Tiberious
- 73
- 3
Poster reminded to use the standard Template for schoolwork
Question - Four
A pipe carrying superheated steam at 300 °C has an outside diameter of 120 mm and is lagged with two layers of insulating material. The first layer (adjacent to the outer pipe wall) is 25 mm thick and has a thermal conductivity of 0.072 W m-1 K-1. The second layer (covering the first layer) is 20 mm thick, has a thermal conductivity of 0.051 W m-1 K-1 and an outside temperature of 28 °C.
Estimate the rate of heat loss per metre length of pipe (assume the thermal resistance of the pipe wall is negligible).
SOLUTION:
Determining r_1
r_1=(120/2)mm
= 60 mm
Determining r_2
r_2=( 120/2+25)mm
= 85 mm
Determining r_3
r_3=(( 120/2+25)+20)mm
= 105 mm
Rate of heat loss ϕ= (Total temperature difference)/ΣR
Determining R_12
R_12= in(r_2/r_1 )/(2πLk_12 )
= in(85/60)/(2π∙1∙0.072)
= 0.7699..K W^(-1)
Determining R_23
R_23= in(r_3/r_2 )/(2πLk_12 )
= in(105/85)/(2π∙1∙0.051)
= 0.6594..K W^(-1)
Determining ΣR
ΣR= R_12+R_23
=0.7699..+0.6594..
= 1.4293..K W^(-1)
Temperature difference between the two points
T_1-T_2=300-28=272°C
Hence
ϕ= 272/(1.4293..)
= 190.30 W
≈190 W per metre length of pipe
SOLUTION:
Determining r_1
r_1=(120/2)mm
= 60 mm
Determining r_2
r_2=( 120/2+25)mm
= 85 mm
Determining r_3
= 105 mm
Determining R_12
= 0.7699..K W^(-1)
Determining R_23
= 0.6594..K W^(-1)
Determining ΣR
ΣR= R_12+R_23
=0.7699..+0.6594..
= 1.4293..K W^(-1)
Hence
ϕ= 272/(1.4293..)
= 190.30 W