Installing sensors to monitor current and rpm

In summary, the conversation discusses the selection of a suitable sensor/transducer to monitor current and RPM from an inverter to a spindle motor. The inverter model and technical information are provided, and suggestions are given for measuring RPM using a Hall Effect or optical sensor. The conversation also mentions the use of a dropbox link for the technical manual and provides equations for calculating the synchronous speed of an induction motor. The relationship between slip, torque, power, and current is also discussed.
  • #1
Crankshaft1983
11
0
I would like some assistance to select the right sensor/transducer to monitor current from an inverter to the spindle motor it feeds. If it is possible to get RPM signals from the inverter please advice on how to go about it. Please suggest the most suitable sensor/s to achieve both current and RPM (if possible), if not, just current.

Inverter: Mitsubishi Transistorized Inverter (FR-A500-3.7K)
Inverter output voltage: 200 to 240 VAC 3-phase (u,v,w terminals pg 12) 50/60 Hz

Attached is some technical info for the inverter. Pages 220, 12, 41, 2 & 36 may be of considerable interest. Page numbers mentioned here are the page numbers printed at the bottom of each page in the attached technical manual for the inverter. Thank you for taking the time to help.
 

Attachments

  • CP_Mitsubishi%20FR-A500E%20Inverter.pdf
    45.1 KB · Views: 244
Engineering news on Phys.org
  • #2
measuring RPM is best done with a Hall Effect sensor or something optical. It is very simple to do. Trying to do it by analyzing the current waveform? Ugh. I would have trouble trusting it, even if you can do it.

And your pdf doesn't work for me. It also seems a bit small for a 220+ page technical manual. I think it did not upload completely.
 
  • Like
Likes 1 person
  • #3
The rotational speed of a motor can't be derived directly from its current.

However, if you painted one side of the motor shaft white and the other side black, you could reflect light off it into a photoelectric sensor and this would give a stream of pulses out as the black and white sections reflect less and more light respectively.

If you have access to EBay, the next step is easy. Buy a non contact optical tachometer.

Measuring current in a three phase motor circuit has to be done carefully and professionally. Get an electrician to supply and fit a suitable meter.
The device supplied will probably monitor the current in each phase.
 
  • Like
Likes 1 person
  • #4
I believe that parameter registers 52, 53, 54 and 158 can be programmed to select display of output current.

You know the output frequency that you have programmed, so you know the synchronous speed of an induction motor, if that is what you are using. An induction motor will have a slip below synchronous speed that is proportional to current. Once you have calibrated your motor RPM to current you will be able to use current as a proxy for slip and from that compute RPM.
 
  • Like
Likes 1 person
  • #5
Last edited:
  • #6
MrSparkle said:
measuring RPM is best done with a Hall Effect sensor or something optical. It is very simple to do. Trying to do it by analyzing the current waveform? Ugh. I would have trouble trusting it, even if you can do it.

And your pdf doesn't work for me. It also seems a bit small for a 220+ page technical manual. I think it did not upload completely.

I have added a dropbox link for the inverter tech docs Sir. Please check out the pages I mentioned in my first post for reference to help suggest a suitable sensor to monitor current based on the demands of the motor.
 
  • #7
Baluncore said:
I believe that parameter registers 52, 53, 54 and 158 can be programmed to select display of output current.

You know the output frequency that you have programmed, so you know the synchronous speed of an induction motor, if that is what you are using. An induction motor will have a slip below synchronous speed that is proportional to current. Once you have calibrated your motor RPM to current you will be able to use current as a proxy for slip and from that compute RPM.

So in otherwords the synchronous speed = RPM (after calibration) ?

Or is there an equation that relates both entities?

Is there a relation to power and rpm?
 
  • #8
Are you using an induction motor? An induction motor has a slip, usually quoted in %.
Slip varies between about 1% at no shaft load to about 10% at full load.
The number of poles in a motor counts the N and the S poles, so the number of pole pairs, or field cycles, is half that.
Induction motor theoretical synchronous speed in RPM = Hz * 60sec * 2 / poles = 120 * Hz / poles.

For 4 poles at 50 Hz, synchronous speed would be 1500 RPM.
Typically, with 4% slip that becomes the 1440 RPM speed rating on the plate.
1440 RPM / 1500 RPM = 0.96 * synchronous speed = 0.04 slip = 4%.

Slip is proportional to torque on the shaft. Therefore, for a fixed voltage, also to power and hence current.
See the graph here; http://en.wikipedia.org/wiki/Induction_motor#Synchronous_speed
 
  • #9
Baluncore said:
Are you using an induction motor? An induction motor has a slip, usually quoted in %.
Slip varies between about 1% at no shaft load to about 10% at full load.
The number of poles in a motor counts the N and the S poles, so the number of pole pairs, or field cycles, is half that.
Induction motor theoretical synchronous speed in RPM = Hz * 60sec * 2 / poles = 120 * Hz / poles.

For 4 poles at 50 Hz, synchronous speed would be 1500 RPM.
Typically, with 4% slip that becomes the 1440 RPM speed rating on the plate.
1440 RPM / 1500 RPM = 0.96 * synchronous speed = 0.04 slip = 4%.

Slip is proportional to torque on the shaft. Therefore, for a fixed voltage, also to power and hence current.
See the graph here; http://en.wikipedia.org/wiki/Induction_motor#Synchronous_speed

This makes lots of sense, thank you. Yes its an induction motor. So frequency is the only variable here. How do I obtain the variable frequency? Do you think I can obtain that from the inverter which powers the motor?
 
  • #10
You control the speed of the motor by programming the frequency produced by the inverter.
3.2 Operation Panel.
With the operation panel (FR-DU04), you can set the running frequency, monitor the operation command display, set parameters, display an error, and copy parameters.
Do you have a front panel on the inverter? or did the inverter have an external PLC?
 
  • #11
If you want to measure rotational speed of a motor, then you need a tachometer.

Here (just as an example) is a tachometer:

http://www.ebay.com.au/itm/141229531364%20

As you can see, they are available, delivered from China, for around US$10. This is probably a lot less you could build one for, even if you had some way of calibrating it.

Current is measured with an AC ammeter. If the currents are large, or you want to monitor the current at a distance, you can use a current transformer followed by a suitable meter.
 
  • #12
Baluncore said:
You control the speed of the motor by programming the frequency produced by the inverter.

Do you have a front panel on the inverter? or did the inverter have an external PLC?

Unfortunately it doesn't have a front panel but there's a PLC display on the machine.
 
  • #13
Crankshaft1983 said:
Unfortunately it doesn't have a front panel but there's a PLC display on the machine.

Please ignore the last last post. Auto correct got me there.

Answer to your question is Yes, there's an external PLC on the machine on which the inverter is installed. Is it possible to pick off output frequency & current signals from the PLC via a DAQ to a computer for RPM computations like you suggested?
 
  • #14
If you have a display with up/down buttons on the VFD, then you can program it's parameters to show the motor current on the VFD.

You will need to get the interconnection diagram that shows how the PLC is interfaced with the VFD inverter. That will show how you might get the analogue? parameter for display.
 
  • #15
Baluncore said:
If you have a display with up/down buttons on the VFD, then you can program it's parameters to show the motor current on the VFD.

You will need to get the interconnection diagram that shows how the PLC is interfaced with the VFD inverter. That will show how you might get the analogue? parameter for display.

Yea the VFD (Inverter tech manual attached) has a display as well as the tool the inverter is installed on outputs current and RPM readings on an inbuilt display. So I was wondering if there is a way to pick those analog or digital signals from the inverter or the machine (machine technical manual attached) then route it through a DAQ to a computer for analysis. Meanwhile I'll dig around for the connection diagram between the PLC and VFD). I checked the attached manual but didn't see anything promising. Please feel free to check as I may have skipped it without knowing. Thanks for all your effort and time Baluncore.
 

Attachments

  • CP_Mitsubishi%20FR-A500E%20Inverter.pdf
    45.4 KB · Views: 226
  • 841%20Maintenance.pdf
    45.2 KB · Views: 226
  • 841Technical%20Reference.pdf
    45.3 KB · Views: 229
  • Data%20Maintenance.pdf
    45.2 KB · Views: 257
  • #16
Note; It seems that your .pdf attachments are actually .html links to the files.
Download, then rename the attached filename.pdf files to filename.html to download the files.
 
  • #17
Page B33 of the 841 Technical Reference shows analogue speed control voltage and current monitor signals on the inverters connecting to the ANLG1 module. See attached image of part of that page.

When you pick off the the voltages at one end of the screened twisted pair cables you will be able to digitise and record those parameters with an external recorder.
 

Attachments

  • page B33.png
    page B33.png
    10.9 KB · Views: 466
  • #18
Baluncore said:
Note; It seems that your .pdf attachments are actually .html links to the files.
Download, then rename the attached filename.pdf files to filename.html to download the files.

Yea they are originally PDF files but I uploaded them to dropbox and shared the link on here because I couldn't upload them directly on here (Physics forum). If you click on it, it should download to your computer.
 
  • #19
Crankshaft1983 said:
So I was wondering if there is a way to pick those analog or digital signals from the inverter or the machine (machine technical manual attached) then route it through a DAQ to a computer for analysis.
Re: My post #17 attachment. Have you looked at page B33 of the 841 Technical Reference ?
I believe that should now have solved your problem.
 
  • Like
Likes 1 person
  • #20
Baluncore said:
Re: My post #17 attachment. Have you looked at page B33 of the 841 Technical Reference ?
I believe that should now have solved your problem.

Yes Sir, thanks much for all the help. Hopefully I can successfully get the data routed to my computer.
Well this is the main reason I'm hassling with this machine. Spindle current for the Z1 axis goes into
over-current mode when it reaches 12.1 amps or more causing it to burn wafers occasionally. The pre-set parameter value is set to 12. I don't know why this is happening but I figured monitoring the current while in operation over time might help shed some light. Any ideas why this is happening? or suggestions on what to check for or look into? Thank you
 
  • #21
I assume you have checked all the obvious things such as coolant water flow and filters.

Grinding is a difficult process to automate because the abrasive wheel characteristics and feed rates play a big part in optimising performance. My first guess would be that the abrasive wheels now being used have a different composition than originally specified for the machine.

Documentation is for 2003, so the machine may be 10 years old. I would still consider contacting the manufacturer technical department. It is highly probable that they have regularly encountered this problem and can tell you exactly what causes it.

It is possible that vibration over time has resulted in an intermittent fault, starting to appear more often now, that upsets the parameter measurement or control feedback loop. That will often appear as connector contamination or cracked solder joints. You can usually test for it with a “technical tap” from a rubber headed hammer on the equipment frame. If it fails when tested with the hammer, be more gentle and use a smaller hammer as you progressively approach the sensitive component.

A machine operator can usually tell the health of a machine by the sound it makes while operating. Ask the operator what it usually sounds like when operating correctly. They will then listen to it more carefully and be able to better advise you when things change.
 
  • #22
Baluncore said:
I assume you have checked all the obvious things such as coolant water flow and filters.

Grinding is a difficult process to automate because the abrasive wheel characteristics and feed rates play a big part in optimising performance. My first guess would be that the abrasive wheels now being used have a different composition than originally specified for the machine.

Documentation is for 2003, so the machine may be 10 years old. I would still consider contacting the manufacturer technical department. It is highly probable that they have regularly encountered this problem and can tell you exactly what causes it.

It is possible that vibration over time has resulted in an intermittent fault, starting to appear more often now, that upsets the parameter measurement or control feedback loop. That will often appear as connector contamination or cracked solder joints. You can usually test for it with a “technical tap” from a rubber headed hammer on the equipment frame. If it fails when tested with the hammer, be more gentle and use a smaller hammer as you progressively approach the sensitive component.

A machine operator can usually tell the health of a machine by the sound it makes while operating. Ask the operator what it usually sounds like when operating correctly. They will then listen to it more carefully and be able to better advise you when things change.

Quite a couple of things to look at. Thanks again Sir, you've been very helpful.
 

Related to Installing sensors to monitor current and rpm

1. How should I choose the type of sensor for current and rpm monitoring?

The type of sensor you choose will depend on the specific application and the type of current and rpm data you want to measure. For example, if you need precise measurements, you may consider using a Hall Effect sensor, while for general monitoring, a simple magnetic sensor may suffice.

2. What is the ideal location to install the sensors for current and rpm monitoring?

The ideal location for sensor installation would be as close to the source of the current or rpm as possible. This will ensure accurate and real-time data collection. Additionally, make sure the sensor is securely mounted and protected from any external factors that may affect its performance.

3. How do I calibrate the sensors for accurate readings?

Calibration of the sensors is crucial for accurate readings. You can use a known standard or a reference signal to calibrate the sensors. Make sure to follow the manufacturer's instructions and perform regular calibrations to maintain the accuracy of the sensors.

4. Can I use one sensor to monitor both current and rpm?

Yes, you can use a single sensor to measure both current and rpm, but it may affect the accuracy of the readings. It is recommended to use dedicated sensors for each parameter to ensure precise measurements.

5. How often should I replace the sensors?

The lifespan of sensors may vary depending on the type and usage. However, it is recommended to replace the sensors every 1-2 years to ensure accurate readings. Regular maintenance and calibration can also help prolong the life of the sensors.