So we have a PID heating system with K-type thermocouples running through labview. We have a chassis that has 6 DAQ cards for Tc inputs (2 daq cards), flowcontroller in/out, an output for the heating elements for the PID control, and another input for a pressure transducer.

Anyway, the thermocouples give nice reading at most temperatures near room temperature. And the PID system seems to work, as I can control temperature pretty closely in the 300K-800K range. However, when I get to 800K+, some (not all) of the thermocouple readings go kind of nuts. They might randomly spike up to 1200K in a second, and then come down to 400K, etc. If I turn off the heating, after enough time passes and things have cooled back down, they might start behaving normally again.

I have all the DAQ cards coms wired together and then sent together to ground. Is this more likely to be a wiring/grounding issue or is it likely some sort of programming/labview issue? I don't suspect the problem is with the Tc's, as they are pretty new. I have no background at all in circuits, so I kind of think it is most likely something I am doing wrong, but I have to admit, when someone says "It's probably a grounding issue," I don't really understand what exactly that means or how I should ground it differently.

Sorry if this is a really basic question, but I guess this is what happens when a mathematician tries to like, actually do stuff.

Thanks!

simms
 
Engineering news on Phys.org
  • #2
Does your DAQ cards have thermocouples wired directly into it or is there a buffer which is commonly called a transmitter between the thermocouples and the DAQ? I would not wire any commons together at the DAQ. What are you measuring? Obviously something that gets hot, but how is it heated? Electrically?
 
  • #3
Sounds to me like the thermocouple Nickel to Chromium weld is opening. I would silver solder the bad ones and give them a try. If you want to run a test of temperature vs t/c voltage, here's a type K temperature (ºC) vs. voltage (millvolts) table.

"www.omega.com/temperature/Z/pdf/z204-206.pdf"
 
Last edited by a moderator:
  • #4
Thanks for the replies. I definitely think it was bad wiring the Tc common to ground. They are
working better now. But still, not perfectly. Now, instead of freaking out at the 800K range,
they start behaving badly at the 1100K range, and become useless at 1200K. I would really
like to go up to 1200K.

To answer your question, I am using electrical heating elements from Omega. There are two
57-Volt heaters wired in series, and then plugged directly into the wall/PID system. The PID
system is controlled by labview through a different set of DAQ cards, but connected to the
same chassis as the TC Daq cards.

I'm starting to think that there may be a programming issue as well, because I noticed that in
the labview program, when I turn off the "start PID" programming loop, the TCs go back to
giving accurate temperatures, even at the high range.

Here is a picture of everything behaving nicely at 1000, and then heating to 1100, and
starting to bug out a bit:

IXV5Y0V.jpg


Here is a picture of everything working completely terribly as I approach 1200K, but
then when I turn off the 'start PID' switch, the TCs acting a lot better as the temp comes down.

DyKmHst.jpg


Thanks again for all the help!

EDIT: yikes! Sorry they are huge. If someone knows how to fix that, let me know. Thank you!
 
Last edited:
  • #5


Hello simms,

Thank you for sharing your issue with the K-type thermocouple malfunction at 800-1000K. Based on the information provided, it seems that there could be multiple factors causing this issue. Let's start by discussing thermocouples and their behavior at high temperatures.

Thermocouples are temperature sensors that work based on the principle of Seebeck effect, which is the generation of a voltage when two dissimilar metals are joined together at two different temperatures. The voltage generated is proportional to the temperature difference between the two junctions. However, at high temperatures, the thermocouple materials can undergo changes in their physical and chemical properties, leading to a deviation in the voltage output and therefore, the temperature readings.

One possible cause of the erratic behavior of the thermocouples could be due to their exposure to high temperatures, which can cause the materials to undergo changes and produce inaccurate readings. Another factor could be the type of thermocouple being used. K-type thermocouples are known to have a limited temperature range, and at 800-1000K, they may not provide accurate readings. It would be beneficial to check the specifications of the thermocouples and make sure they are suitable for the temperature range being measured.

Furthermore, wiring and grounding issues can also affect the accuracy of thermocouple readings. As you mentioned, all the DAQ cards are wired together and sent to ground. It is possible that there could be a loose connection or a short circuit in the wiring, causing interference and resulting in erratic readings. I would suggest checking the wiring and connections to ensure they are secure and properly grounded.

In terms of programming and Labview, it is always a good idea to double-check your code and make sure everything is functioning correctly. However, based on the description of the issue, it seems that the problem is more likely related to the thermocouples or the wiring.

In summary, the K-type thermocouple malfunction at 800-1000K could be caused by exposure to high temperatures, limitations of the thermocouple type, or wiring and grounding issues. I would recommend checking these factors and addressing any potential issues to ensure accurate temperature readings. I hope this helps, and please let me know if you have any further questions.

Best,

Scientist
 

Related to K type thermocouple malfunction at 800-1000K

1. What is a K type thermocouple?

A K type thermocouple is a type of temperature sensor that is commonly used in industrial and scientific applications. It is made up of two different metals (usually nickel-chromium and nickel-aluminum) that are joined together to form a junction. This junction produces a small electrical voltage when exposed to heat, which can be measured and used to determine the temperature.

2. How does a K type thermocouple malfunction at high temperatures?

At high temperatures, the two metals in a K type thermocouple can start to react and form an intermetallic compound. This can cause the junction to become less responsive and produce inaccurate temperature readings. Additionally, the wires connecting the thermocouple to the measuring device may also degrade at high temperatures, leading to further malfunctions.

3. What is the temperature range for a K type thermocouple?

K type thermocouples are able to measure temperatures in a wide range, from -200°C to 1372°C (-328°F to 2502°F). However, their accuracy may decrease at extreme temperatures, and they are typically not recommended for use at temperatures above 1000°C (1832°F).

4. How can I prevent a K type thermocouple malfunction at 800-1000K?

One way to prevent a K type thermocouple malfunction at this temperature range is to use a protective sheath to shield the thermocouple from direct contact with the hot environment. Alternatively, using a different type of thermocouple (such as a type R or S) may also be more suitable for high temperature applications.

5. Can a K type thermocouple be recalibrated after a malfunction at 800-1000K?

Yes, a K type thermocouple can be recalibrated after a malfunction at high temperatures. This typically involves comparing the readings from the thermocouple to a known reference temperature and adjusting the calibration accordingly. However, if the thermocouple has been damaged or degraded due to the high temperature, it may need to be replaced entirely.

Similar threads

  • Electrical Engineering
Replies
30
Views
3K
Replies
19
Views
2K
Replies
1
Views
758
  • General Engineering
Replies
6
Views
2K
  • General Engineering
Replies
1
Views
5K
  • Mechanical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
4
Views
5K
  • Electrical Engineering
Replies
13
Views
4K
  • Electrical Engineering
Replies
24
Views
4K
  • Mechanical Engineering
Replies
2
Views
6K
Back
Top