Heat Transfer with Recirculating Chiller Problem

  • #1
kishanb_01
6
0
TL;DR Summary
Using a recirculating chiller to cool an insulated container via copper tubing clamped to an aluminum plate. Chiller cools water 30°C to 10°C in 5 mins, but plate takes 40 mins to reach 12°C. Seeking insight on why actual cooling is slower than calculated estimates.
Hi All,
So I am trying to use a recirculating chiller to cool/heat an insulated container. This chiller sends deionized water through silicone tubing that enters the insulated container it then is passed through copper tubing in the container before it goes back through silicone tubing to go back to the chiller. The copper tubing fits into a slot on an aluminum plate that I am effectively trying to cool. The copper tubing is also clamped to this plate. The chiller has a temperature display on it that tells me the apparent temperature of the water. It tells me that effectively the temperature can go from 30 °C to 10 °C in 5 minutes. I have attached a temperature sensor to the aluminum plate to find that it takes around 40 minutes to reach 12 °C. I am trying to calculate if this temperature change should be this slow but have found from my calculations that the temperature change should be much faster. Im hoping someone can offer me an explanation as to why my math doesn't match my actual results.
1734699702854.png
1734699709491.png
1734699714757.png
1734699721932.png
1734699731023.png
 
Engineering news on Phys.org
  • #2
Are you trending the return water temperature or just the supply? If you have the return water temperature also(wait - do you also not have flow rate?), you can calculate the exact heat removal. Having only the supply temperature and volume tells you very little.

My guess is you're not on the chiller performance curve because of a mismatch in assumed conditions -- likely flow rate.
 
  • #3
russ_watters said:
Are you trending the return water temperature or just the supply? If you have the return water temperature also(wait - do you also not have flow rate?), you can calculate the exact heat removal. Having only the supply temperature and volume tells you very little.

My guess is you're not on the chiller performance curve because of a mismatch in assumed conditions -- likely flow rate.
The chiller is operating at a flow rate of 12 LPM. If I were to figure out the return waters temperature with respect to time how could I then find the calculated time to cool?
 
  • #4
kishanb_01 said:
The chiller is operating at a flow rate of 12 LPM.
Measured or assumed?

kishanb_01 said:
If I were to figure out the return waters temperature with respect to time how could I then find the calculated time to cool?
If you measure it you have the real cooling rate over time:
Q=M* Cp (Treturn - Tsupply)

Q=heat flow rate
M=mass flow rate.

Trend it and then numerically integrate it and you'll have total heat removed.

If I had to guess, I'd guess that your flow rate is less than you think, so you are removing less heat than you think.
 
  • Like
Likes kishanb_01 and berkeman
  • #5
russ_watters said:
Measured or assumed?


If you measure it you have the real cooling rate over time:
Q=M* Cp (Treturn - Tsupply)

Q=heat flow rate
M=mass flow rate.

Trend it and then numerically integrate it and you'll have total heat removed.

If I had to guess, I'd guess that your flow rate is less than you think, so you are removing less heat than you think.
I am assuming the flow rate given this chart given by the chiller manufacturer and the pressure gage reading on the device
1734712355046.png
 
  • #6
russ_watters said:
Measured or assumed?


If you measure it you have the real cooling rate over time:
Q=M* Cp (Treturn - Tsupply)

Q=heat flow rate
M=mass flow rate.

Trend it and then numerically integrate it and you'll have total heat removed.

If I had to guess, I'd guess that your flow rate is less than you think, so you are removing less heat than you think.
This makes sense my follow up question is if I am removing less heat than I think what is a possible way I could increase this to get to the cooling capacity specification
 
  • #7
kishanb_01 said:
I am assuming the flow rate given this chart given by the chiller manufacturer and the pressure gage reading on the device View attachment 354695
What is your pressure differential across the chiller or the pump. Inlet pressure - outlet pressure? I ask because you say "pressure gauge reading" - singular.
 
Last edited:
  • Like
Likes russ_watters
  • #8
erobz said:
What is your pressure differential across the chiller or the pump. Inlet pressure - outlet pressure? I ask because you say "pressure gauge reading" - singular.
That I'm not too sure The gauge on the device is measuring the outlet pressure of the fluid but I have no way of measuring the return pressure in my current set up.
 
  • #9
kishanb_01 said:
This makes sense my follow up question is if I am removing less heat than I think what is a possible way I could increase this to get to the cooling capacity specification
Bigger pump or bigger pipes/less restriction. Though -- positive displacement pump? That's surprising for a chiller. It came with the chiller?
 
  • Like
Likes erobz and kishanb_01
  • #10
russ_watters said:
Bigger pump or bigger pipes/less restriction. Though -- positive displacement pump? That's surprising for a chiller. It came with the chiller?
The pump did come with the chiller. I may look into getting a new one in that case should I look for one with a higher cooling capacity or better pump?
 
  • #11
kishanb_01 said:
That I'm not too sure The gauge on the device is measuring the outlet pressure of the fluid but I have no way of measuring the return pressure in my current set up.
To me it seems like they are giving you optional pump curves. Anyhow, unless it is a differential pressure meter already plumbed across the pump you need a two measurements to determine the flow. The pressure on both sides of the pump. A one sided pressure in a closed loop is not helpful in regards to flow specification.
 
  • Like
Likes russ_watters