What those of you who think that there can be no benefit in using waste heat from AC units are failing to account for is when the system that benefits is required to run anyway. Then the work can be eliminated from the equation to find the savings.
Take my balanced water source heat pump system, water is already being circulated to both the units requiring heat and those required to cool. The savings is found in not using a boiler to add heat to the loop or not using a cooling tower to remove heat from the loop.
The loop temperature raises slightly leaving the cooling units, but lowers again after leaving the heating units, so the cooling units are not placing their heat into a hotter heat sink, they are seeing the same cooler temperature as before.
Also, the work losses can actually be reduced by bypassing the cooling tower and the boiler to eliminate head losses in the piping through these.
So, where are the increased losses you are referring to?
Remember the cost to move the heat from one unit to the other in this system already exists, the water is moving constantly. You need to compare this to two separate systems one doing heating and one doing cooling. Then you need to add the boiler losses and the cooling tower losses, including pumping the water through these units, then you can see your savings.
Take my balanced water source heat pump system, water is already being circulated to both the units requiring heat and those required to cool. The savings is found in not using a boiler to add heat to the loop or not using a cooling tower to remove heat from the loop.
The loop temperature raises slightly leaving the cooling units, but lowers again after leaving the heating units, so the cooling units are not placing their heat into a hotter heat sink, they are seeing the same cooler temperature as before.
Also, the work losses can actually be reduced by bypassing the cooling tower and the boiler to eliminate head losses in the piping through these.
So, where are the increased losses you are referring to?
Remember the cost to move the heat from one unit to the other in this system already exists, the water is moving constantly. You need to compare this to two separate systems one doing heating and one doing cooling. Then you need to add the boiler losses and the cooling tower losses, including pumping the water through these units, then you can see your savings.