Hey folks. please help me out, I am having trouble finding the problem with a thyristor driver circuit. So this circuit has been working for many years without problems. It works from 2 of the 3 phases, so 400VAC (I am in Europe).
The thyristor is in series with a large coil, aka electromagnet located inside a box attached to a sand separator. The box works like a vibrator. It can be powered directly from 2 phases but in order to lower the vibration amplitude the thyristor circuit is installed.
Recently the thyristor circuit started working intermittently. It works for about 5 mins then stops for about 5 mins or so.
I took the whole circuit box home, checked every part, measured the capacitors (with capacitor tester), measured the transistors, checked the circuit board, connections everything, and it was all fine.
The problem still continues. Then today I was measuring the circuit as it was working LIVE. The thyristor gate driver is supplied from a rectified but unfiltered DC supply of 25 volts, this sags to 22.5 roughly as it begins working.
When the gate drive circuit stops working and the thyristor shuts off, I noticed there is a voltage of 25 VDC across the pulse transformer primary (measuring across the 1N4007 flyback diode) The transformer primary has a resistance of some 2 ohms or less. It is a small gate drive transformer. Clearly a voltage drop of 25 volts across the transformer isn't resulting from current flow through it but most likely I'm measuring from - terminal to which one side of the primary is attached through the unijunction transistor across the 220 ohms resistor connected to + side.
Now here is the weird part. When the gate drive circuit has stopped working, as i touch the cathode side pin of the primary flyback diode (1N4007) with a screwdriver or multimeter probe, it immediately starts working.
Clearly as I touch it even though with an isolated probe, there is a small change in capacitance introduced by my body and this is enough to get the drive going again. Then it stops after a little while again, touch it once more it works again.
It seems to me this could be some kind of a problem with a trimpot maybe changing it's originally set resistance (the two yellow ones are on board 3 pin potentiometers ) or maybe one of the capacitors is bad, although I checked all of them. I even changed the 2N2646 unijunction transistor simply because I had one and I wasn't sure whether the original measured correctly.
Any suggestions? Pleasesee the attachedschematic
The thyristor is in series with a large coil, aka electromagnet located inside a box attached to a sand separator. The box works like a vibrator. It can be powered directly from 2 phases but in order to lower the vibration amplitude the thyristor circuit is installed.
Recently the thyristor circuit started working intermittently. It works for about 5 mins then stops for about 5 mins or so.
I took the whole circuit box home, checked every part, measured the capacitors (with capacitor tester), measured the transistors, checked the circuit board, connections everything, and it was all fine.
The problem still continues. Then today I was measuring the circuit as it was working LIVE. The thyristor gate driver is supplied from a rectified but unfiltered DC supply of 25 volts, this sags to 22.5 roughly as it begins working.
When the gate drive circuit stops working and the thyristor shuts off, I noticed there is a voltage of 25 VDC across the pulse transformer primary (measuring across the 1N4007 flyback diode) The transformer primary has a resistance of some 2 ohms or less. It is a small gate drive transformer. Clearly a voltage drop of 25 volts across the transformer isn't resulting from current flow through it but most likely I'm measuring from - terminal to which one side of the primary is attached through the unijunction transistor across the 220 ohms resistor connected to + side.
Now here is the weird part. When the gate drive circuit has stopped working, as i touch the cathode side pin of the primary flyback diode (1N4007) with a screwdriver or multimeter probe, it immediately starts working.
Clearly as I touch it even though with an isolated probe, there is a small change in capacitance introduced by my body and this is enough to get the drive going again. Then it stops after a little while again, touch it once more it works again.
It seems to me this could be some kind of a problem with a trimpot maybe changing it's originally set resistance (the two yellow ones are on board 3 pin potentiometers ) or maybe one of the capacitors is bad, although I checked all of them. I even changed the 2N2646 unijunction transistor simply because I had one and I wasn't sure whether the original measured correctly.
Any suggestions? Pleasesee the attachedschematic