To select a suitable heat exchanger for cooling 28 liters per minute from 70°C to 25°C, it is essential to calculate the required cooling capacity using the kw/C metric. The kw/C value indicates how much power the heat exchanger can remove for each degree Celsius of temperature rise. For this scenario, the energy to be extracted is approximately 92 kW/s, leading to a required kw/C of 2.04. It is crucial to ensure that the chosen radiator can achieve this cooling effect at the specified flow rate. Accurate calculations are vital, as the kw/C metric may not hold true at extreme energy inputs.
Su Solberg
Messages
72
Reaction score
0
Hello, everyone.

I have a problem in finding a suitable heat exchanger for cooling coils.
I would like to cool down 28 lier/min; from 70 Celsius to at least 25 Celsius.

I wonder how to fit "kw/C"(performance spec.) to my case so that i can find a suitable heat exchanger.

Thanks for your help.
 
Engineering news on Phys.org
kw/C is a measure of how much power (kw) the heatsink can remove for each degree C temperature it rises.
Once the heat sink reaches the temperature of the incoming hot fluid it is obviously not going to remove any more heat.

You can work out the amount of energy to be extracted each second to cool 28/60 litres of water by 45 C and then from the kw/c work out how much this will heat the heatsink.

Note - this is just an approximation - the kw/c is only correct for a certain amount of power. At very high or very low energy inputs it might not be accurate..
 
mgb_phys said:
kw/C is a measure of how much power (kw) the heatsink can remove for each degree C temperature it rises.
Once the heat sink reaches the temperature of the incoming hot fluid it is obviously not going to remove any more heat.

You can work out the amount of energy to be extracted each second to cool 28/60 litres of water by 45 C and then from the kw/c work out how much this will heat the heatsink.

Note - this is just an approximation - the kw/c is only correct for a certain amount of power. At very high or very low energy inputs it might not be accurate..

Thanks for your reply.

To confirm your meaning, is that mean suppose the water will reject heat 92kw/s (from 70->25;Q=M*Cp*(T1-T2) ) then the kw/C required is 92kw/45C=2.04kw/c.

That's mean I have to find a radiator that can achieve 2.04kw/c cooling effect at 28l/min?

Thanks for your help.
 
LEt see, you need 60 liters per minute of Water to drop from 70 down to 25 C?
 
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...
Thread 'What type of toilet do I have?'
I was enrolled in an online plumbing course at Stratford University. My plumbing textbook lists four types of residential toilets: 1# upflush toilets 2# pressure assisted toilets 3# gravity-fed, rim jet toilets and 4# gravity-fed, siphon-jet toilets. I know my toilet is not an upflush toilet because my toilet is not below the sewage line, and my toilet does not have a grinder and a pump next to it to propel waste upwards. I am about 99% sure that my toilet is not a pressure assisted...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
Back
Top