Inrush current in a transformer chain

In summary, inrush current in a transformer chain refers to the high initial current that flows when a transformer is first energized. This phenomenon occurs due to the sudden application of voltage, which magnetizes the core and can lead to a peak current several times greater than the normal operating current. The inrush current is influenced by factors such as the transformer's core material, design, and the phase of the supply voltage at the moment of energization. Understanding inrush current is crucial for designing protection systems and ensuring the reliability of transformer operations.
  • #1
Guineafowl
796
386
TL;DR Summary
How does connecting two transformers in a chain affect the inrush current (at switch-on), as opposed to one transformer on its own?
1707921595020.png


This is the proposal, except the two middle voltages are 110V, not 12V.

Say the max switch-on inrush current of XFMR1 is xA with the secondary open, would the value change significantly in the above arrangement, with the secondary of XFMR2 open?
 
Engineering news on Phys.org
  • #2
You have twice the leakage inductance, so the inrush may be a little lower.
 
  • Informative
Likes Guineafowl
  • #3
berkeman said:
You have twice the leakage inductance, so the inrush may be a little lower.
Thanks.
 
  • #4
Hard to answer without knowing what causes the inrush current.

- If it's from the load circuitry, the I'm with @berkeman, more series impedance buffer means less inrush magnitude, but longer duration (probably).

- If it's from the transformer core saturation because of residual magnetization, then it's just not predictable, at least to me. But, the same or maybe more.

- If it's from winding capacitance then you get an addition of some sort. Complicated by turns ratio and leakage inductance.

The short answer is that you need a much more detailed model, which is pretty difficult. As you drew it, I'd say there's no inrush surge in any case.
 
Last edited:
  • Like
Likes berkeman
  • #5
If the magnetic core was in demagnetized position when it was de-energized

then up to 100 A/m magnetic field the flux density is about 0 so E1=0 and E2=0 and I2=0 since the second loop E=0.

So, no inrush current is expected in the secondary.

0=U-(E+Z*Iinrush)

U is the supply voltage, E it is the electromotive force in the primary or secondary windings and Z is the short-circuit impedance.

E=Φ*ω Φ=Bfe*A [A= magnetic core cross section area].The current will rise in time from 0 to Iinrush .

If the magnetic core was in demagnetized position when it was de-energized then up to 100 A/m magnetic field the flux density is about 0 then Φ=0 so E1=0 and so E2. So, no inrush current is expected in the secondary.

Iinrush=(U-E)/Z [ if E1=0 then Iinrush=U/Z] ; Z=R+jXe Xe=leakage magnetic flux reactance Xe=Le*ω it is considered independent of main flux level.
 

Attachments

  • Magnetic flux density vs Field.jpg
    Magnetic flux density vs Field.jpg
    37.2 KB · Views: 36
  • Hard and soft magnet magnetic flux density.jpg
    Hard and soft magnet magnetic flux density.jpg
    40.5 KB · Views: 27

FAQ: Inrush current in a transformer chain

What is inrush current in a transformer chain?

Inrush current is the initial surge of current that occurs when a transformer is energized. This current can be significantly higher than the normal operating current and typically lasts for a short duration, usually a few cycles. It is primarily caused by the magnetization of the transformer's core as it transitions from a de-energized state to an energized state.

What causes inrush current in transformers?

The inrush current in transformers is mainly caused by the non-linear characteristics of the magnetic core. When the transformer is switched on, the core requires a large amount of magnetizing current to reach its saturation point. Additionally, the phase angle of the voltage at the moment of switching can influence the magnitude of the inrush current, especially if it coincides with the peak of the voltage waveform.

How does inrush current affect transformer operation?

Inrush current can have several effects on transformer operation, including mechanical stress on the windings, potential damage to insulation, and tripping of protective devices due to overcurrent conditions. While inrush current is typically temporary, it can pose challenges for system stability and protection coordination in electrical networks.

How can inrush current be reduced in transformer installations?

Inrush current can be reduced through various methods, including using controlled switching devices that minimize the voltage applied to the transformer at the moment of energization, implementing soft starters, or utilizing inrush current limiting reactors. Additionally, selecting transformers with lower inrush current characteristics can help mitigate the impact of inrush on the electrical system.

What are the typical values of inrush current for transformers?

The typical value of inrush current for transformers can range from 5 to 10 times the full-load current, depending on factors such as the transformer design, size, and the characteristics of the power system. In some cases, particularly with larger transformers, inrush currents can exceed 12 times the full-load current. The specific value can vary based on the transformer's core material and construction.