- #36
knightsof3
- 14
- 4
So we finally got the vendor back with the load bank. We reinstalled the burden resistor across the CT and viola we cranked the generator right up to 570 kW with no issues. Problem solved! Thanks everyone! Now what's going to eat away at me is the electrical theory aspect of why with no ground fault current and with the CT core both not a fully rectane and also installed correctly fully enclosed, how was a voltage being induced onto the secondary winding of the CT? I guess without the burden resistor the secondary circuit is an open circuit but how was anything at all being induced into secondary circuit to mess with the solid stare ground fault relay? And why was at always when we went over 350 kW, 400+ amps? It consistently tripped at the exact point. My mind would think that if the CT secondary open circuit is screwy it would just trip the unit as soon as a load is applied? Any electrical theory thoughts on why an open circuit CT gets an output at with no magnetic field from the load cables?jim hardy said:well i think you're almost there...
with that resistor missing it'll be spectacularly oversensitive.
If you can hang a simple battery handheld 'scope across it it'd sure be interesting to see the waveform . 60 hz, 180 hz, or a mix ?
old jim