Hi,
If you've got an arbitary magnetic Flux1 and Flux2, traveling in the same or opposite directions, through a core, it doesn't matter with regards to the point on the saturation curve does it? Opposing or in the same direction it'll still be at the same point on the mag curve won't it?Thanks a lot, I just need a sanity check
 
Engineering news on Phys.org
  • #2
The point at which the iron saturates will simply depend on the NET magnetic flux.
 
  • #3
uart said:
The point at which the iron saturates will simply depend on the NET magnetic flux.
Great, the magnetic moments don't fight each other, once they're full, they're full. I thought so. Thanks for the confirmation.
 
  • #4
It's no different to current in a wire in terms of how this superposition operates Tim.

Say you had a wire in a circuit which you analysed using superposition, and you found that it had 100A flowing from left to right and 90A flowing from right to left. Then the net current (10A from left to right) is the only one that is physically a real current. No fuse or other circuit element will "care" about the 100A, nor the 90A, they don't really exist. It is only the net current that matters. Same deal with your flux analogy.
 
  • #5
uart said:
It's no different to current in a wire in terms of how this superposition operates Tim.

Say you had a wire in a circuit which you analysed using superposition, and you found that it had 100A flowing from left to right and 90A flowing from right to left. Then the net current (10A from left to right) is the only one that is physically a real current. No fuse or other circuit element will "care" about the 100A, nor the 90A, they don't really exist. It is only the net current that matters. Same deal with your flux analogy.

Oh...oh...Well if that's true then say you had a 95A fuse on that wire, it wouldn't blow. So if I had a flux1 traveling in the opposite direction of flux2, and they're of equal magnitude, there'd be NO FLUX because the NET flux has canceled out?? And it's only saturated when they're in the same direction?

One reason I ask is because if you've got a Short Circuit secondary TX the flux from the primary will cause by lenz's law an current to flow which creats a flux to oppose the primary flux. So I imagine the net flux will be low or zero, does this mean this case is different to just going up the saturation B vs H curve? Because this would mean it has a LOW B, yet still has no inductance on the primary and so the primary is acting like a short circuit.

Thanks
 
Last edited:
  • #6
tim9000 said:
and so the primary is acting like a short circuit.

uart speaks truth.

C'mon tim, finish your thought, you're soooo very nearly there...
Indeed, more current will rush into the primary.

What does that increased primary current do to flux?
 
  • #7
jim hardy said:
uart speaks truth.

C'mon tim, finish your thought, you're soooo very nearly there...
Indeed, more current will rush into the primary.

What does that increased primary current do to flux?

Ahaha, oh, yeah, the story doesn't end there, the primary will oppose the decrease in flux ...so where does B of the core end up in steady state? Somewhere in the middle? I'd have to guess the primary overwhelms the flux of the secondary, saturates the core AND THAT'S WHAT CAUSES heaps of current to be drawn by the primary, and flow in the secondary.
 
  • #8
tim9000 said:
I'd have to guess the primary overwhelms the flux of the secondary,

Why would it overwhelm ?

Why couldn't they balance?

Maybe your trouble is in thinking about fluxes. While that's mathematically valid, as uart points out there's only one flux.

Have you forgotten about mmf, magneto-motive-force, that pushes flux ? It's measured in amp-turns.

Sum of the amp-turns is what's available to push flux around the core.
So what balances is the MMF's. (Primary mmf - Secondary mmf )/ ℝeluctanceof core = flux

How much flux must there be? Somewhere between zero and saturation, surely.
Just enough to match voltage applied to primary (minus IR drop there)..
 
  • #9
jim hardy said:
Why would it overwhelm ?

Why couldn't they balance?

Maybe your trouble is in thinking about fluxes. While that's mathematically valid, as uart points out there's only one flux.

Have you forgotten about mmf, magneto-motive-force, that pushes flux ? It's measured in amp-turns.

Sum of the amp-turns is what's available to push flux around the core.
So what balances is the MMF's. (Primary mmf - Secondary mmf )/ ℝeluctanceof core = flux

How much flux must there be? Somewhere between zero and saturation, surely.
Just enough to match voltage applied to primary (minus IR drop there)..
Point 1: Ok, so under shorted secondary condition: the Primary MMF will be Number of primary turns * [ Voltage on primary / (resistance of primary wire + internal impedance of voltage source) ] ?
as per the picture:
t.png


And the primary MMF is significantly greater than the secondary?

Is it fair to say that any section of core with a winding on it can be modeled as a reluctance and an MMF, irrespective of which is infront of wich, so long as they're in series next to each other?

Point 2: [below] Because I know if Nm is 10, then the flux in the middle section double the two outter sections, but what if Nm is higher or lower, what will the flux in the circuit be then? What if Nm was 5 or 20 turns?
Will the current flowing through them make the flux through all the them be the same?
figure out.png
 
Last edited:
  • #10
tim9000 said:
Point 1: Ok, so under shorted secondary condition: the Primary MMF will be Number of primary turns * [ Voltage on primary / (resistance of primary wire + internal impedance of voltage source) ] ?
as per the picture:

your red V = Vsource should read V = Vsource - I X (Rsource + Rwinding)

tim9000 said:
And the primary MMF is significantly greater than the secondary?
Significantly? By just enough to magnetize the core, flux/reluctance. By an amount about the same as transformer's no-load magnetizing current X Nprimary.

tim9000 said:
Is it fair to say that any section of core with a winding on it can be modeled as a reluctance and an MMF,...
sounds fair

tim9000 said:
irrespective of which is infront of wich, so long as they're in series next to each other?
I think so. mmf's in series add just as do emf's, and reluctances in series add just as do resistances.

tim9000 said:
Point 2: [below] Because I know if Nm is 10, then the flux in the middle section double <<[make that SUM OF ] the two outter sections, but what if Nm is higher or lower, what will the flux in the circuit be then? What if Nm was 5 or 20 turns?
Will the current flowing through them make the flux through all the them be the same? <<No, electrical current causes MMF. Flux is analogous to current because it flows in proportion to MMF.
Flux flows in closed loops, just like current. So you solve picture below just like a DC electric circuit using Kirchoff's laws. Sum of mmf's around any closed loop is zero, sum of fluxes at any junction is zero.
Solve it by branch or loops just as if it were an electrical circuit instead of magnetic.
Each winding is a MMF source and each reluctance is a MMF drop, flux X reluctance.

Ohm's law for magnetic circuits: MMF = Flux X Reluctance , or (Amp-Turns) = Webers X (Amp-Turns per Weber)
So traversing around either branch you'll encounter two mmf sources and two mmf drops. Assign polarities and write the sums. Kirchoff rules !
Write your KVL equations in terms of mmf and ℝ(for reluctance).


figure-out-png.81066.png
http://en.wikipedia.org/wiki/Magnetic_circuit#Hopkinson.27s_law:_the_magnetic_analogy_to_Ohm.27s_law
Hopkinson's law: the magnetic analogy to Ohm's law
In electronic circuits, Ohm's law is an empirical relation between the EMF
fbd3f8f623c8a757a55dcc4f30410355.png
applied across an element and the current I it generates through that element. It is written as:

a3efa262fc42e1f75d4022737eaf0076.png

where R is the electrical resistance of that material. Hopkinson's law is a counterpart to Ohm's law used in magnetic circuits. The law is named after the British electrical engineer, John Hopkinson. It states that[3][4]

71f3a048d0507350fda26bd376e3ae1b.png

where
5e78a8f41cf96997100080668c97132f.png
is the magnetomotive force (MMF) across a magnetic element,
d70bcd6d6326bba398f9a1d064c0914a.png
is the magnetic flux through the magnetic element, and
ba8db5353eefcf2edc621e0660dbbab9.png
is the magnetic reluctance of that element.
 
Last edited by a moderator:
  • #11
jim hardy said:
your red V = Vsource should read V = Vsource - I X (Rsource + Rwinding)
Ah! yes, thank you.

jim hardy said:
Significantly? By just enough to magnetize the core, flux/reluctance. By an amount about the same as transformer's no-load magnetizing current X Nprimary.
These two questions are critical for some pieces of the puzzel falling into place:
Riiiight, so the permeability mu is still high enough for the inductance of the core to be substantial? Even though the primary is drawing a lot of current? I perhaps made the incorrect assumption that the inductance would drop, but if the inductance is quite high than so is the VARs it's drawing?
[/QUOTE]

Ok Jim, so I can have an two equal MMF sources in a set-up like above, but one can have more flux passing through it than the other, there's no problem with that?

For some reason I've been thinking each MMF source could only pass as much flux as it created.
 
  • #12
tim9000 said:
Riiiight, so the permeability mu is still high enough for the inductance of the core to be substantial? Even though the primary is drawing a lot of current? I perhaps made the incorrect assumption that the inductance would drop, but if the inductance is quite high than so is the VARs it's drawing?

Maybe we're not using "inductance" in the same sense.

Inductance is a property of a structure, determined by its permeability , length, area, and how many turns encircle it.
L = μ0μrN2Area/Length

Old books use another term "Induction" to describe how much magnetic flux is flowing in a magnetic circuit.

Further complicate that by definition of inductance being NΦ/I , flux linkages per ampere, and we now have a mishmash of similar words that draw the mind to mix up basic concepts.
That's the trouble with English versus Math... Back to Lavoisier, below...

When i feel and hear a transformer humming because of the flux in its core swapping direction 120 times a second, i think "Now there's induction. There's enough flux in there to support 120 volts on its primary".

By contrast when i look at its windings i say " That'll have inductance because it's wires encircle some area, mu X n^2 X area/length"
Lavoisier said:
The impossibility of separating the nomenclature of a science from the science itself, is owing to this, that every branch of physical science must consist of three things; the series of facts which are the objects of the science, the ideas which represent these facts, and the words by which these ideas are expressed. Like three impressions of the same seal, the word ought to produce the idea, and the idea to be a picture of the fact. And, as ideas are preserved and communicated by means of words, it necessarily follows that we cannot improve the language of any science without at the same time improving the science itself; neither can we, on the other hand, improve a science, without improving the language or nomenclature which belongs to it. However certain the facts of any science may be, and, however just the ideas we may have formed of these facts, we can only communicate false impressions to others, while we want words by which these may be properly expressed.
https://web.lemoyne.edu/giunta/lavpref.html
tim9000 said:
Ok Jim, so I can have an two equal MMF sources in a set-up like above, but one can have more flux passing through it than the other, there's no problem with that?
That's just fine.

tim9000 said:
For some reason I've been thinking each MMF source could only pass as much flux as it created.
No such rule.
You are still developing your basics of flux and MMF. Read that Hopkinson's page linked above.
 
  • #13
jim hardy said:
Maybe we're not using "inductance" in the same sense.

Inductance is a property of a structure, determined by its permeability , length, area, and how many turns encircle it.
L = μ0μrN2Area/Length

Old books use another term "Induction" to describe how much magnetic flux is flowing in a magnetic circuit.

Further complicate that by definition of inductance being NΦ/I , flux linkages per ampere, and we now have a mishmash of similar words that draw the mind to mix up basic concepts.
That's the trouble with English versus Math... Back to Lavoisier, below...

When i feel and hear a transformer humming because of the flux in its core swapping direction 120 times a second, i think "Now there's induction. There's enough flux in there to support 120 volts on its primary".

By contrast when i look at its windings i say " That'll have inductance because it's wires encircle some area, mu X n^2 X area/length"

https://web.lemoyne.edu/giunta/lavpref.html
That's just fine.No such rule.
You are still developing your basics of flux and MMF. Read that Hopkinson's page linked above.

Thanks for the response, it was helpful.
I was inafact using the definition of Inductance you gave first: L = μ0μrN2Area/Length
However I should have perhaps used the term impedance. It is the specific concept of opposing (Net) Flux and how it affects the aformentioned Inductance that I'm addressing, I'll rephrase:

So with a TX that has a shorted secondary, there are two opposing MMFs: (Primary mmf - Secondary mmf ) / ℝeluctanceof core = Net flux

There is a large current in both primary and secondary. As you said this will result in the Secondary coil producing just enough flux to match the primary voltage. You also said "How much flux must there be? Somewhere between zero and saturation, surely." So there is a Net Flux, meaning that the Primary MMF is in some magnitude bigger than the Secondary. But surely it is more one end of the Mag curve than the other.
You said that two opposing fluxes that Net near zero will have a mag density of B near zero.
(Side observation: when a transformer saturates, the permiability drops and the impedance drops, so it draws heaps of current)
What I previously was getting at was that, since the Primary current is quite high and there would be a number of turns, then the MMFs are quite high, But B in the core is quite low, then I was thinking the impedance of the transformer would still be quite high, and the inuctance would still be quite high.
Thus it would draw a lot of VARs. I'll run through how I see it:

Fluxfrom Pri = Vpri/ [Npri turns*wfreq of supply]
this in turn makes the shorted secondary produce a counter flux of:
Nsecondary turns*[(emf= Nsecondary turns*d(flux)/dt) / resistance of secondary]
is Flux from Sec= Nsecondary turns*[(emf= Nsecondary turns*{Peak Fluxfrom pri/wfrequency of supply} / resistance of secondary]
Thus
Net Flux = {Fluxfrom Pri - Flux from Sec} / Reluctance

So since the Inductance of the TX is L = μ0μrN2Area/Length and μ depends on B which is low meaning μ is quite high, than L is quite high and X = 2wL
then the Icurrent in primary*X is a lot of Vars?

You're thoughts?

Thanks!
 
  • #14
tim9000 said:
What I previously was getting at was that, since the Primary current is quite high and there would be a number of turns, then the MMFs are quite high,

Good. There will be large opposing mmf's .

But B in the core is quite low,
You're still speaking of transformer with short circuited secondary? Yes flux will be low.

then I was thinking the impedance of the transformer would still be quite high, and the inuctance would still be quite high
slow down... you take the stairs too many at a time..
wiki has a pretty decent link... http://en.wikipedia.org/wiki/Transformer
"" impedance of the transformer would still be quite high, and the inuctance would still be quite high ""
Which impedance? Which inductance?
500px-TREQCCT.jpg

Fluxfrom Pri = Vpri/ [Npri turns*wfreq of supply
Remember that applied voltage divides between primary losses and counter-emf ,
so counter-emf is only that fraction of applied voltage not dropped as primary losses I X (Rp +jXp).
So your Vpri = Vapplied - I X (Rp +jXp) which will be fairly small .
i think the rest of that paragraph is okay though.

So since the Inductance of the TX is L = μ0μrN2Area/Length
That would be XM, magnetizing inductance,
and μ depends on B which is low meaning μ is quite high,
i don't think that's right.

You've made a false leap . We all want the answer to be easy, and it is but it's several steps to get there not one.
The mind will concatenate words and fool us.
μ is quite high because the core is made from good ferromagnetic material.
http://hyperphysics.phy-astr.gsu.edu/hbase/solids/ferro.html#c5
When ferromagnetic materials are used in applications like an iron-core solenoid, the relative permeability gives you an idea of the kind of multiplication of the applied magnetic field that can be achieved by having the ferromagnetic core present. So for an ordinary iron core you might expect a magnification of about 200 compared to the magnetic field produced by the solenoid current with just an air core. This statement has exceptions and limits, since you do reach a saturation magnetization of the iron core quickly, as illustrated in the discussion of hysteresi

What is changing is not permeability and inductance. , but flux and counter-emf; induction..
That leaves primary current at the mercy of winding resistances Rp & Rs, and leakage reactances Xp & Xs.
Those are 'necessary evils' so kept low on purpose.

tim9000 said:
than L is quite high and X = 2wL

L is not changed
then the Icurrent in primary*X is a lot of Vars?

And a lot of watts.

Primary current is high because there's hardly any counter-emf induced to oppose it
so what limits Iprimary ?
Winding resistances and leakage reactances.
Both of those are 'necessary evils', kept low on purpose.
That's why primary current is high.

It's important to work your mental model until it leads you to the right formula.
μ is not truly constant but for first approximations we treat it as constant, refining only when called for.

You're getting there. Study that wiki equivalent circuit.
Visualize that flux inside the core.
 
  • #15
Thanks Jim, you're practically my mentor :p
jim hardy said:
Good. There will be large opposing mmf's .

You're still speaking of transformer with short circuited secondary? Yes flux will be low.
slow down... you take the stairs too many at a time..

"" impedance of the transformer would still be quite high, and the inuctance would still be quite high ""
Which impedance? Which inductance?
Sorry I should have been more clear, the magnetising impedance Xm and the Inductance of the Primary.
jim hardy said:
Remember that applied voltage divides between primary losses and counter-emf ,
so counter-emf is only that fraction of applied voltage not dropped as primary losses I X (Rp +jXp).
So your Vpri = Vapplied - I X (Rp +jXp) which will be fairly small .
Hmm, ok, Hopefully you can help me sort out what's going on with the Counter-EMF, with regard to your diagam:
]
oxy.php?image=http%3A%2F%2Fupload.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F3%2F39%2FTREQCCT.jpg

So the current IO through the core impedance won't change, but the counter EMF Ep is usually quite high, but with a secondary short, the counter EMF is low, so heaps of current flows through primary and secondary? (I didn't think that was right because I thought the part of Ep was the ideal transformer and no currnt flowed through an ideal transformer) but that's the only place where I see counter emf and where else could the current flow?
[As a side note let me see if I remember what the counter EMF IS: As the Vapplied resulting Current goes into the primary, causes a flux, that flux goes round and comes back through the primary coils, the coils try to produce a counter flux to oppose the origianl flux's return, via Lenz's law, and the coil does this by inducing a counter EMF Ep. Is that right?]
jim hardy said:
i don't think that's right.
You've made a false leap . We all want the answer to be easy, and it is but it's several steps to get there not one.
The mind will concatenate words and fool us.
Sorry what I should have said was that μ is a property of the steel that we can observe from the B vs H relationship. (Good to know that inductance and Magnetising impedance is still as high as it would be if there was an open circuit secondary) But what is/was confusing me is that usually I'd think of the graph:
perm.PNG

And I'd think, 'not much flux, B is low, μ must be low', but I can't use that graph here. MMF H ~ NI, and since I is large, N is substantial and constant, then H is large, but B on the graph is NET B, which is low, thus μ is low. That's what I meant.

I think I'm getting my mental model close, thanks to your help.
 
  • #16
tim9000 said:
So the current IO through the core impedance won't change,
oxy.php?image=http%3A%2F%2Fupload.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F3%2F39%2FTREQCCT.jpg


observe IO is in proportion to applied voltage Vp minus I X(Rp + Xp)
Xm is impedance due to primary inductance, and Rc is core loss, ohm's law applies
tim9000 said:
but the counter EMF Ep is usually quite high, but with a secondary short, the counter EMF is low, so heaps of current flows through primary and secondary?
Yes. Counter emf is low because secondary mmf has canceled almost all the primary mmf . Not much flux but large opposing mmf's.

tim9000 said:
(I didn't think that was right because I thought the part of Ep was the ideal transformer and no currnt flowed through an ideal transformer) but that's the only place where I see counter emf and where else could the current flow?
An ideal transformer needs no magnetizing current, that's why Xm in model is is to left of it.
But an ideal transformer has primary current equal to secondary current(load current) X turns ratio.

tim9000 said:
[As a side note let me see if I remember what the counter EMF IS: As the Vapplied resulting Current goes into the primary, causes a flux, that flux induces counter-emf ndΦ/dt in the primary , and is shown as Ep in the model above. goes round and comes back through the primary coils, the coils try to produce a counter flux to oppose the origianl flux's return, via Lenz's law, and the coil does this by inducing a counter EMF Ep. Is that right?]

Under shorted secondary, what limits current? Look at the model.

tim9000 said:
But what is/was confusing me is that usually I'd think of the graph:
perm-png.81219.png
remember we operate transformers below saturation.
Where's saturation on your graph?
BHCurveU.gif

https://www.nde-ed.org/EducationResources/CommunityCollege/MagParticle/Physics/Permeability.htm
 
  • #17
Here's a good link for magnetizing iron.
http://phys.thu.edu.tw/~hlhsiao/mse-web_ch20.pdf

see fig 20.13
 
Last edited by a moderator:
  • #18
jim hardy said:
oxy.php?image=http%3A%2F%2Fupload.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F3%2F39%2FTREQCCT.jpg


observe IO is in proportion to applied voltage Vp minus I X(Rp + Xp)
Xm is impedance due to primary inductance, and Rc is core loss, ohm's law applies

An ideal transformer needs no magnetizing current, that's why Xm in model is is to left of it.
But an ideal transformer has primary current equal to secondary current(load current) X turns ratio.
Aah, ok Let me see If I've got this straight: so on that diagram, even though it is an ideal transformer on the right, the bulk of the large current DOES flow through it and Ep which is through (Np), and is limited only by: Rp, Rs and the small counter-EMF ofcourse. And THATs where the lion's share of the Power is burnt. As the magnetising branch will only use:
(Vp - I*(Rp + Xp))2/ Xm Watts
Which is less power in the mag branch than for a non-shorted secondary because I is so much higher through the coils and thus the voltage on them detracts from the voltage on Xm.

Right so "counter-emf ndΦ/dt in the primary" is the counter emf in the secondary depending on the turns of the secondary. That's faraday and Lenz's laws I gather.

jim hardy said:
Where's saturation on your graph?
BHCurveU.gif

https://www.nde-ed.org/EducationResources/CommunityCollege/MagParticle/Physics/Permeability.htm
Saturation on my graph is at the top right, and I imagine opperating a shorted secondary TX is below the maximum tangent of your hysteresis quadrant. What I was saying before was that when I first started this thread I was thinking that there were huge magnetising forces (H was really high) however they're opposing each other, so NET H is far to the left of the graph, likewise for B.

If what I wrote above regarding the power is correct then I think you may have cracked it for me, this is a fundementally different way I'm viewing where the current is going than when I started the thread. THANKS
 
  • #19
tim9000 said:
And THATs where the lion's share of the Power is burnt. As the magnetising branch will only use:
(Vp - I*(Rp + Xp))2/ Xm Watts ? look again at that model, magnetizing branch watts go into core loss Rc . Might you have meant vars into Xm ?
Which is less power in the mag branch than for a non-shorted secondary because I is so much higher through the coils and thus the voltage on them detracts from the voltage on Xm.
yes to that logic .
tim9000 said:
Right so "counter-emf ndΦ/dt in the primary" is the counter emf in the secondary depending on the turns of the secondary.
Secondary turns see same dΦ/dt, but we don't call its voltage counter emf.

tim9000 said:
If what I wrote above regarding the power is correct then I think you may have cracked it for me, this is a fundementally different way I'm viewing where the current is going than when I started the thread. THANKS

Glad it helped.
Feels good, doesn't it? Work transformers in your head next few weeks until it's intuitive how they balance mmf's.,

Then take a break and read that Lavoisier introduction to treatise on chemistry i linked way back... When i was a young man he affected my thinking process for the better. Pay particular attention to his Abbe de Condillac quote, it's outrageously funny, and happens all the time
old jim
 
  • #20
Sorry I should have said the mag branch (Xm, Rc) will use less VARs, not watts.

jim hardy said:
Secondary turns see same dΦ/dt, but we don't call its voltage counter emf.

Glad it helped.
Feels good, doesn't it? Work transformers in your head next few weeks until it's intuitive how they balance mmf's.,

Then take a break and read that Lavoisier introduction to treatise on chemistry i linked way back... When i was a young man he affected my thinking process for the better. Pay particular attention to his Abbe de Condillac quote, it's outrageously funny, and happens all the time

old jim
Over the next week I will read Lavoisier's treatise, thanks.
If this is wrong that correct it, if not, then no need to reply: Just to be doubly clear, you did say that the current that flows into the 'ideal' transformer part is IP , where IS = IP/a
when the transformer is not Open circuit.

Great, again another misconception I was opperating under was that the ideal transformer had no current in it, but what you said was that the ideal transformer had not 'magnetising current' flowing through it (the mag branch was taken out so that could happen elsewhere), it will still have Ip and Is flowing through it. I'm not sure why I get muddled up like this but hopefully that'll be the last time. Thanks again Jim, have a good one!
 
  • #21
tim9000 said:
If this is wrong that correct it, if not, then no need to reply: Just to be doubly clear, you did say that the current that flows into the 'ideal' transformer part is IP , where IS = IP/a

You're quite right.

And i missed something in that model... look at the little trick they used, it's not obvious at first (wasn't to me anyway) :
They made their ideal transformer 1::1 and moved secondary side leakage inductance Xs and secondary resistance Rs over to primary side.
oxy.php?image=http%3A%2F%2Fupload.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F3%2F39%2FTREQCCT.jpg

Then they re-named the current flowing into ideal transformer's primary winding IS !
I'd have named it Ip - (IC + jIM) , and shown IS on secondary side with Xs and Rs there too.BUT since the transformer is ideal, their relocation of secondary impedances to primary after correcting for turns ratio, works just fine.
Kirchoff tells us that my Ip - (IC +jIM) equals their IS .

So i stand corrected.

I think you have it now
good job and thanks for sticking with it.
To help young folks over the same hurdles i struggled with makes an old guy feel a little less useless.
Today's curricula seem more math intensive than in my day.
I hope they still have labs.

Best of luck in your studies, and in your career.

old jim
 

FAQ: Flux Direction effect on Saturation, Quick Question

1. How does flux direction affect the saturation of a substance?

Flux direction refers to the direction in which a substance is moving in relation to the surface of a material. When a substance is moving parallel to the surface, it can increase the rate of diffusion and therefore lead to higher saturation. On the other hand, when a substance is moving perpendicular to the surface, it can decrease the rate of diffusion and result in lower saturation.

2. What is the relationship between flux direction and saturation?

The relationship between flux direction and saturation is inverse. This means that as the flux direction increases, the saturation decreases, and vice versa. This is due to the fact that flux direction affects the rate of diffusion, which ultimately determines the level of saturation.

3. Can the flux direction affect the saturation of all substances?

Yes, the flux direction can affect the saturation of all substances. This is because all substances have different diffusion rates and properties, which can be influenced by the direction in which they are moving. For example, a substance with a low diffusion rate may experience a significant change in saturation when the flux direction is altered.

4. Does the temperature of the substance affect the flux direction?

No, the temperature of the substance does not directly affect the flux direction. However, temperature can indirectly impact the saturation by altering the diffusion rate of the substance. Higher temperatures can lead to higher diffusion rates, which can then affect the flux direction and ultimately the saturation.

5. How can the flux direction effect on saturation be measured?

The effect of flux direction on saturation can be measured by conducting experiments where the flux direction is controlled and the resulting saturation is measured. This can be done using various techniques such as spectrophotometry or gravimetric analysis. Additionally, mathematical models and simulations can also be used to predict the effect of flux direction on saturation.