##, ##i_{cb}=-3##
Which is claimed to have no circulating currents because of some "minimum norm" argument that I couldn't really follow.
This solution defines the network (for the applied voltages), with ##Z_{AC} = \frac{V_{AC}}{1A}##, etc.
So now, if we add a "circulating current" of ##1A## then for each phase we get ##i_{ac}=2##, ##i_{ba}=3##, ##i_{cb}=-2##.
This defines a different network, ##Z_{AC} = \frac{V_{AC}}{2A}##, etc.
Both examples are unique solutions to KVL and KCL for their network. In particular, they each satisfy KVL for the load loop: ##i_{ba}Z_{BA}+i_{ac}Z_{AC}+i_{cb}Z_{CB}=0##
So, I claim any passive load network can't have steady state circulating currents, because of KVL, even though I don't really know what they are. Please enlighten me with as few words as possible (equations are preferred to minimize my confusion).
  • #33
You are the one who brought up the notion of circulating currents in post #4.
I said in post #25: "As an aside, I've been using a DC circuit in my examples because the arithmetic is easier. I've also used the phrase "circulating currents" but the physics of a DC version of this circuit can't really have circulating currents although the math is consistent as though there were such a thing." The same is true in an AC circuit with loads that are not reactive (pure resistances) so we are in agreement about that.
In post #4 you must have been talking about what could happen in AC circuits with reactive loads. Can you give an example where that would happen?
  • #34
That post was just wrong. And no, they can't happen with any passive load network in steady state, IMO. Of course that doesn't include transformers or other induced voltages.
But as I said, I'm a bit confused about what others mean when they mention them. It seems like a catch-all phrase like "stray" or "parasitic", but not literally circulating. OTOH, I suppose all currents circulate, what with conservation of charge...
  • #35
Transformers are passive; do you mean resistive, as post #1 described?
What I mean by "circulating" is this: The delta of branches form a loop. If a positive current of the same value is added to the current in each branch of the delta, the directions of those added currents travel in the same direction around the loop--they "circulate" around the loop.
Post #1 made no mention of impedances or voltages, just line and phase currents. It is possible, given only the phase currents to determine the line currents.
The problem is underdetermined (https://en.wikipedia.org/wiki/Underdetermined_system), so the solution for the line currents is not unique; there an infinite number mathematical solutions, but the physics of the situation may rule out some, or all but one.
For example, if we have a vector of phase currents [1,2,-3] and transform that to line currents as I showed in post #19, we get a line current vector of [-1,5,-4] which transforms back to a phase current vector of [1,2,-3].
We can represent the 3 line or phase currents as a vector, for example phase currents [1,2,-3]. This vector has a Euclidean length (norm) of sqrt(1^2+2^2+3^2) = sqrt(14). If we add 1 to each current (this is adding a circulating current of 1) we have another solution, a current vector [2,3,-2], which has length sqrt(17), larger than the norm of the currents with no circulating current. Of all the infinity of solutions for the phase currents with line currents of [-1,5,-4], the one with no circulating current is [1,2,-3], and it has the smallest norm. AND, it is the only one that is physically possible if circulating phase current is impossible.
The same thing applies in the other direction.
Starting with phase currents of [1,2,-3], perform the transformation to line currents.
We get line currents of [-1,5,-4]; add 100 amps in the direction of the delta to each line current. Then we would have line currents of [99,105,96]. These line currents don't add up to zero, so they are physically impossible. But if we premultiply them by the transformation matrix to convert back to phase currents, we get [1,2,-3]; these added currents are ruled out as solutions by the physics of the situation, but they satisfy the math. Knowing only currents (no impedances, that is), the problem is underdetermined, and it has an infinite number of (mathematical) solutions, but all but one are ruled out by the physics of the circuit if circulating current is impossible.
As an aside :smile:, can you answer Baluncore's question in post #23: "Why do you deny the existence of circulating currents in reactive AC systems ?"
Likes Baluncore
10K