Overhead transmission line protection failure

In summary, a 13.8 Kv OHTL fell on the ground in a desert and caused the death of over 30 camels. The Earth fault relays and overcurrent relays failed to operate, possibly due to the dry sand or dirt not providing a good ground fault, or both wires falling together causing a differential current. Non-directional ground relays may also operate at a lower setting in transmission systems, but this can lead to inadvertent tripping. Solutions for this issue in the desert could include setting the relays at a lower percentage and using different types of relays for ground protection.
  • #1
Tee
8
0
Hello everyone ,

I am still new to the protection field so i would appreciate if you can help me with analysis of the following,

A 13.8 Kv OHTL was cut and fell on ground , the cable was still live although being protected by Earth fault relays and Over current relays(Instantaneous and Time delay) , but for some reason they failed to operate.

This incident caused death of over 30 camels in Saudi Arabia.

This line was located in the desert and the marks on the sand showed that it stayed on ground for longer than one day.

What do you think could possibly cause EFR and OCR not to operate?

All opinions are much appreciated.

Thank you in advance
 
Engineering news on Phys.org
  • #2
The Earth ground fault will only trigger if there is a good ground fault, so if the wires landed on dry sand or dirt, the GFCI may not trip. Also, if both wires fell together, then the current might have looked differential, and again the GFCI would not trip.
 
  • #3
I agree with berkeman. High resistance of the soil(sand) could cause both relays to not sense the downed lines. The gound potential rise near the lines would cause the animals to be killed. With there long steps, there would be a large potential difference between the legs.
 
  • #4
Thanks for the replies , that was really helpful.
 
  • #5
Also:

Non directional ground relays may operate is the setting is below the current unbalance setting. Normally they set above to prevent inadvertent tripping during high demand period, typical in feeder circuits fro their neutral protection.

Tansmission system are trated as a balance circuit which can be set much lower in percentage terms to feeder circuit rating and often can be set to operate for broken conductor or single line to groundf ault with very low fault current on dry terrain or high ground impedance ... abnormal case for setting describe above.
 
  • #6
good analysis
but
what are the suggested solutions for this problem in desert ?
 

FAQ: Overhead transmission line protection failure

1. What causes overhead transmission line protection failure?

There are several potential causes of overhead transmission line protection failure, including lightning strikes, equipment malfunctions, or human error. These failures can occur in the protection devices, such as fuses or circuit breakers, or in the transmission lines themselves.

2. How can overhead transmission line protection failure be prevented?

To prevent overhead transmission line protection failure, regular maintenance and inspections are essential. This includes checking the condition of protection devices and making any necessary repairs or replacements. It is also important to have a robust protection system design and to properly train personnel in operating and maintaining the system.

3. What are the potential consequences of overhead transmission line protection failure?

The consequences of overhead transmission line protection failure can range from minor power outages to widespread blackouts and damage to equipment. In some cases, protection failure can also lead to safety hazards for personnel working on or near the transmission lines.

4. How is overhead transmission line protection failure detected?

Overhead transmission line protection failures are typically detected through monitoring and control systems, which can identify abnormal conditions and send alerts to operators. Additionally, regular inspections and maintenance can help detect any potential issues before they lead to failure.

5. What steps are taken to address overhead transmission line protection failure?

If overhead transmission line protection failure occurs, it is important to take immediate action to mitigate any potential safety hazards and restore power as quickly as possible. This may involve isolating the affected section of the transmission line, repairing or replacing protection devices, or conducting a thorough investigation to determine the cause of the failure.

Similar threads

Replies
2
Views
1K
Replies
3
Views
9K
Replies
3
Views
15K
Replies
4
Views
7K
Replies
33
Views
5K
Replies
49
Views
7K
Back
Top