- #1
Soumalya
- 183
- 2
Considering two thermal energy reservoirs, one at a higher temperature of TH compared to the other at TL, if we operate a reversible refrigeration cycle between the reservoirs then its coefficient of performance is given by,
COPR,rev=TL/TH-TL
This is the basically the maximum COP a refrigeration cycle can achieve operating between two thermal energy reservoirs at TH and TL.Since a Carnot refrigerator is a reversible refrigeration cycle the above expression for COPR,rev is valid for the reversed Carnot cycle.
If we consider any other reversible refrigeration cycle operating between the same two temperature limits it should have a similar COP as given by the above expression.Now considering a reversed Brayton cycle which is a reversible cycle (all processes are internally reversible) operating between two TERs at TH and TL,it should be given similarly as,
COPreversed brayton cycle=TL/TH-TL=COPreversed carnot cycle
But my textbook outlines that the COP of a reversed Brayton cycle is less than that of a reversed Carnot cycle operating under similar temperature limits.(Please refer to the attachment)
This seems contradictory as all reversible refrigerators should have the same COP operating between the same temperature limits.
Any thoughts?
COPR,rev=TL/TH-TL
This is the basically the maximum COP a refrigeration cycle can achieve operating between two thermal energy reservoirs at TH and TL.Since a Carnot refrigerator is a reversible refrigeration cycle the above expression for COPR,rev is valid for the reversed Carnot cycle.
If we consider any other reversible refrigeration cycle operating between the same two temperature limits it should have a similar COP as given by the above expression.Now considering a reversed Brayton cycle which is a reversible cycle (all processes are internally reversible) operating between two TERs at TH and TL,it should be given similarly as,
COPreversed brayton cycle=TL/TH-TL=COPreversed carnot cycle
But my textbook outlines that the COP of a reversed Brayton cycle is less than that of a reversed Carnot cycle operating under similar temperature limits.(Please refer to the attachment)
This seems contradictory as all reversible refrigerators should have the same COP operating between the same temperature limits.
Any thoughts?