In summary, the role of a step-up transformer is to increase the voltage while decreasing the current, resulting in a lower overall heating effect. This is important in transmission lines where high voltages are necessary to prevent melting. However, when connecting a lamp to a step-up secondary coil, the lamp gets brighter due to the increased voltage, which causes the filament to draw more current and burn brighter. The confusion may arise from the fact that in transmission lines, the current is lowered to reduce losses, but in the lamp circuit, the current is determined by the load and the voltage it receives. By omitting the step-down transformer, the load receives a higher voltage and draws more current than it is rated for.
  • #1
DWarrington
6
0
Hello everyone,
I need some help with transformers as I am very confused...
I understand the role of a step up transformer - the secondary coil has more turns thus has a higher voltage induced. This in turn reduces the current and the overall heating effect is reduced. This is why transmission lines have such high voltages i.e so that they do not melt.
So, when I connect a lamp to a step-up secondary coil the lamp gets brighter. I understand it so that if voltage increases then current DECREASES as with transmission lines. So why does it get brighter - what am I missing?

Thanks for any help!
 
Physics news on Phys.org
  • #2
DWarrington said:
I need some help with transformers as I am very confused...
I understand the role of a step up transformer - the secondary coil has more turns thus has a higher voltage induced. This in turn reduces the current and the overall heating effect is reduced. This is why transmission lines have such high voltages i.e so that they do not melt. So, when I connect a lamp to a step-up secondary coil the lamp gets brighter. I understand it so that if voltage increases then current DECREASES as with transmission lines. So why does it get brighter - what am I missing?

You are assuming the load draws constant power which is not correct.

It gets brighter because the voltage is higher.

The current in the secondary (Is) is determined by the load (the light bulb) not the transformer. It works like this...

The step up transformer creates a voltage Vs. The current in the secondary is determined by the resistance of the filament and is given by Is = Vs/R.

The transformer equation (Vs/Vp = Ip/Is = turns ratio) allows you to calculate the primary current Ip
 
  • #3
CWatters said:
You are assuming the load draws constant power which is not correct.

It gets brighter because the voltage is higher.

The current in the secondary (Is) is determined by the load (the light bulb) not the transformer. It works like this...

The step up transformer creates a voltage Vs. The current in the secondary is determined by the resistance of the filament and is given by Is = Vs/R.

The transformer equation (Vs/Vp = Ip/Is = turns ratio) allows you to calculate the primary current Ip
Hi - thanks for this.

So I shouldn't think that a transmission line behaves like a filament lamp then? Is that because it is non-ohmic or is it because a transmission line has negligible resistance compared with a filament? Therefore because the transmission line has zero resistance then current goes down when voltage goes up. And because a filament's resistance increases when voltage goes up then current goes up too?
I this right?
Thanks again
 
  • #4
No it's nothing to do with the difference between a transmission line and a filament...

When they build a transmission line they put a step up transformer at the power station end and a step down transformer at the town end. So the town always gets 110V (USA), 230V (UK/Europe).

Your experiment only mentioned adding a step up transformer. In that case the filament gets a higher voltage than it did originally. It's the higher voltage which causes the filament to draw more current and burn brighter. Had you used a step up and a step down the brightness would be unchanged.
 
  • #5
I like old military documentaries

 
  • #6
CWatters said:
No it's nothing to do with the difference between a transmission line and a filament...

When they build a transmission line they put a step up transformer at the power station end and a step down transformer at the town end. So the town always gets 110V (USA), 230V (UK/Europe).

Your experiment only mentioned adding a step up transformer. In that case the filament gets a higher voltage than it did originally. It's the higher voltage which causes the filament to draw more current and burn brighter. Had you used a step up and a step down the brightness would be unchanged.

Thanks for taking the time to help me.

I am still confused. I guess I don't get this as much as I thought!
I thought that by having a step up transformer this meant that voltage would be increased and that current would be decreased. I thought that was the point of the step up transformer. So if current is decreased how can a filament become brighter?
I get that more voltage means a greater 'push' of electrons but surely resistance would increase and current drop using Ohm's law?
 
  • #7
No, the lowered current only happens when the power consumption remains the same as with the original voltage. Mind you, to keep the power consumption steady with a different voltage you need to adjust the resistance (or impedance, in general). They do this with transmission lines, but your lightbulb filament doesn't.

I think your confusion stems from the fact that indeed in transmission lines the point of the step-up transformer is to lower the current. But, again, the current is lower because they draw the same power as if they did with the original voltage.
The reason for lowering the current in transmission lines is because the losses along the line are proportional to the square of the current (I^2*R).
 
  • #8
I thought that by having a step up transformer this meant that voltage would be increased and that current would be decreased. I thought that was the point of the step up transformer.

It is (in a power transmission system) but you are misunderstanding what determines the current. It's not the transformer but the load and the voltage it sees that determines the current.

In a transmission line system the voltage is stepped up at the power station and down again at the load. This means the load sees the correct voltage and draws it's rated current. The current on the transmission line between the two transformers is reduced.

In your circuit you omitted the step down transformer so the load saw the higher voltage and drew more than it's rated current.

A
 
  • Like
Likes lonely_nucleus
  • #9
CWatters said:
It is (in a power transmission system) but you are misunderstanding what determines the current. It's not the transformer but the load and the voltage it sees that determines the current.

In a transmission line system the voltage is stepped up at the power station and down again at the load. This means the load sees the correct voltage and draws it's rated current. The current on the transmission line between the two transformers is reduced.

In your circuit you omitted the step down transformer so the load saw the higher voltage and drew more than it's rated current.

A
I think you answered the OP's question good response.
 
  • #10
CWatters said:
It is (in a power transmission system) but you are misunderstanding what determines the current. It's not the transformer but the load and the voltage it sees that determines the current.

In a transmission line system the voltage is stepped up at the power station and down again at the load. This means the load sees the correct voltage and draws it's rated current. The current on the transmission line between the two transformers is reduced.

In your circuit you omitted the step down transformer so the load saw the higher voltage and drew more than it's rated current.

A

Thank you once again. This is starting to make sense mathematically.

I did an experiment so I was able to see this so it would make even more sense (I am a kinaesthetic learner!).
I got a 1200 coil primary coil and attached a 120 secondary coil to it and measured the current and voltage using a multimeter. I then changed the secondary coil from 120 turns with one of 600, then one of 900, then one of 1200 and then one of 2400. Each time the current went lower and lower. How is this explained - surely the current should go up when the number of turns on the secondary coil increases??

Thanks for your time again!
 
  • #11
DWarrington said:
Thank you once again. This is starting to make sense mathematically.
That's good!
The essence of understanding what goes on here is to get a clear view of what actually effects what (cause and effect). The glib statement that "increasing the volts reduces the current" can be very confusing (it was for you) if you take it at face value but you have to be careful about the actual message in the statement. Your experiment would show you very well what you get when you tweak different things.
The load resistor is the pivotal factor, governing what Power goes through the transformer (zero power if it's an open circuit, irrespective of the supply volts). Thereafter, it's the same power (VI) at each stage. You have to look in both directions at once to get what happens. Maths does this vey well, of course - as you have seen.

PS I don't understand what your experiment actually shows. What load resistor were you using?
 
  • #12
sophiecentaur said:
That's good!
The essence of understanding what goes on here is to get a clear view of what actually effects what (cause and effect). The glib statement that "increasing the volts reduces the current" can be very confusing (it was for you) if you take it at face value but you have to be careful about the actual message in the statement. Your experiment would show you very well what you get when you tweak different things.
The load resistor is the pivotal factor, governing what Power goes through the transformer (zero power if it's an open circuit, irrespective of the supply volts). Thereafter, it's the same power (VI) at each stage. You have to look in both directions at once to get what happens. Maths does this vey well, of course - as you have seen.

PS I don't understand what your experiment actually shows. What load resistor were you using?

Thanks!
I connected the secondary coil was connected to a filament lamp so that provided the resistance.
 
  • #13
Problem with a filament lamp is that its resistance is very much dependent upon its temperature so that can't be considered as a constant load R. As the supply volts to the lamp increase, the temperature rises and so will the resistance (10:1 ratio at least!)
Use a heater element (low power soldering iron, perhaps?) and you experiment may behave much better because the heater element doesn't get white hot!
 
  • #14
sophiecentaur said:
Problem with a filament lamp is that its resistance is very much dependent upon its temperature so that can't be considered as a constant load R. As the supply volts to the lamp increase, the temperature rises and so will the resistance (10:1 ratio at least!)
Use a heater element (low power soldering iron, perhaps?) and you experiment may behave much better because the heater element doesn't get white hot!

Ok - I will have a go at that and get back to you!

he original issue I had was that I thought that a step up transformer increased the voltage and reduced the current. As I increased the number of coils on the secondary coil I would have expected the current to drop. But it didn't - the filament lamp got brighter suggesting current increased which was not what I expected.
I now think that as the resistance drops, due to higher voltage, the current increases. A second transformer is needed to see voltage increase and current fall. Is this sounding right?
 
  • #15
The original issue in the OP is a common one in physics problems (also seen a lot in fluid flow/venturi questions). The issue is not recognizing that the equation applies to a uniqe/static situation, not to what happens when you change a circuit. When a transformer exists in a circuit, the power is equal on both sides of the transformer. But when you add a transformer to a circuit, the power is not equal in the circuit before and after the transformer is added.
 
  • #16
DWarrington said:
I now think that as the resistance drops, due to higher voltage, the current increases
Hang on. As the supply volts increase, the filament gets hotter and its resistance Increases. A hot filament has a (10X) higher resistance than a cold filament so you really can't say anything straightforward about what's going on in your experiment.
As I said before, you have to be careful to get your causes and effects in the right order if you want to get it right in 'yer head'. Use the simplest model to learn on - which means you need a load with an unchanging resistance.
 
  • #17
Please stop using a light bulb and use an ordinary resistor instead! Otherwise you will get really confused.

I did an experiment so I was able to see this so it would make even more sense (I am a kinaesthetic learner!). I got a 1200 coil primary coil and attached a 120 secondary coil to it and measured the current and voltage using a multimeter. I then changed the secondary coil from 120 turns with one of 600, then one of 900, then one of 1200 and then one of 2400. Each time the current went lower and lower. How is this explained - surely the current should go up when the number of turns on the secondary coil increases??

Which current? The current in the primary or the secondary?

Can you tell us more about this transformer with adjustable secondary coils? A photo would be good.
 
  • #18
I was trying to find a link that would explain fully what the OP needs to know, without getting too deep.
I have just looked at a load of google hits on simple transformer theory. There is a problem. The secondary school level pages all concentrate on the turns ratio equalling the volts ratio and the fact that VI is the same for primary and secondary. They do not seem to deal with the 'real situation' of a loaded transformer, like the OP is using. Secondary teachers also seem to trip out at that level and will often struggle to explain the practicalities. (Using high voltage transmission lines is just something they repeat parrot fashion.)
There is a big jump in the complexity of the higher level of google hits, which includes the other elements in a real transformer system (losses in the transformer, due to its own resistance etc.)
If someone could find a suitable link, at the right level, it could help the OP a lot.
 
  • #19
lonely_nucleus said:
I like old military documentaries


I liked the film but have the same problem with the fact that the current in the secondary can only be known when the load resistance is known. and that is not made at all clear. No wonder people have problems when there is a history of education being delivered like that.
 
  • #20
To add insult to injury, at some point you can't neglect the resistance of the secondary coil anymore either once it has enough turns.

That's why, while it's understandable to want to do things kinaesthetically, doing the circuit analysis at some point becomes inevitable.
 
  • #21
Anyone who wants to have a good understanding of the Physical sciences is bound to be disappointed if they don't or can't use the language (maths). I can't name a single ground breaking Physicist who managed to get there solely with kinaesthetics. That has to tell you something.
 
  • #22
russ_watters said:
The original issue in the OP is a common one in physics problems (also seen a lot in fluid flow/venturi questions). The issue is not recognizing that the equation applies to a uniqe/static situation, not to what happens when you change a circuit. When a transformer exists in a circuit, the power is equal on both sides of the transformer. But when you add a transformer to a circuit, the power is not equal in the circuit before and after the transformer is added.

Yes, that is all that is going on here. The step-up transformer is doing what it is supposed to do by lowering the current at the load with respect to the current at the source. But it cannot lower the current at the load with respect to the circuit without the transformer because the higher voltage at the load draws more current from the source. A case of comparing apples with oranges and getting orples; not a fruitful result!
 
  • #23
Tom_K said:
The step-up transformer is doing what it is supposed to do by lowering the current at the load
That is misleading. A step up transformer, with the same load, will put more current through the load (and more Power into it, of course) and also it will have the effect of presenting a lower resistance to the supply to its primary (more Power again). You are confusing cause and effect. Why not just say that a step up transformer increases the volts supplied to the load? What happens thereafter will depend upon the Resistance of the Load.
 
  • #24
sophiecentaur said:
That is misleading. A step up transformer, with the same load, will put more current through the load (and more Power into it, of course) and also it will have the effect of presenting a lower resistance to the supply to its primary (more Power again). You are confusing cause and effect. Why not just say that a step up transformer increases the volts supplied to the load? What happens thereafter will depend upon the Resistance of the Load.

What I wrote: The step-up transformer is doing what it is supposed to do by lowering the current at the load with respect to the current at the source.

What you quoted: The step-up transformer is doing what it is supposed to do by lowering the current at the load


Yes, that is definitely misleading.
 
  • #25
Tom_K said:
What I wrote: The step-up transformer is doing what it is supposed to do by lowering the current at the load with respect to the current at the source.

What you quoted: The step-up transformer is doing what it is supposed to do by lowering the current at the loadYes, that is definitely misleading.
Ummm. I think I can see where you're coming from. In the context of Electrical Power Transmission, the 'job' of the step up transformer (along with the step down transformer at the other end) is to send less current along the transmission lines - for a given transmitted Power. But the transformers just alter voltages. It is the whole system that arranges for the transmitted current to be as low as possible. I wouldn't say that any component's job is specifically to keep the current low, though.
An ideal transformer is a Voltage source and, apart from some inefficiency, its output voltage is independent of load. This is the function of most transformers - particularly the types we are discussing here.
'Current transformers ' do exist , for measuring high currents on transmission lines and, yes, they are step up transformers, with a single turn primary and multiple turn secondary windings. In that case, they have such a high output voltage that they are regarded as Current sources; nevertheless, they are Voltage Changers. I don't think that's what you are referring to, though.
 
  • #26
Can only corroborate sophie's post here. It's not the step-up transformer that lowers the current, it is the receiving station that does so by adjusting its load. With the purpose of maintaining the same power transmission as if it was the original voltage.
 

FAQ: Help with Transformers: Understand Step-Up Coils & Voltage

1. What is the purpose of a step-up coil in a transformer?

A step-up coil in a transformer is used to increase the voltage of an electrical current. This is achieved by having more turns in the secondary coil compared to the primary coil, which results in a higher output voltage.

2. How does a step-up coil work?

A step-up coil works by utilizing the principle of electromagnetic induction. When an alternating current flows through the primary coil, it creates a changing magnetic field. This changing magnetic field then induces a current in the secondary coil, resulting in a higher voltage output.

3. What is the difference between a step-up coil and a step-down coil?

A step-up coil increases the voltage of an electrical current, while a step-down coil decreases the voltage. This is achieved by having a different number of turns in the primary and secondary coils.

4. What is the relationship between the number of turns in a coil and the voltage output?

The number of turns in a coil is directly proportional to the voltage output. This means that as the number of turns increases, the voltage output also increases.

5. What factors affect the efficiency of a step-up coil?

The efficiency of a step-up coil can be affected by factors such as the quality of the materials used, the design of the transformer, and the amount of resistance in the coils. A higher quality transformer with lower resistance and a well-designed coil will result in a more efficient step-up coil.

Similar threads

Back
Top