- #1
tim9000
- 867
- 17
- TL;DR Summary
- Above nameplate kVA, theoretical implications.
Hi,
I was having a discussion with a colleague today now I'm second guessing myself.
My understanding of nameplate kVA is that it is based on 'ambient temperature, temperature rise, heat transfer, thermal mass, thermal time constant, materials used, and expected transformer life'.
However, when I do fault current calculations I use the nominal power and impedance of the transformer. This makes sense to me, as the net flux in the core won't ever change much from O/C to fault. This makes sense as there will be a voltage drop on the leakage impedance and resistance of the primary side. And as the secondary side is a short, most of the current will flow through the secondary side, as the magnetising branch is relatively a larger impedance then the secondary windings, as per the model of an ideal transformer. So in my mind it is the windings which limit the power of the transformer under high load. I don't see core saturation being a factor.
In the case of a fault I always imagined the current rising into the kA while the voltage on the secondary side drops right down, I always imagined that the power was still around nameplate power.
But I know that some transformers if you put a fan on to force cool the fins, you can extract above passive kVA rating.
So I've had concepts of Voltage regulation and Thevinin maximum transfer theorum running around my head. So my question is, does the power of the transformer rise under a fault or stay around nominal? Is the secondary voltage going to drop right down under a bolted fault? Maybe the voltage drop on the impedance of the windings isn't as much of a factor as I expected.
If the power output can just rise based on increasing load (assuming ammpacity of secondary conductors is not limiting) if you were cooling a transformer, what limits the amount of power it will output?
Thanks!
I was having a discussion with a colleague today now I'm second guessing myself.
My understanding of nameplate kVA is that it is based on 'ambient temperature, temperature rise, heat transfer, thermal mass, thermal time constant, materials used, and expected transformer life'.
However, when I do fault current calculations I use the nominal power and impedance of the transformer. This makes sense to me, as the net flux in the core won't ever change much from O/C to fault. This makes sense as there will be a voltage drop on the leakage impedance and resistance of the primary side. And as the secondary side is a short, most of the current will flow through the secondary side, as the magnetising branch is relatively a larger impedance then the secondary windings, as per the model of an ideal transformer. So in my mind it is the windings which limit the power of the transformer under high load. I don't see core saturation being a factor.
In the case of a fault I always imagined the current rising into the kA while the voltage on the secondary side drops right down, I always imagined that the power was still around nameplate power.
But I know that some transformers if you put a fan on to force cool the fins, you can extract above passive kVA rating.
So I've had concepts of Voltage regulation and Thevinin maximum transfer theorum running around my head. So my question is, does the power of the transformer rise under a fault or stay around nominal? Is the secondary voltage going to drop right down under a bolted fault? Maybe the voltage drop on the impedance of the windings isn't as much of a factor as I expected.
If the power output can just rise based on increasing load (assuming ammpacity of secondary conductors is not limiting) if you were cooling a transformer, what limits the amount of power it will output?
Thanks!