In Mexico, industrial power typically operates at 480Y/277V, with 460V being a common measurement due to a 5% voltage drop in distribution. The 3-phase voltage of 460V is likely derived from a nominal 480V supply, while the single-phase 127V is standard for residential use. It's important to verify the customer's specifications, as 460V is not a standard industrial voltage. For the integration of a single-phase circulation pump, a step-down transformer may be necessary to convert from 460V to 127V. Understanding these voltage distinctions is crucial for ensuring compatibility with the machinery being built.
Alan Sheedy
Messages
1
Reaction score
0
TL;DR Summary
Voltages in Mexico
Hello
We are building a machine for a company in Mexico. They have stated that the 3 phase voltage is 460v 60hz. No problem there as we can fit a main motor with this voltage/frequency. But we need to fit a small single phase circulation pump in the machine, so I asked about the single phase voltage and they said 127v. I'm a mechanical engineer with a fair understanding of electrics (I think) Can anyone explain this to me?
Regards Alan
 
Last edited by a moderator:
Engineering news on Phys.org
The 3∅ 460V and 1∅ 127V must be from different sources, or there's a step down transformer involved. 460V 3∅ can have 266V from phase to neutral, but no less. Theoretically you could have an unbalanced neutral with 127V from phase to neutral, but this would be too weird, and difficult, for anyone to actually do, I think.

So in the EE labs I worked in for high power stuff we basically had two systems 480/277V 3∅ and 208/120V 3∅. the difference was two separate giant transformers at the power entrance to the building where these voltages were generated.

So, I think you just need to take them at their word. They probably have either source available. If you want a single 460V power source to your equipment, then you'll need a step down transformer (autotransformer?) to make the lower voltage.
 
Mexican residential 1PH is 127 V to neutral.
Residential 3PH is therefore; 127 * Sqrt(3) = 220 V.
Your customer claims to have industrial 3PH of 460 V.

https://en.wikipedia.org/wiki/Mains_electricity_by_country
Lists Mexico as; 1PH Residential 127 V; and 3PH as 220 V or 380 V.

https://www.worldstandards.eu/electricity/three-phase-electric-power/
Lists Mexico 3PH as; 127/220 V; 120/240 V; 440 V; 240/480 V.

I would expect industrial 3PH to be specified as 440 V or 480 V, NOT 460 V.
I think you should check the 3PH specification your customer has provided.
Industrial 440 V is double the 220 V domestic 3PH.
I think it likely that the customer receives a nominal 440 V 3PH, that typically measures 5% high at 460 V
 
Last edited:
  • Like
Likes DaveE and jim mcnamara
I can only say I too have never seen a 460 volt 3 phase standard.
@Alan Sheedy make sure to double, triple check.
 
Mexican industrial power distribution is specified as 480Y277V. That is also the voltage rating of the contactors and circuit breakers used. 480Y277V has 480 V between phases, 277 V between each phase and neutral.

A voltage drop of about 5% is expected in distribution, so the 3PH voltage falls from 480 V to 460 V. That is why a class of NEMA motors for use with 480 V 3PH are commonly specified as 230/460 V.

The Mexican residential distribution voltage is unrelated to the industrial distribution. Residential power is distributed to the street as 3PH, 220 V, with neutral. A single 127 V phase to neutral is then provided with the neutral to each residence.
 
460V is the low end of the tolerance for 480V, so many machines were spec'd to this value.

As for the 127V - there a are number of buck/boost autotransformers giving 5-10-15% type steps. Probably best to just price one into the project.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...