- Homework Statement
- The adiabatic compressor of a refrigeration system compresses saturated R-134a vapor at 0°C to 600 kPa and 50°C. What is the isentropic efficiency of this compressor?
- Relevant Equations
- n=(h2s-h1)/(h2a-h1)
We know that if potential and kinetic energy our negligible, the isentropic efficiency of a compressor is isentropic enthalpy change divided by actual enthalpy change: n=(h2s-h1)/(h2a-h1)
So I already answered this question and here is the answer: n1 is the isentropic efficiency of the compressor (0.37). Also h2a is the actual enthalpy value at the exit, and h2s is the isentropic enthalpy value at the exit (if process was reversible). Entropy (s1) was found as given temperature and quality value for the refrigerant. The entropy at outlet must be equal to entropy at inlet for isentropic process.
However, I'm confused about one thing. My lecturer told us that in order to find the isentropic enthalpy value at exit, the enthalpy should be found at the given specific entropy value and "pressure".
Here is my question, why can't we find the enthalpy using temperature as one of the independent properties instead of the pressure? I have calculated the isentropic efficiency using entropy and temperature instead of pressure (h2s_2), and I get a much higher efficiency. (0.72)