In summary: CF lights. Propane appliances. The odd drain from the washing machine or the monitor/satellite/computers. I can live 'off the sun' in the summer with just the old system (640 watts) but I expect to live 'off the sun' for the spring and fall with 2100 watts. Building codes hardly apply. NO one cares. No house insurance available. No roads. No 'grid' of any kind. Having said that, I built to exceed all codes so that part is NOT a problem.When I say, "I built...", I mean: my wife and built it all ourselves. No help. Except this
  • #1
jdc
9
0
I have a three circuit solar array. Live off the grid. Each is 48 volt rated but two are really 90 volt rated (3 x 250 watt x 24 volt which are really 30 volt). The other is more like 60 volt. (2 strings of 4 80 watt panels x 12 volt -really 17.5 volt - total 640 watts. I have three + armored cable (3 wires plus a bare ground) - Tec cable #6. Why can't I run three circuits - using the three insulated wires - with the bare copper as the common neutral? The armor acts as the ground.
 
Engineering news on Phys.org
  • #2
Are you trying to hook them together in parallel or series? It seems that in parallel one might burn out the other because of the voltage differences.

As an example, I can hook two 12V batteries together in parallel and everything is okay but if I hook a 12V and a 3V in parallel then there'd be an unwanted current going thru the 3V battery which wouldn't be good.

http://www.batterystuff.com/kb/articles/battery-articles/battery-bank-tutorial.html
 
  • #3
jdc said:
I have a three circuit solar array. Live off the grid. Each is 48 volt rated but two are really 90 volt rated (3 x 250 watt x 24 volt which are really 30 volt). The other is more like 60 volt. (2 strings of 4 80 watt panels x 12 volt -really 17.5 volt - total 640 watts. I have three + armored cable (3 wires plus a bare ground) - Tec cable #6. Why can't I run three circuits - using the three insulated wires - with the bare copper as the common neutral? The armor acts as the ground.

Welcome to the PF.

What is your electrical background? What is your experience with home wiring and building codes? What kind of inverter system are you running with these solar panels? What kind of loads are you wanting to drive with this power (including any storage systems, batteries, etc.)?

What kind of terrain do you live in? Rural, urban, etc.? How close are your nearest neighbors?
 
  • #4
Electrical background: Zip. Nada. Zilch. Used How-to books to wire my house. Used how to guides to wire up original solar array and OUTBACK system. Outback is 48v. Original system was 640 watts. Keeping that system. New system is also 48 volts (by label) but made from different panels and even has different voltages. So, I was going to wire up another charge controller to handle the second system. Even tho the batteries are three banks (220 ah each), I was going to 'pulse' in the 'charge' from the old system into the front of the battery bank and MPPT charge the 'back end. Whatever the different 'types of charge were, they would be 'cushioned by the battery bank. I think.

Mountainous terrain. Solid rock, kinda. Ocean. Remote - beyond rural. Closest summer neighbours are half a mile but closest all-year neighbours are two miles.

My house is typical off-grid stuff. CF lights. Propane appliances. The odd drain from the washing machine or the monitor/satellite/computers. I can live 'off the sun' in the summer with just the old system (640 watts) but I expect to live off the sun for the spring and fall with 2100 watts.

Building codes hardly apply. NO one cares. No house insurance available. No roads. No 'grid' of any kind. Having said that, I built to exceed all codes so that part is NOT a problem.

When I say, "I built...", I mean: my wife and built it all ourselves. No help. Except this kind of thing - a forum.
 
  • #5
jdc said:
Electrical background: Zip. Nada. Zilch. Used How-to books to wire my house. Used how to guides to wire up original solar array and OUTBACK system. Outback is 48v. Original system was 640 watts. Keeping that system. New system is also 48 volts (by label) but made from different panels and even has different voltages. So, I was going to wire up another charge controller to handle the second system. Even tho the batteries are three banks (220 ah each), I was going to 'pulse' in the 'charge' from the old system into the front of the battery bank and MPPT charge the 'back end. Whatever the different 'types of charge were, they would be 'cushioned by the battery bank. I think.

Mountainous terrain. Solid rock, kinda. Ocean. Remote - beyond rural. Closest summer neighbours are half a mile but closest all-year neighbours are two miles.

My house is typical off-grid stuff. CF lights. Propane appliances. The odd drain from the washing machine or the monitor/satellite/computers. I can live 'off the sun' in the summer with just the old system (640 watts) but I expect to live off the sun for the spring and fall with 2100 watts.

Building codes hardly apply. NO one cares. No house insurance available. No roads. No 'grid' of any kind. Having said that, I built to exceed all codes so that part is NOT a problem.

When I say, "I built...", I mean: my wife and built it all ourselves. No help. Except this kind of thing - a forum.

Well all of that makes me a bit more comfortable with having a discussion here. It sounds like if you start a fire, you won't be catching your neighbors' houses on fire, or wasting the local fire department's time. Your wife is still at risk, but hopefully she understands the risk since she helped you to build it.

It's also good that you are trying to build it all to code. Even if inspections are not an issue, the codes are there for safety, so it's good to always follow them anyway.

:smile:
 
  • #6
More than that, B, if you read the codes as well as the How-to books, it is all easier to understand. And we needed 'easy'. Both of us are pretty stupid. How stupid? Well, I used to race motocross when I was young...just for starters (seeing your avatar) ;)

No problem with wasting anyone's time. We are way, way remote. See: offthegridhomes.org

Having said all that...are you sayin' that what I am proposing is dangerous? I mean, aside from using the ground wire as a neutral and aside from back-and-front loading of the battery bank? By the way...I pretty much resolved the ground wire-as-neutral thing. I found some wire (we gathered a lot of supplies to be able to do this and sometimes I forget what I have) and so I am running dedicated wires from all three systems now.
 
  • #7
jedishrfu said:
Are you trying to hook them together in parallel or series? It seems that in parallel one might burn out the other because of the voltage differences.
I believe he is wanting to run them independently, but sharing a common Earth return. 3 wires, plus an Earth return of a bare copper wire.
 
  • #8
The original question was really two questions - how can I use my Tec cable for all of what I wanted to do. I was going to run three circuits using the three wires in my cable and use the ground as a common neutral. But then I found some more cable so I have decided to give dedicated wires to each circuit. Sounds silly to those who live 'on the grid' but, for those off, making do with what you have is crucial. So, I collect junk. Fortunately I collected some cable I forgot about.

The second is a bit more 'physics' oriented. I am going to charge a bank of batteries from the charge controller that manages two fo the circuits and I am going to charge that same bank with a second charge controller that manages the third circuit. The only real difference is that one of the charge controllers goes on to the first (front) set of batteries and the second CC goes to the back set. In theory each CC is delivering the right charge so what difference does it make that one is getting a different input from the other? BUT one CC is PWM and the other is MPPT. That means they pulse 'juice' in differently. I figure the 12 batteries are like a giant electrical cushion and it doesn't matter if the front four get an MPPT charge and the back four get a PWM charge. Let the middle four sort it out.
Stupid?
 
Last edited by a moderator:
  • #9
jdc said:
The second is a bit more 'physics' oriented. I am going to charge a bank of batteries from the charge controller that manages two fo the circuits and I am going to charge that same bank with a second charge controller that manages the third circuit. The only real difference is that one of the charge controllers goes on to the first (front) set of batteries and the second CC goes to the back set. In theory each CC is delivering the right charge so what difference does it make that one is getting a different input from the other? BUT one CC is PWM and the other is MPPT. That means they pulse 'juice' in differently. I figure the 12 batteries are like a giant electrical cushion and it doesn't matter if the front four get an MPPT charge and the back four get a PWM charge. Let the middle four sort it out.
Stupid?

that doesn't bode well for the lifetime of the batteries. I would suggest incorporating ultra capacitors, but i don't know if you have the capabilities.
 
  • #10
My capabilities are pretty limited but if there are capacitors for this, I can do it. IF I KNEW what an ultra capacitor spec for this was. But back to the main question...why does this bode poorly for the batteries? Why would the PWM going in one way and the MPPT going in the other make any difference to a lead acid battery? Aren't they even dumber than me?
 
  • #11
An ultracapacitor is, it seems, just a HUGE, more efficient capacitor acting as a battery. MIT is developing them. Which is good. For maybe, Ford Motor Company. But, for those of us living in the forest and 'making do', it is not an option. We Luddites have to use lead acid. Rich Luddites maybe Lithium ion. Maybe. Who knows? OUR rich Luddites still just use more diesel in their gensets.
So, back to the lead acid...I have the option (I suppose) of 'isolating' four of the twelve batteries and then 'swtiching' them in and out on a rotational basis (like with the BIG RED Marine switch). But, I'd rather plug and play and let the sun do the work. Btw, the inevitable genset charge that comes in the winter comes by way of the charger built into the OUTBACK.
Your point is well taken. We OTG'ers (off the gridders) kill batteries like psychopaths kill hitchhikers. It's ugly. I do what I can but this is generation three in the last ten years. Five years is about max. Well, I may get 7 this time because each battery has a personality and I have learned to 'read' them a bit. Don't forget - we may be Luddites but batteries are prehistoric. Just a smidge more sophisticated than a big club. Battery development is the largest great leap forward that has yet to be accomplished.
 
  • #12
jdc said:
We OTG'ers (off the gridders) kill batteries like psychopaths kill hitchhikers. It's ugly. I do what I can but this is generation three in the last ten years. Five years is about max. Well, I may get 7 this time because each battery has a personality and I have learned to 'read' them a bit. Don't forget - we may be Luddites but batteries are prehistoric. Just a smidge more sophisticated than a big club. Battery development is the largest great leap forward that has yet to be accomplished.
bold by me

If you haven't seen this site yet, you'll probably enjoy it and it may help you get a longer battery life.

http://batteryuniversity.com/learn/

regards
 
  • #13
Thanks, Don. No, I hadn't seen it and it will provide me with a lot of info. Appreciated. Mind you, I have come to know that everyone has at least two opinions on the nature of batteries but, as I have about wtenty, this might help narrow it down a bit.
But what about the PWM up the back end and the MPPT in the front?
 
  • #14
Good ol' Battery U seems a bit dated. I have read some of their stuff but it is 'past era' stuff. They have solar panels at $5.00 a watt and that sort of thing. Doesn't make him wrong, of course, but it also seems NOT to be current. And, sadly, there is no reference to combining charger types - my main question.
 
  • #15
You should be using a MPPT charge controller between the panels and the batteries. The controller manual and/or the manufacturer's website will probably instruct you on how to connect multiple panels of different voltages. They probably will even give a circuit diagram that you could follow.

I believe that may be a better route to your answers than questions posted to this forum.
 
  • #16
You are probably right. But this is a theoretical question as well as a practical one. I really want to know what would happen doing it the way I proposed and why.
 
Last edited by a moderator:

FAQ: Maximizing Solar Power: Understanding Circuit Ratings for Off-Grid Living

1. What is the importance of understanding circuit ratings for off-grid living?

Understanding circuit ratings is crucial for off-grid living because it allows you to properly size your solar power system and ensure it can handle the energy demands of your household. Without proper understanding of circuit ratings, you may risk overloading your system and causing damage or underutilizing your system and not maximizing its potential.

2. How do I determine the circuit ratings for my off-grid solar system?

The circuit ratings for your off-grid solar system can be determined by calculating the total watts of all the appliances and devices that will be powered by your system. This includes the starting watts and running watts for each device, as well as factoring in any potential future additions to your system. This information can be found on the labels or manuals of your appliances.

3. What is the difference between AC and DC circuit ratings?

AC (alternating current) and DC (direct current) are two types of electrical circuits. AC is the type of current used in most household appliances and is typically rated in watts, while DC is commonly used in off-grid solar systems and is measured in volts. It is important to understand the difference between the two when selecting and sizing components for your off-grid solar system.

4. Can I mix different circuit ratings in my off-grid solar system?

No, it is not recommended to mix different circuit ratings in your off-grid solar system. This can cause imbalances in the system and potentially lead to overloading or underutilizing certain components. It is important to have a consistent and appropriate circuit rating throughout your system.

5. How can I ensure my off-grid solar system is maximizing solar power?

To ensure your off-grid solar system is maximizing solar power, it is important to regularly monitor and maintain your system. This includes cleaning and checking for any obstructions on your solar panels, regularly checking and replacing batteries as needed, and keeping track of your energy usage to make any necessary adjustments. It is also important to have a properly sized and rated system to efficiently capture and utilize solar energy.

Similar threads

Replies
7
Views
3K
Replies
17
Views
11K
Replies
21
Views
5K
Replies
30
Views
2K
Replies
25
Views
6K
Replies
7
Views
2K
Back
Top