- #1
Rx7man
- 425
- 189
Well, I've been trying to design a microhydro power project, and I contacted a supplier on Alibaba and we're a bit at odds about the recommended transmission voltage, I'd like to go with 480V and a transformer back down to 120/240V on the other end, their 'engineers' say this isn't necessary and that 240V is fine
I'm looking at a 10KW unit, transmission distance is about 500 meters, I'd like to go with 6ga wire at heaviest..
So I plugged my numbers into an online voltage loss calculatorHere's the 240V version, 51V drop (25%) at 40A, a loss of 1000W
https://www.calculator.net/voltage-...=500&distanceunit=meters&eres=40&x=73&y=14
and here's the 480V version, 25V (5%) drop at 20A, a loss of 500W
https://www.calculator.net/voltage-...500&distanceunit=meters&eres=20&x=121&y=25
Besides a crazy voltage instability under load, am I missing something or am I wrong? wouldn't transmitting at 480 or even 600V and having a transformer at the other end be FAR more cost and energy efficient? Most Teck cable has a 600V rating on it anyhow
I'm looking at a 10KW unit, transmission distance is about 500 meters, I'd like to go with 6ga wire at heaviest..
So I plugged my numbers into an online voltage loss calculatorHere's the 240V version, 51V drop (25%) at 40A, a loss of 1000W
https://www.calculator.net/voltage-...=500&distanceunit=meters&eres=40&x=73&y=14
and here's the 480V version, 25V (5%) drop at 20A, a loss of 500W
https://www.calculator.net/voltage-...500&distanceunit=meters&eres=20&x=121&y=25
Besides a crazy voltage instability under load, am I missing something or am I wrong? wouldn't transmitting at 480 or even 600V and having a transformer at the other end be FAR more cost and energy efficient? Most Teck cable has a 600V rating on it anyhow