Efficiency Calculation of 10-kVA Transformer at 0.85 Power Factor Lagging

In summary, the given transformer has an efficiency of 89% when delivering its rated kVA at 0.85 power factor lagging. This is calculated by adding the core loss and copper loss, which are 450W and 600W respectively, and then dividing the rated output power by the total losses.
  • #1
graygoh
1
0

Homework Statement


A 10-kVA, 200:400 V transformer gave these test results:
open circuit (LV winding supplied): 200V, 3.2A, 450W
short circuit (HV winding supplied) : 38 V, 25A, 600W
calculate the efficiency when the transformer delivers its rated kVA at 0.85 power factor lagging

Homework Equations



efficiency = output power / input power

The Attempt at a Solution


I totally don't know how to start. help pls. thanks
 
Physics news on Phys.org
  • #2
graygoh said:
open circuit (LV winding supplied): 200V, 3.2A, 450W
This gives the core loss of the transformer.
Pi=450W
graygoh said:
short circuit (HV winding supplied) : 38 V, 25A, 600W
This gives the copper loss of the transformer at full load.
Pcu=600W
Iron loss is fixed loss and doesn't depend on the load. Copper loss varies proportional to the square of the current. In general, copper loss=x2Pcu, where x is the fraction of full load with which the transformer is loaded. Since the transformer is operated at full load, x=1 and the losses will be,
P=Pi+Pcu
=450+600=1.050kW.
Efficiency η= Output power/input power
=Output kW/(Output kW+losses)
∴ η=10×0.85/(10×0.85+1.050)
∴ η=0.89
The transformer is 89% efficient.
 
Last edited:

FAQ: Efficiency Calculation of 10-kVA Transformer at 0.85 Power Factor Lagging

How does a transformer work?

A transformer works by using electromagnetic induction to transfer electrical energy from one circuit to another. It consists of two or more coils of wire, known as the primary and secondary coils, which are wrapped around a shared iron core. When an alternating current (AC) is passed through the primary coil, it creates a magnetic field that induces a current in the secondary coil, resulting in the transfer of energy.

What is the difference between a step-up transformer and a step-down transformer?

A step-up transformer increases the voltage of an alternating current, while a step-down transformer decreases the voltage. This is achieved by varying the number of turns in the primary and secondary coils, which affects the strength of the magnetic field and the resulting voltage induced in the secondary coil.

How does the number of turns in a transformer's coils affect its performance?

The number of turns in a transformer's coils is directly proportional to its efficiency. More turns in the primary coil result in a stronger magnetic field and a higher induced voltage in the secondary coil. However, too many turns can also cause energy losses due to resistance in the wire, so it is important to find a balance between the number of turns and the desired voltage output.

What are the different types of transformers?

There are two main types of transformers: step-up and step-down transformers. Within these categories, there are also auto-transformers, isolation transformers, and instrument transformers. Auto-transformers have a shared winding between the primary and secondary coils, while isolation transformers have separate windings. Instrument transformers are used for measuring and monitoring purposes.

What are the main applications of transformers?

Transformers are used in a variety of applications, including power distribution, electrical appliances, and electronic devices. They are also used in renewable energy systems, such as wind and solar power, to convert the energy into a usable form. Additionally, transformers are used in industrial settings for voltage regulation and in medical equipment for diagnostic imaging.

Back
Top