- TL;DR Summary
- What are the electrical consequences of running an ac induction motor above design frequency?
This is a question on a welding/machining forum.
The OP has a lathe powered by a 6-pole (c.1000rpm) 3ph, 3hp, 50Hz, inverter-duty motor run in delta at 240V by a VFD capable of 400Hz output. Hobby use.
The lathe is mechanically set to low speed, for maximum torque when parting off, etc. He wants to use frequency control to increase speed for convenience, to save repeatedly swapping belt positions. What is a sensible maximum frequency? The motor specs don’t provide one. As far as I can see, there are are mechanical and electrical considerations:
Mechanical:
- Bearings are rated well above any speed contemplated.
- Rotor balance may become a problem above design speed, but the same motor is offered in a 2-pole (c.3000 rpm) version.
Electrical:
- Torque will drop off steeply above 50Hz, but since higher speeds are used for smaller parts, this may not matter too much.
- Skin effect at higher frequencies will increase effective winding resistance, but this may be offset by higher fan speed and so better cooling.
Given the above, I can’t immediately see why operating at 150Hz (c.3000 rpm for the 6-pole), or even higher, would be a problem. Is there anything we’re missing? Remember, this is hobby use, so perhaps we could push the envelope further than in an industrial setting.
The OP has a lathe powered by a 6-pole (c.1000rpm) 3ph, 3hp, 50Hz, inverter-duty motor run in delta at 240V by a VFD capable of 400Hz output. Hobby use.
The lathe is mechanically set to low speed, for maximum torque when parting off, etc. He wants to use frequency control to increase speed for convenience, to save repeatedly swapping belt positions. What is a sensible maximum frequency? The motor specs don’t provide one. As far as I can see, there are are mechanical and electrical considerations:
Mechanical:
- Bearings are rated well above any speed contemplated.
- Rotor balance may become a problem above design speed, but the same motor is offered in a 2-pole (c.3000 rpm) version.
Electrical:
- Torque will drop off steeply above 50Hz, but since higher speeds are used for smaller parts, this may not matter too much.
- Skin effect at higher frequencies will increase effective winding resistance, but this may be offset by higher fan speed and so better cooling.
Given the above, I can’t immediately see why operating at 150Hz (c.3000 rpm for the 6-pole), or even higher, would be a problem. Is there anything we’re missing? Remember, this is hobby use, so perhaps we could push the envelope further than in an industrial setting.