- #1
yahastu
- 79
- 7
Context: I'm building an off-grid, 100% solar powered home. I have a 12 kw solar array wired up to a Sol-Ark inverter and a Fortress 18.5 kwh lithium battery.
Question: What is the ideal grounding/earthing scheme?
Additional context: where I'm building, there is currently no requirement that my setup be exactly to code. I know that code is written under the assumption that one is connected to the electric grid, and so the recommendations don't always necessary apply logically to me, and so I don't want to just assume that code is best. I want to do what is actually most logical for my situation. With that said, if doing something to code doesn't result in a inferior design, then I'm all for it.
Lightning protection: Typically, lighting protection is one of the reasons cited for why homes usually have an Earth ground. If a lightning surge goes into your house wiring, then an Earth ground gives it somewhere to go so it's less likely to damage your electronics (or start a fire). On the other hand, adding an Earth ground actually makes your electrical system a more attractive target to lightning (by helping to create a low resistance path between the origin of the lighting and somewhere deep in the Earth). A much better protection from lightning is to create a separate lightning rod that provides a lower resistance pathway for the lightning than your house's electrical system. In addition, any nearby lightning strikes that miss your electrical system, could still cause damage to the electrical system by traveling through the ground in the nearby radius. For these reasons, I intend to install a separate, Earth grounded lighting rod...and as a result, it doesn't seem like there is no benefit to having an Earth ground on the house for lightning protection.
Shock protection: Typically, a house receives electricity from the mains power, which is grounded to Earth. If there is a short in an appliance whereby, say, one of the current carrying AC wires is shorted to the case of the appliance, and someone touches the appliance, then the person may form a lower resistance pathway from the case of the appliance to Earth ground, because the person is likely standing on Earth ground. This is often cited as a reason for having an Earth ground at the house: because if the appliance has a ground terminal, then the appliance case will be bonded to ground which goes all the way to Earth ground, and as a result, a person touching the case isn't going to be electrocuted. However, this protection is only necessary because the house power system is referenced to Earth ground in the first place. If the house had a floating ground, then the excess current wouldn't be searching for a pathway to Earth ground, and would have no reason to travel through the body of a person touching the electrified appliance case. It would be safe to touch the electrical wire, just as it is safe for a bird to land on an exposed electrical wire. So, when talking about an off-grid house, the desire for shock protection doesn't seem to motivate adding an Earth ground. In fact, it seems that a floating ground would be safer from a shock perspective standpoint, because that way a human standing on the ground will be unlikely to be on the lowest resistance pathway to complete a circuit.
All power to the house will come from the inverter -- either directly, as passed through from the battery system. Therefore, in the event of a broken appliance which has a short from a current carrying wire to the case, then the excess current will be searching for a path back to one of the inverter terminals. This seems like a decent reason to wire up my house's ground to one of the inverter terminals (say, negative)...as it would provide some circumstantial shock protection, although it seems the only possible circumstance would involve a person touching the inverter terminals while simultaneously touching a broken appliance case that is shorted out -- a pathologically unlikely circumstance.
Electrical interference: having the house grounded to Earth can introduce electrical disturbances into my own electronics, which at best is undesirable (eg, not great for HAM radio), and at worst, a danger, if there is a nearby lightning strike that energizes the house via the Earth ground.
Solar array: typically, the solar panel frames are all bonded together, and bonded to the house ground, which is of course bonded to the Earth ground. For better or worse, I did not run a ground through my buried conduit between the panels and the house, so it is not really possible for me to ground the panels to the house ground. However, I can't think of any reason to do so, other than by convention. The panels generate their own DC electricity, which is totally separate from the AC electricity generated by the inverter, so I don't see any reason why the two systems should want to share the same ground, especially if neither of them benefit from an Earth ground. The existence of the separate lightning protection system seems to eliminate any desire to bond the panels to Earth from a lighting protection perspective. From a shock protection perspective, I'm thinking perhaps it would be beneficial to bond the negative terminals of each panel to the solar panel frame assembly? But I don't think that is usually done.
Current plan: based on the above considerations, my current plan is to: a) bond the steel joists/I-beam of the house to the negative terminal of the inverter, to the ground wire in my main panel; b) not bother grounding the DC panel array; c) create an independent pathway to Earth ground in the form of a lightning rod, which is not connected to my AC or DC electrical systems.
Any thoughts/feedback is appreciated
Question: What is the ideal grounding/earthing scheme?
Additional context: where I'm building, there is currently no requirement that my setup be exactly to code. I know that code is written under the assumption that one is connected to the electric grid, and so the recommendations don't always necessary apply logically to me, and so I don't want to just assume that code is best. I want to do what is actually most logical for my situation. With that said, if doing something to code doesn't result in a inferior design, then I'm all for it.
Lightning protection: Typically, lighting protection is one of the reasons cited for why homes usually have an Earth ground. If a lightning surge goes into your house wiring, then an Earth ground gives it somewhere to go so it's less likely to damage your electronics (or start a fire). On the other hand, adding an Earth ground actually makes your electrical system a more attractive target to lightning (by helping to create a low resistance path between the origin of the lighting and somewhere deep in the Earth). A much better protection from lightning is to create a separate lightning rod that provides a lower resistance pathway for the lightning than your house's electrical system. In addition, any nearby lightning strikes that miss your electrical system, could still cause damage to the electrical system by traveling through the ground in the nearby radius. For these reasons, I intend to install a separate, Earth grounded lighting rod...and as a result, it doesn't seem like there is no benefit to having an Earth ground on the house for lightning protection.
Shock protection: Typically, a house receives electricity from the mains power, which is grounded to Earth. If there is a short in an appliance whereby, say, one of the current carrying AC wires is shorted to the case of the appliance, and someone touches the appliance, then the person may form a lower resistance pathway from the case of the appliance to Earth ground, because the person is likely standing on Earth ground. This is often cited as a reason for having an Earth ground at the house: because if the appliance has a ground terminal, then the appliance case will be bonded to ground which goes all the way to Earth ground, and as a result, a person touching the case isn't going to be electrocuted. However, this protection is only necessary because the house power system is referenced to Earth ground in the first place. If the house had a floating ground, then the excess current wouldn't be searching for a pathway to Earth ground, and would have no reason to travel through the body of a person touching the electrified appliance case. It would be safe to touch the electrical wire, just as it is safe for a bird to land on an exposed electrical wire. So, when talking about an off-grid house, the desire for shock protection doesn't seem to motivate adding an Earth ground. In fact, it seems that a floating ground would be safer from a shock perspective standpoint, because that way a human standing on the ground will be unlikely to be on the lowest resistance pathway to complete a circuit.
All power to the house will come from the inverter -- either directly, as passed through from the battery system. Therefore, in the event of a broken appliance which has a short from a current carrying wire to the case, then the excess current will be searching for a path back to one of the inverter terminals. This seems like a decent reason to wire up my house's ground to one of the inverter terminals (say, negative)...as it would provide some circumstantial shock protection, although it seems the only possible circumstance would involve a person touching the inverter terminals while simultaneously touching a broken appliance case that is shorted out -- a pathologically unlikely circumstance.
Electrical interference: having the house grounded to Earth can introduce electrical disturbances into my own electronics, which at best is undesirable (eg, not great for HAM radio), and at worst, a danger, if there is a nearby lightning strike that energizes the house via the Earth ground.
Solar array: typically, the solar panel frames are all bonded together, and bonded to the house ground, which is of course bonded to the Earth ground. For better or worse, I did not run a ground through my buried conduit between the panels and the house, so it is not really possible for me to ground the panels to the house ground. However, I can't think of any reason to do so, other than by convention. The panels generate their own DC electricity, which is totally separate from the AC electricity generated by the inverter, so I don't see any reason why the two systems should want to share the same ground, especially if neither of them benefit from an Earth ground. The existence of the separate lightning protection system seems to eliminate any desire to bond the panels to Earth from a lighting protection perspective. From a shock protection perspective, I'm thinking perhaps it would be beneficial to bond the negative terminals of each panel to the solar panel frame assembly? But I don't think that is usually done.
Current plan: based on the above considerations, my current plan is to: a) bond the steel joists/I-beam of the house to the negative terminal of the inverter, to the ground wire in my main panel; b) not bother grounding the DC panel array; c) create an independent pathway to Earth ground in the form of a lightning rod, which is not connected to my AC or DC electrical systems.
Any thoughts/feedback is appreciated