Can I use individual capacitor IR for parallel circuit balancing resistors?

  • Thread starter Thread starter sodoyle
  • Start date Start date
  • Tags Tags
    Resistor Sizing
AI Thread Summary
Balancing resistors are essential for series capacitors to prevent voltage mismatches due to leakage currents. For parallel capacitors, the equivalent insulation resistance (IR) decreases, suggesting that balancing resistors should be sized accordingly, potentially at one order of magnitude lower than the individual capacitor IR. However, the discussion highlights that the sizing of these resistors can also be based on the individual capacitor IR rather than the equivalent IR of the parallel branch. While considering the time constant, it's noted that increasing the number of parallel capacitors necessitates lower resistance values, but practical limits exist due to power consumption concerns. Ultimately, each capacitor should ideally have its own resistor to maintain effective voltage balancing across the system.
sodoyle
Messages
34
Reaction score
1
TL;DR Summary
I would like to size voltage balancing resistors for capacitors.
I am going to have several series/parallel capacitors so need balancing resistors. I understand that for series capacitors, it is wise to use voltage balancing resistors so mismatch in individual series capacitors leakage current can flow through the resistors which prevents individual capacitors from charging more than desired.

As an example, let's say the insulation resistance (IR) of a given capacitor is 50MEG. I think selecting a resistor at least one order of magnitude lower (5MEG) would be suitable. Assuming I have 2 series capacitors, I would place a resistor across each so I'd also have two series 5MEG resistors.

My question comes to parallel capacitors. If I place two capacitors in parallel, circuit theory would give an equivalent IR of 25MEG. This would mean that I now need maximum 2.5MEG balancing resistors. Thinking about it using the current divider though, it seems like 5MEG should still be fine. Let's say I still have two in series and two in parallel...if the top parallel capacitors have combined 1 mA leakage current and the bottom parallel capacitors have a combined 0.95 mA leakage current, the real impedance of each capacitor would still be 50MEG so the excess 0.5 mA would still have the same difference in impedance when "deciding" to flow through the capacitors or balancing resistor. Therefore, I think the balancing resistor sizing can be based on an individual capacitors IR and not the "equivalent IR" of the parallel branch.

Is this correct or am I off in my reasoning?
 
Last edited:
Engineering news on Phys.org
Maybe look at it from a time constant point of view. Each capacitor has a parallel resistor, such that the product R·C is a constant in the capacitor bank. That way, as the system voltage rises or falls, the capacitors all rise and fall in proportion.
 
  • Like
Likes sophiecentaur and hutchphd
Baluncore said:
Maybe look at it from a time constant point of view. Each capacitor has a parallel resistor, such that the product R·C is a constant in the capacitor bank. That way, as the system voltage rises or falls, the capacitors all rise and fall in proportion.
Looking at it from the time constant point of view it looks like the resistance would need to decrease proportionally to the increase in capacitance. In other words, if I have 4 capacitors in parallel, the balancing resistors would need to be 4x lower than the value with no parallel caps (assuming all capacitors are the same value). If that's the case, it seems reasonable only to a certain extent. At some point the resistance would get too low and losses through them would be too high. I still see why it's important to consider the dynamic response for these resistors though.

From the steady state point of view, the R·C time constant wouldn't be as important as they'll only effect the static voltage balancing. As mentioned above, the RC time constant cannot be reasonably kept the same in all cases. If I parallel 50 capacitors, it may not be feasible to have 50x lower balancing resistors simply because of the increase in power consumption.
 
sodoyle said:
If I parallel 50 capacitors, it may not be feasible to have 50x lower balancing resistors simply because of the increase in power consumption.
If you have 50 capacitors in parallel, the leakage current will be 50 times greater so you will need one resistor with 1/50th of the resistance to conduct that leakage current.

Think of each capacitor as having it's own resistor. If there are 50 capacitors, there will be 50 resistors in parallel. The time constant of any combination will remain the same.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...