Calculating the Mass Flow Rate of a boiler
In summary, to solve the past exam paper, you need to use the formula "Heat lost by steam = Heat taken up by water" to calculate the mass flow rate of the steam, which is 0.011 kg/s. However, the answer given in the past paper is 0.09 kg/s. Then, for the natural gas requirements, you can use the equation Q=UAdT and the 1st law of thermodynamics to calculate the mass flow rate, which is 0.093 kg/s. Lastly, to find the steady state heat supplied to the boiler, you can use the equation (kg of steam)(steam enthalpy)(temp) / time and the given values to get the answer of
sci0x
83
Natural gas is burned in a shell and tube boiler to raise 5 tonnes per hr of dry saturated steam at 4.0 bar g. Condensate is returned to boiler at 4.0 bar g., 100 degrees C.
i) calculate mass flow rate of natural gas required (kgs-1)
ii) the steady state heat supplied to the heating application (MW)
Net enthalpy of combustion of natural gas = 45.6Mj kg-1
Boiler Effeciency = 76%
Enthalpy dry saturated steam at 4 bar g =2748 kJ kg-1
Enthalpy of dry saturated steam at 0 bar g. = 2676 kJ kg-1
Enthalpy of dry saturated water (152 degrees) = 637 kJ kg-1
Enthalpy of dry satirated waterat 0 bar g. (100 degrees C) = 419 kJ kg-1
Q = UAdT
Im trying to do some past exam papers. If i can get help with the method on how to solve and have correct formulas, it will help me.
I) There is one formula in the notes to get mass flow rate:
GsHfg = (GwCpw)(change in temp)
Gs x 2748 x 10x103 = (5000/3600) x 419 x (152-100)
Gs = 0.011 kg/s
However the past paper says answer is 0.09 kg/s
If I can get help from an expert I would appreciate it.
sci0x said:
Homework Statement:: Natural gas is burned in a shell and tube boiler to raise 5 tonnes per hr of dry saturated steam at 4.0 bar g. Condensate is returned to boiler at 4.0 bar g., 100 degrees C.
Homework Equations:: Q = UAdT
This is not the correct equation to use. The correct equation to use is the open system (control volume) version of the 1st law of thermodynamics. Please write down the form of this equation that applies to the water/steam stream flowing between the entrance and exit of the tubular heat exchanger.
Likes sci0x
I think I am on the right track, although I am confused by all the enthalpy options given and this isn't the correct final answer for mass flow rate but anyway:
In 1 second 5000kg/3600s = 1.38kg
Final Enthalpy:
H2 = (m)(h2)
= (1.38)(2748)
= 3792.24
Initial Enthalpy:
H1 = (1.38)(419)
= 578.22
Final - Initial = 3214.02kJ = Q
Boiler has 76% effeciency so need to burn (3214)(100/76) = 4228.97 = Q
Water heat in = - steam heat out
(M)(637)(152-100) = - - 4228.97
M = 0.127kg/s
The answer should be 0.09 kgs-1
Maybe you should use units. Your gas energy requirement is 4229 kJ/s = 4.22 MJ/s. The heating value of the natural gas is 45.6 MJ/kg. So the gas rate is 4.22/45.6 = 0.093 kg/s
Likes sci0x
Thank you, can you help with the last part:
Ii) the steady state heat supplied to the boiler:
(Kg of steam)(steam enthalpy)(temp) / time
(5000)(2748)(52) / 3600
= 198466.6 W = 1.98MW
The answer should be 3.23 MW
Thanks
Thanks
$$\frac{(5000)(2748-419)}{(3600)(1000)}$$
Likes MCTachyon and sci0x
Related to Calculating the Mass Flow Rate of a boiler
What is the mass flow rate of a boiler?
The mass flow rate of a boiler is the amount of mass that enters or exits the boiler per unit of time. It is commonly measured in kilograms per second (kg/s) or pounds per hour (lb/hr).
Why is calculating the mass flow rate important?
Calculating the mass flow rate is important because it helps in determining the efficiency of the boiler. It also helps in determining the amount of fuel needed to produce a certain amount of steam, which is important for cost and energy efficiency.
How is the mass flow rate of a boiler calculated?
The mass flow rate of a boiler can be calculated by dividing the total mass of steam produced by the time taken to produce it. This can be measured using a flow meter or by measuring the volume of water that enters the boiler and converting it to mass using the density of water.
What factors can affect the mass flow rate of a boiler?
The mass flow rate of a boiler can be affected by several factors, including the type and size of the boiler, the temperature and pressure of the steam, the type and quality of fuel used, and any obstructions or restrictions in the steam pipes.
How can the mass flow rate of a boiler be optimized?
The mass flow rate of a boiler can be optimized by ensuring proper maintenance and cleaning of the boiler, using high-quality fuel, and adjusting the steam pressure and temperature to the optimal levels. Regular monitoring and adjustment of these factors can help to improve the efficiency and reduce the energy consumption of the boiler.
10K
  • Aerospace Engineering