In summary, the rated inductive current for a contactor is less than the rated resistive current because inductive loads such as motors experience significant inrush current. The contactor's utilization category (AC-1, AC-3, AC-4) will determine the required rated inductive current. The contactor must also be rated for unusual operating conditions, such as high ambient temperature, and more frequent operation.
srinaath
52
I have a elctromechanical contactor (contactor is an electrically operated switch - It is larger version of relay) which has following specification,
Inductive full load current - 30A
Resistive full load current - 40A
Why is rated inductive current less than rated resistive current?
Could you supply the manufacturer and part number of the contactor? Is the controlled load AC or DC?
Generally speaking, inductive current rating is lower because inductive loads such as motors experience significant inrush current.
Another specification to pay attention to is the kW or HP power rating.
Contactors for DC loads require more scrutiny during selection, and are often designed specifically for DC operation.
Likes Delta2
You already know the answer. What happens when you interrupt current through an inductor?
see section "Contact" about 1/3 of the way down this document.
https://media.digikey.com/pdf/Other%20Related%20Documents/Panasonic%20Other%20Doc/Small%20Signal%20Relay%20Techincal%20Info.pdf
Likes Asymptotic and davenn
great datasheet, @jim hardy thanks for that ... has been saved :)
Dave
Likes jim hardy
This has been answered in the posts above, but another, and perhaps more important question is, "What do you intend to use the contactor for?" A particular make and model contactor will be rated differently depending upon the application.
In the IEC world the nature of the application is called it's utilization category. Categories prefaced with "DC" describe DC load applications. AC-1 (switching AC to resistive loads), AC-3 (switching AC to squirrel cage induction motors in typical start-stop service), and AC-4 (same as AC-3, except the contactor must withstand locked rotor amp breaking currents encountered when the application includes inching and/or jogging service) are the most common. Transformer, capacitor, and various forms of lighting present different challenges to the contacts, and have their own utilization categories.
Unusual operating conditions must also be accounted for. For example, a manufacturer's specifications may be valid for 50 operations or less per hour, and a higher-rated contactor will likely be required to provide more frequent operation. Same goes for operation in high ambient temperature environments, and so on.
Siemens, ABB, Eaton-Cutler Hammer, Allen-Bradley, and other contactor manufacturers provide detailed information in their specifications, and typically offer additional sizing and application guidelines, for instance, "Low-Voltage Switchgear and Controlgear - An Application Guide", document # LVSAM-RM003A-EN-P from Allen-Bradley.
Likes jim hardy
Related to Current rating for an electromechanical contactor
What is the purpose of a current rating for an electromechanical contactor?
The current rating for an electromechanical contactor indicates the maximum amount of electrical current that the contactor can safely handle. This is important for preventing damage to the contactor and ensuring proper functioning of the electrical system.
How is the current rating for an electromechanical contactor determined?
The current rating is determined by the contactor's design, materials used, and the manufacturer's testing and certification processes. It is typically measured in amps (A) and can range from a few amps to several hundred amps.
Why is it important to match the current rating of a contactor to the electrical load?
Mismatching the current rating of a contactor to the electrical load can result in the contactor overheating and failing, which can lead to equipment damage or even electrical fires. It is crucial to select a contactor with a current rating that is equal to or greater than the current of the load.
What happens if the current rating of a contactor is exceeded?
If the current rating of a contactor is exceeded, it can cause the contactor to overheat and potentially melt or fuse together, resulting in a complete failure of the contactor. This can also create hazardous conditions and damage to the electrical system.