Car Radiator as Air-to-Water Heat Exchanger

In summary: This flow rate cannot be delivered by the three 240 CFM fans you are using. A solar powered fan, rated at 500 CFM, could be used to deliver the required flow.The fan could be placed on the roof or in the sunniest part of the yard. The fan should be placed so that the air flow is directed at the exchanger. The fan should be mounted so that it can be turned off if the temperature reaches the desired level.The fan should have a controller to limit the speed to prevent it from running continuously.The fan should run for 8 hours a day, 7 days a week.
  • #1
Gusto
2
0
TL;DR Summary
I have a steady source of 110 degree air. Would flowing my pool water through a couple of truck radiators situated in the heat flow in an insulated chamber be an effective way to heat my pool?
I am looking for a passive way to convert a supply of hot air into warm pool water. My pool can be in the low 70s without heat. Looking to get a 10 degree lift in pool temp. Pool is in-ground and relatively small at 8,500 gal. Water flow rate through the radiators can be regulated by valves. The airflow at the delivery point can range from 100-120F consistently for about 8 hours a day (daylight) depending on the source intensity. Airflow is currently delivered by three 8" flexible ducts each with a 240 CFM in-line duct fan used for proof of concept.

I am looking for: 1. Confirmation that this is viable; 2. the most efficient passive heat exchange method to convert the air to warmer water; and 3. Assessment of whether solar powered fans can be used to deliver totally self-sustained operations.

I have scoured online forums and cannot seem to find a definitive answer. I know that there are a lot of broadly expressed variables, but hopefully someone can point me in the right direction. Many thanks. Gusto
 
Engineering news on Phys.org
  • #2
Welcome, Gusto! :cool:

For an estimate, I would start by investigating the heat-exchange performance, as well as resistance to different flow rates, of those radiators, for both, water and air side.

The airflow rate will be more or less constant, but certain percentage less that 240x3 cfm’s due to the restriction rate of both radiators.
The water flow rate will depend on how much your pump can reasonably due (especially if driven by wind, which tend to be best when Sun is high and heating less necessary).

Your water will gain some energy from the radiators and will lose some while flowing through pipes; therefore, the shorter and more insulated pipes the better.
 
  • #3
Lnewqban said:
Welcome, Gusto! :cool:

For an estimate, I would start by investigating the heat-exchange performance, as well as resistance to different flow rates, of those radiators, for both, water and air side.

The airflow rate will be more or less constant, but certain percentage less that 240x3 cfm’s due to the restriction rate of both radiators.
The water flow rate will depend on how much your pump can reasonably due (especially if driven by wind, which tend to be best when Sun is high and heating less necessary).

Your water will gain some energy from the radiators and will lose some while flowing through pipes; therefore, the shorter and more insulated pipes the better.
Thanks Lnewqban! So the concept of the radiator working in reverse sounds viable? Radiators normally dissipate heat. Will the thermal transfer properties be the same in reverse (meaning if a radiator can cool fluid at a certain rate of air and fluid flow, will the same rates apply to heating fluid)? Sorry if that is a basic question. Best. Gusto
 
  • #4
Gusto said:
Thanks Lnewqban! So the concept of the radiator working in reverse sounds viable? Radiators normally dissipate heat. Will the thermal transfer properties be the same in reverse (meaning if a radiator can cool fluid at a certain rate of air and fluid flow, will the same rates apply to heating fluid)? Sorry if that is a basic question. Best. Gusto
I am not sure, but I believe that heat transfer mainly depends on the temperature difference and the area of the interchage surface.
If any, the reduced rate of exchange should not be dramatic.
Perhaps other members of this site have a more accurate idea.
 
  • #5
A car radiator will transfer heat from air to water exactly as well as it transfers heat from water to air. Car radiators are optimized for large air flow and large water flow. They work even better at low air and water flows.
If you are interested in calculating the effect of changing air and/or water flows on heat exchanger performance, a good book is Compact Heat Exchangers by Kays and London: https://www.amazon.com/dp/1575240602/?tag=pfamazon01-20. The book has numerous graphs that show the effect of changing flow, saving the need for tedious calculations.

Some ball park calculations to get started:
You mention 240 CFM duct fans in 8" flex duct. Flex duct has extremely high friction loss. If those duct fans are muffins that have low static pressure, the air flow will be lot less than 240 CFM per fan and duct. I will assume a total of 500 CFM at 100 deg F.

Assume the air enters the heat exchanger at 100 F, and leaves at 85 F. The heat will be:

##500 ft^3/min * 0.018 BTU/ft^3-deg F * (100 - 85) deg F * 60 min/hr = 8100 BTU/hr##

If we further assume that the water enters at 75 F and leaves at 80 F, the required flow rate will be:

##8100 BTU/hr / (80 - 75) deg F * 1 lb-deg F/ BTU * 1 gal / 8.34 lbs * 1 hr/60 min = 3.2 GPM##

Increasing the water flow rate will result in less temperature rise across the heat exchanger, and slightly increase the total heat transferred. The above temperatures are rough guesses, but should be good enough to to give you an idea of the amount of heat you can expect to put into the water with an automotive heat exchanger. They also show that the water pump needs to move at least 3 GPM of water.
 
  • Like
  • Informative
Likes berkeman, 256bits and Lnewqban
  • #6
jrmichler said:
Assume the air enters the heat exchanger at 100 F, and leaves at 85 F. The heat will be:

500ft3/min∗0.018BTU/ft3−degF∗(100−85)degF∗60min/hr=8100BTU/hr
So 8100 pounds of water ( 810 gallons ) increases in temp 1 degree F in 1 hour.
His pool is 8500 gallons - 10 hours for a one degree rise in temperature.

Off the cuff, I honestly thought it would be more than that.

If he leaves it running, he should notice a difference.
 
  • Like
Likes rbelli1
  • #7
One thing to keep in mind is that once you get this all built you will probably not feel the temperature difference in the outlet flow. It will still be doing its job but the small fraction of a degree increase is too small for the human body to differentiate.

BoB
 
  • #8
IIRC, the main heat loss from swimming pools is evaporation. You might want to check that effect and compare it to the BTU gain of the proposed solution.
 
  • Like
Likes 256bits, russ_watters and Lnewqban
  • #9
Gusto said:
...the most efficient passive heat exchange method to convert the air to warmer water...
Those radiators are not really optimal. They are meant to change the temperature of the air flow by a few degrees only (so the temperature of the air flow on the output will be just a few degrees apart from the input temperature), but an ideal heat exchanger would change the temperature of the outgoing air to the temperature of the water in the pool.
Check 'counter flow heat exchanger'.

You can make it work though: just use more than one radiator in series with the first one, attached to the air output of the first one, to serve as the first one for the water flow.
... and if the output airflow is still warm, then just add one more, depending on your supply of truck radiators :wink:
 
Last edited:
  • #10
A radiator for, say, a 300 hp engine is operating in a different regime than the same radiator in the OP's situation. For example, assume a radiator for a 300 hp engine. That engine burns about 25 gallons of gasoline per hour at maximum power: 300 hp * 0.5 lb/hp-hr / 6 lb/gallon = 25 gal/hr.

Gasoline has about 120,000 BTU per gallon, and about 1/3 of that goes to the cooling system. The heat to the radiator is then 25 gal/hr * 120,000 BTU/gal / 3 = 1,000,000 BTU/hr. That's more than 100 times as much heat as the OP wants to transfer.

The book referenced in Post #5 has the following performance chart for a cross flow heat exchanger with fluids unmixed:
Heat Exchanger.jpg
In an automotive application where large amounts of heat are transferred from large amounts of fluid, the operating point is somewhere around 1 NTU. With the much smaller flow rate in the swimming pool application, the operating point is off the chart to the right. With the flow rates in Post #5, the ##C_{min}/C_{max}## is 0.33, so the effectiveness approaches that of a counterflow heat exchanger.
 
  • Like
Likes gavalerushikesh_18, 256bits and hutchphd

Related to Car Radiator as Air-to-Water Heat Exchanger

1. How does a car radiator work as an air-to-water heat exchanger?

A car radiator works as an air-to-water heat exchanger by using a series of tubes and fins to transfer heat from the hot engine coolant to the surrounding air. The hot coolant flows through the tubes, while the fins increase the surface area for heat transfer to the air passing through them. This process cools the coolant and allows it to continue circulating through the engine, preventing it from overheating.

2. What are the benefits of using a car radiator as an air-to-water heat exchanger?

Using a car radiator as an air-to-water heat exchanger is beneficial because it is a cost-effective and efficient way to transfer heat. Car radiators are designed to withstand high temperatures and have a large surface area, making them ideal for heat exchange. Additionally, the air flow created by a moving vehicle helps to increase the efficiency of the heat transfer process.

3. Can a car radiator be used for other heat exchange purposes?

Yes, a car radiator can be used for other heat exchange purposes. In addition to cooling engine coolant, car radiators can also be used to cool transmission fluid, power steering fluid, and other fluids in a vehicle. They can also be used in industrial settings for heat exchange in various processes.

4. How do you maintain a car radiator as an air-to-water heat exchanger?

To maintain a car radiator as an air-to-water heat exchanger, it is important to regularly check and replace the coolant to ensure it is clean and at the proper level. It is also important to keep the radiator fins clean and free of debris to allow for efficient heat transfer. Regularly inspecting for any leaks or damage is also recommended.

5. Are there any disadvantages to using a car radiator as an air-to-water heat exchanger?

One potential disadvantage of using a car radiator as an air-to-water heat exchanger is that it may not be as efficient in extreme temperatures. In very cold weather, the coolant may not reach its optimal operating temperature, and in very hot weather, the radiator may struggle to keep the coolant cool enough. Additionally, if the radiator becomes damaged or clogged, it may not function properly and could lead to engine overheating.

Similar threads

  • General Engineering
Replies
10
Views
3K
Replies
1
Views
2K
  • General Engineering
Replies
11
Views
2K
Replies
6
Views
3K
Replies
5
Views
2K
  • Mechanical Engineering
Replies
2
Views
457
Replies
24
Views
6K
  • General Engineering
Replies
1
Views
6K
Replies
3
Views
3K
  • Mechanical Engineering
Replies
3
Views
703
Back
Top