A Yd1 transformer connection results in a -30 degree phase shift due to the alignment of primary and secondary windings to the same phase angle. The phase angle of C1-A1 relative to N-A1 demonstrates this shift. Proper vector alignment is essential; for instance, in a delta configuration, the c1-a1 vector should be vertical, aligning with N-A1. The connection follows a specific arrangement based on the transformer nameplate, maintaining the same phase relationships across windings. For further details on transformer connections, IEC 60076-1 Annex D provides comprehensive explanations.
OliskaP
38
7
Hi,

I have problems understanding why, for example, a Yd1 connection introduces a -30 degree phase shift, see image below.

How should I think when I want to produce vector groups like that, and derive myself what the phase shift should be?

Thanks..
Yd1.JPG
 
Engineering news on Phys.org
First - just consider the actual phase angle of C1-A1 relative to N-A1 - there will be a 30deg Shift there. So it is not really any magic in the transformer - each winding Primary and Secondary are aligned to the same phase angle.

If you keep the vectors properly aligned - you will see... for example in the bottom Delta configuration, c1-a1 vector should be vertical because it is in the same phase as N-A1 above.
Now using the same Vector angle for N-B1 and N-B2 - connect the "tail" of a1-b1 to the head of the c1-a1, and then the same for b1-c1 - this should close the triangle of the delta.

I proper transformer nameplate will maintain this same arrangement. EXAMPLE
 
  • Like
Likes OliskaP
As windadct said A1_N is same phase as a1_4 , B1_N is same phase as b1_5, C1_N is same phase as c1_6 since the same magnetic flux will pass through both windings.
The connection will be as per attached sketch- for Yd11 : 5 with a1 ,6 with b1 and 4 with c1 and
for Yd1 a1_6, b1_4, c1_5.
The convention states an imaginary neutral point in the intersection of all three medians of the equilateral triangle , and an imaginary voltage to this neutral from each point of triangle. The a1 to neutral n is the first phase and the angle from HV A1_N is the considered angle which divided by 30 degrees gets the symbol of the connection[in Yd11 case 330/30=11].
You may find in IEC 60076-1 Annex D all the connections.
upload_2016-10-13_21-31-35.png

upload_2016-10-13_21-32-10.png
 
  • Like
Likes OliskaP
Very nice explanation, thanks, both of you.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...