In summary, the picture on the Wikipedia page shows a pole-mounted transformer that is responsible for providing split-phase secondary winding for household power. The three thick insulated black wires are the split-phase secondary winding, with the center wire also being grounded. The two wires on the right side of the bucket are likely ground wires, as one of the three phases and a ground wire are needed for the primary winding to create split phase.
  • #1
BrunoIdeas
14
0
Hello. I've been reading numerous texts about mains electricity but I'm not getting some of the things.

I'll start with some questions, considering Live, Neutral, and Ground wires.
1) Does the neutral wire return/come from the supply company? In that case, where does the company connect the neutral wire?

I ask this because I've heard/read that "ground closes the circuit", asi if, the could have a grand neutral grounded wire, and an "independant" live wire. I have serious doubts about that.

2) What does it mean that neutral wire is at zero potencial? OK, voltage is about differences. So when the wire is not connected to an appliance, say a bulb, it has a zero potential (conductor in equilibrium), but when it is conected, I asume it oscillates, and the voltage drop will be such that RMS is zero. Is that correct?

Sorry for not writing the questions clearly, I think I have a big mess up about this, so any comments, or a diagram with WHERE DO WIRES COME FROM AND GO TO, including the supply company will be of great help.

Thanks in advance to everyone.
 
Engineering news on Phys.org
  • #2
BrunoIdeas said:
Hello. I've been reading numerous texts about mains electricity but I'm not getting some of the things.

I'll start with some questions, considering Live, Neutral, and Ground wires.
1) Does the neutral wire return/come from the supply company? In that case, where does the company connect the neutral wire?

I ask this because I've heard/read that "ground closes the circuit", asi if, the could have a grand neutral grounded wire, and an "independant" live wire. I have serious doubts about that.

2) What does it mean that neutral wire is at zero potencial? OK, voltage is about differences. So when the wire is not connected to an appliance, say a bulb, it has a zero potential (conductor in equilibrium), but when it is conected, I asume it oscillates, and the voltage drop will be such that RMS is zero. Is that correct?

Sorry for not writing the questions clearly, I think I have a big mess up about this, so any comments, or a diagram with WHERE DO WIRES COME FROM AND GO TO, including the supply company will be of great help.

Thanks in advance to everyone.

(I moved your thread from General Physics to the EE forum for now)

The wikipedia article on electrical power distribution is pretty good:

http://en.wikipedia.org/wiki/Electrical_power_distribution

.
 
  • #3
BrunoIdeas said:
Hello. I've been reading numerous texts about mains electricity but I'm not getting some of the things.
As berkema mentioned, the Wikipedia page on http://en.wikipedia.org/wiki/Electric_power_distribution" is a good general source. The first section gives a pretty good overview of why this is so complicated:
The modern distribution system begins as the primary circuit leaves the sub-station and ends as the secondary service enters the customer's meter socket. A variety of methods, materials, and equipment are used among the various utility companies, but the end result is similar.

In the U.S., household power is generally http://en.wikipedia.org/wiki/Split_phase" , with the neutral at ground potential -- literally. There is a long copper rod stuck in the Earth outside my house. If I place a volt meter between a "hot" conductor (either of the two wires coming from the power company) and the ground (earth), it will measure 120 volts AC. I get 220 VAC by connecting to both of the "hot" conductors (each line is 120 VAC, at opposing phase angles.)

I'll start with some questions, considering Live, Neutral, and Ground wires.
1) Does the neutral wire return/come from the supply company? In that case, where does the company connect the neutral wire?

I ask this because I've heard/read that "ground closes the circuit", asi if, the could have a grand neutral grounded wire, and an "independant" live wire. I have serious doubts about that.
In the simplest view, for (U.S.) household split-phase power, yes, you can consider the neutral and ground wires to be connected directly to the Earth, with the power company also connected to the Earth. The "live" conductor can be thought of as being physically connected to the power company.

2) What does it mean that neutral wire is at zero potencial? OK, voltage is about differences. So when the wire is not connected to an appliance, say a bulb, it has a zero potential (conductor in equilibrium), but when it is conected, I asume it oscillates, and the voltage drop will be such that RMS is zero. Is that correct?
I don't understand the bolded portion. To me, "voltage drop" is the measurable reduction in voltage due to parasitic losses, such as the resistance in a long run of copper wire.
The voltages talked about for electrical power distribution is expressed in VRMS, even if it's not written as such.

Sorry for not writing the questions clearly, I think I have a big mess up about this, so any comments, or a diagram with WHERE DO WIRES COME FROM AND GO TO, including the supply company will be of great help.
The http://en.wikipedia.org/wiki/Electric_power_distribution" mentioned above has a simple diagram that may help (although, it doesn't show the neutral or Earth connections.)
500px-Electricity_grid_simple-_North_America.svg.png
 
Last edited by a moderator:
  • #4
Could someone confirm if what I'm saying about this picture is correct:

http://en.wikipedia.org/wiki/File:Polemount-singlephase-closeup.jpg

[URL]http://en.wikipedia.org/wiki/File:Polemount-singlephase-closeup.jpg[/URL]

There are three thick insulated black wires which are the split phase secondary winding, and the center wire should also be grounded (since it's the neutral wire and neutral is grounded), but you can't really see that in the picture. One of the leads of the primary winding is entering the bucket through the top, and is one of the three phases. But there needs to be another lead for the primary winding, and there seem to be two other wires, on the right side of the bucket, at the top and bottom. The Wikipedia article suggests that one of the three phases and a ground wire are the primary leads to create split phase, so I'm assuming that the two wires on the right side of the bucket are ground wires. But why are there two of them?
 
Last edited by a moderator:
  • #5
RedX said:
...
There are three thick insulated black wires which are the split phase secondary winding, and the center wire should also be grounded (since it's the neutral wire and neutral is grounded), but you can't really see that in the picture. One of the leads of the primary winding is entering the bucket through the top, and is one of the three phases. But there needs to be another lead for the primary winding, and there seem to be two other wires, on the right side of the bucket, at the top and bottom. The Wikipedia article suggests that one of the three phases and a ground wire are the primary leads to create split phase, so I'm assuming that the two wires on the right side of the bucket are ground wires. But why are there two of them?

Looking at the image in http://upload.wikimedia.org/wikipedia/en/1/1c/Polemount-singlephase-closeup.jpg" , I can see the second primary lead connected to neutral/ground (the uninsulated cable), along with the secondary center conductor, and the steel case of the transformer (the lower connection seen toward the ride side of the image). The neutral is connected to the house as a bare steel wire, which doubles as a structural support/strain relief for the two conductors.

The neutral-primary and case-to-ground connections on the transformer are separated in that manner as a type of redundancy. The reasoning, as I understand it, is to insure a solid connection to ground (earth), should there be an interruption of the neutral wire. I don't know enough of the electrical theory to understand how it would be any different than simply connecting the neutral and earth-ground to the same terminal.
 
Last edited by a moderator:
  • #6
pantaz said:
Looking at the image in http://upload.wikimedia.org/wikipedia/en/1/1c/Polemount-singlephase-closeup.jpg" , I can see the second primary lead connected to neutral/ground (the uninsulated cable), along with the secondary center conductor, and the steel case of the transformer (the lower connection seen toward the ride side of the image). The neutral is connected to the house as a bare steel wire, which doubles as a structural support/strain relief for the two conductors.

I don't see how the secondary center conductor (the middle black wire) is connected to neutral/ground. That middle black wire seems to end at a dielectric spacer that separates a ground wire (the wire where you can see the braids) from other wires.
 
Last edited by a moderator:
  • #7
RedX said:
I don't see how the secondary center conductor (the middle black wire) is connected to neutral/ground. That middle black wire seems to end at a dielectric spacer that separates a ground wire (the wire where you can see the braids) from other wires.
That connector (circled below) is metal, not an insulator. The white three-armed piece to the right is an insulating standoff. Farther right is another metal connector that attaches the household neutral.
attachment.php?attachmentid=37927&stc=1&d=1313097524.jpg
 

Attachments

  • Polemount-singlephase-detail.jpg
    Polemount-singlephase-detail.jpg
    23.4 KB · Views: 958
  • #8
Thanks.

I find it interesting that the reason for separating the electric industry into power plants, transmission lines, substations, primary and secondary distribution, is to prevent a monopoly of the entire electric industry. But I find that odd, as I'd imagine that power plants have a monopoly because it doesn't seem profitable to have two power plants competing against each other to serve one area. Also, how many different transmission lines can you have coming out of a single power plant? It seems like only a few companies can own transmission lines. It just seems like the power plant people will charge the owner of the transmission lines for electricity, and the owners of the transmission line will mark it up and pass it to the substation owners, and the substation owners will mark it up and pass it to the primary, etc. At anyone of those links, they could mark it up however much they want, and the end secondary user will blame it on the secondary distribution company because that's the only bill they see and the markups from all the previous stages are hidden.
 
  • #9
RedX said:
I find it interesting that the reason for separating the electric industry into power plants, transmission lines, substations, primary and secondary distribution, is to prevent a monopoly of the entire electric industry. ...

Where did you learn this? Power plants output very high voltage for reasons of long distance transmission efficiency. Substations are necessary to reduce the very high voltages. I'm not aware of legislation or agreements that prohibits power generation companies from owning and/or operating substations, etc.
 
  • #10
I got it from the link that was given by berekeman in this thread. The very last paragraph says:

Wikipedia said:
Traditionally the electricity industry has been a publicly owned institution but starting in the 1970s nations began the process of deregulation and privatisation, leading to electricity markets. A major focus of these was the elimination of the former so called natural monopoly of generation, transmission, and distribution. As a consequence, electricity has become more of a commodity. The separation has also led to the development of new terminology to describe the business units (e.g., line company, wires business and network company).

I can sort of understand how internet operates: some companies build a network of cables that cross the country, and charge ISPs to connect to this backbone. They sell usage of their lines to ISPs, and ISPs collect the money from their customers. I just can't see it scaling down to the local area that a powerplant serves.
 

Related to How does mains electricity work?

1. What is mains electricity?

Mains electricity refers to the electricity that is supplied by power stations and distributed through a network of transmission and distribution lines to homes and businesses for everyday use.

2. How is electricity generated for mains electricity?

Electricity is generated through the use of turbines, which are turned by a variety of sources including coal, nuclear power, wind, and water. The spinning turbines then create electricity, which is sent to substations for distribution.

3. How does electricity travel through mains electricity?

Electricity travels through mains electricity in the form of alternating current (AC). The electricity is sent from the power station to a substation, where it is stepped down to a lower voltage for distribution. It then travels through transmission and distribution lines to homes and businesses.

4. How is the voltage of electricity regulated in mains electricity?

The voltage of electricity in mains electricity is regulated through the use of transformers. These devices step up or step down the voltage as needed to ensure safe and efficient delivery of electricity to different areas.

5. How does a circuit breaker work in mains electricity?

A circuit breaker is designed to automatically shut off the flow of electricity when there is a sudden surge or overload. This helps to prevent damage to electrical devices and potential fires. The circuit breaker is connected to a bimetallic strip that expands when heated, causing it to trip and break the circuit.

Similar threads

  • Electrical Engineering
2
Replies
42
Views
901
  • Electrical Engineering
3
Replies
83
Views
4K
Replies
28
Views
2K
  • Electrical Engineering
Replies
12
Views
2K
Replies
16
Views
2K
Replies
4
Views
2K
  • Electrical Engineering
Replies
32
Views
2K
  • Electrical Engineering
Replies
10
Views
958
  • Electrical Engineering
Replies
5
Views
8K
  • Electrical Engineering
Replies
5
Views
611
Back
Top