Converting PSI Pressure Loss in a Pipe to Fluid Loss Rate

In summary: Welcome to the PF. :smile:In summary, the 8" PVC line at 150 PSI will leak if the test gauge drops 10 PSI per hour. The formula to determine gallons per hour lost is 1300 gallons of water plus more water to pressurize it.
  • #1
CWPeltzer
2
1
TL;DR Summary
Pipe Testing
Summary: Pipe Testing

I need some help on how to calculate PSI loss to gallons per hour?

We will be testing this 8" PVC line at 150 PSI for 4 hours. If the test gauge drops 10 PSI per hour, what is the formula to determine the gallons per hour lost?

Thank you for your help.
 
Last edited by a moderator:
Engineering news on Phys.org
  • #2
Welcome to the PF. :smile:

How long is the pipe? You are not replenishing the water in the pipe while running this test? So the leaked water is replaced by air that bubbles in via the leak?
 
  • #3
berkeman said:
Welcome to the PF. :smile:

How long is the pipe? You are not replenishing the water in the pipe while running this test? So the leaked water is replaced by air that bubbles in via the leak?
500' long with roughly 60 offset fittings. no we will not be adding water through test.

Thank you for the help
 
  • Like
Likes berkeman
  • #4
Are you aware of the property known as bulk compressibility? If so, how is it defined? Could you analyze this if the pipe did not get any smaller in total volume?
 
  • Like
Likes berkeman
  • #5
When you pump the water into the pipe, you are compressing:
1) The water, as @Chestermiller pointed out, and
2) Stretching the pipe, mostly increasing the diameter, and
3) Compressing any air bubbles trapped inside. With 500 feet of pipe and 60 fittings, I can guarantee there will be air bubbles.

It will take about 1300 gallons of water to fill that pipe, plus more water to pressurize it. I suggest filling the pipe until it is full, but not pressurized. Then measure the amount of water to pressurize it. One way is by pumping the water in through a water meter. Record the total amount every 10 PSI or so, and plot the results to get a graph of volume vs pressure. Draw a smooth line through the appropriate data points, and you will know exactly how much water per 1 or 10 PSI pressure drop. Here is one possible meter: https://www.mcmaster.com/4119k41. They also have other water meters.

The PVC might creep a little the first or second time you run the test, so repeat the test if the results are marginal. If the apparent leak rate decreases with successive tests, blame it on creep and/or trapped air bubbles dissolving into the water.
 
  • Like
Likes berkeman
  • #6
Do you have a pass/fail leak criteria for your pipe system; and, if so, who is determining this criteria i.e. is it your's internally or is it a customer's specification.
 
  • Like
Likes russ_watters
  • #7
Assuming negligible change in pipe volume and no dissolved air, for a water bulk modulus of 320000 psi, a 10 psi decrease corresponds to about 5 oz on 1300 gallons.
 
  • Like
Likes russ_watters and jrmichler
  • #8
Using std 8" sch 40 PVC pipe dimensions; and, PVC material physical data from the below reference, I calculate about 0.65 Gal / 10 psi will be expelled due to pipe diametrical and longitudinal contraction while reducing the test pressure from 150 to 0 psig with an initial 1300 gallon pipe filled volume at 0 psig.

https://www.usplastic.com/knowledgebase/article.aspx?contentkey=557
 
  • Like
Likes jrmichler
  • #9
Temperature changes will probably swamp your data. A 10 PSI decrease could be a 5 oz leak, or it could be a 0.2C temp decrease.
 
  • #10
Dullard said:
Temperature changes will probably swamp your data. A 10 PSI decrease could be a 5 oz leak, or it could be a 0.2C temp decrease.
@JBA showed that the pipe contraction swamps the liquid water expansion, and that the actual water loss for a 10 psi decrease will be more like 85 oz. And this is only for a 10 psi change.
 
Last edited:
  • #11
So what y'all are saying are that this is an ill-advised (and poorly designed) test. Can you make suggestions to the OP for a better test? The pipe is kind of long, but if it were shorter, they could maybe drain the water out afterward and compare that to the initial volume to find the leaked volume?

And to @CWPeltzer -- Who defined/required this test? Do they understand these pretty severe limitations? Do they just want to know if the fittings will leak?
 

Related to Converting PSI Pressure Loss in a Pipe to Fluid Loss Rate

1. How do I convert PSI pressure loss to fluid loss rate?

The formula for converting PSI pressure loss to fluid loss rate is: Fluid Loss Rate (gpm) = (Pressure Loss (psi) * Pipe Area (in²)) / (1,725 * Pipe Length (ft)). This formula takes into account the pressure loss in pounds per square inch (psi), the pipe area in square inches (in²), and the pipe length in feet (ft).

2. What is the significance of converting PSI pressure loss to fluid loss rate?

Converting PSI pressure loss to fluid loss rate is important in understanding the amount of fluid that is being lost in a pipe due to pressure. This information can be used to determine the efficiency of a system and identify potential leaks or issues.

3. Can I use the same formula for all types of pipes?

No, the formula for converting PSI pressure loss to fluid loss rate may vary depending on the type of pipe being used. Different types of pipes have different areas and lengths, which will affect the calculation. It is important to use the correct formula for the specific type of pipe being used.

4. How do I measure the pipe area and length?

The pipe area can be measured by finding the inside diameter of the pipe and using the formula for the area of a circle (A = πr²). The pipe length can be measured using a measuring tape or ruler. It is important to measure the length of the entire pipe, including any bends or curves.

5. Is there a way to simplify the conversion process?

Yes, there are online calculators and conversion charts that can help simplify the process of converting PSI pressure loss to fluid loss rate. These tools can be useful for quickly obtaining accurate results without having to manually calculate the conversion.

Similar threads

Replies
13
Views
3K
  • Mechanical Engineering
Replies
12
Views
2K
  • Mechanical Engineering
Replies
9
Views
645
Replies
8
Views
1K
  • Mechanical Engineering
Replies
8
Views
1K
  • Mechanical Engineering
Replies
11
Views
1K
  • Mechanical Engineering
Replies
3
Views
1K
Replies
10
Views
5K
Replies
6
Views
3K
Replies
1
Views
2K
Back
Top