Overvoltage Protection
In a three-phase four-wire system with 380V line-to-line and 220V line-to-neutral voltages, accidental disconnection of the neutral can cause line-to-neutral voltages to spike to 380V. An overvoltage protector rated for up to 300V is being installed, but there is uncertainty about the maximum voltage it can tolerate without damage. Discussions emphasize that the protection strategy should consider the entire system, including upstream protective devices and the specific configuration of the neutral system (TN-C or TN-S). Voltage monitoring relays are recommended for neutral break protection, as surge protection devices may not respond effectively to the voltage increase from 220V to 380V. Ultimately, while electrical distribution systems are generally reliable, they cannot protect against every potential failure.
Hfuda
A three-phase four-wire system has 380V LL, 220V LN voltages. A number of single phase 220V loads are connected between each phase and neutral. If the neural gets accidentally disconnected from the source, the 230V LN jumps to 380V LL. I am installing an overvoltage protector that can protect up to 300V. However, I am not sure what is the maximum voltage that the input terminals can accept without damage to the protector device? The specs do not provide an answer other than the fact that overvoltage setting can range from 270V to 300V. This implies that it can tolerate voltages above that. But to what level? And for how long?
Welcome to PF.
What power levels are we talking about here? What are the main breakers rated at for this 3-phase system? Can you post a link to the protection device datasheet?
It's likely the energy or power dissipated in the OVP device that causes their failure. Hence @berkeman's question about upstream protective devices. Voltage is only part of the data you need. Think of this as a system, not a single device.
I am well aware of this problem. I design such electrical installations. If you use the TN-C system (combined working and protective neutral, that is, PEN), the protection against neutral breakage is performed as follows: 1) reliable re-grounding of the neutral conductor (PEN conductor) is performed at the input to the electrical switch cabinet; 2) a voltage monitoring relay is used, which controls the release of the input circuit breaker. If you use the TN-S system (separated operating and protective neutral, that is, N and PE), neutral break protection is performed only by using a voltage monitoring relay that controls the release of the input circuit breaker. The N wire is not re-grounded, the PE wire is re-grounded. The control circuit with the voltage monitoring relay is designed so that the input circuit breaker is switched off if the relay is defective. This relay protection circuit ensures voltage control in case of any voltage deviations.
The use of surge arresters or surge protection devices to protect against neutral conductor breakage is unknown to me personally. The fact is that such devices are used for large overvoltages, for example, a lightning strike in an electrical line. Such devices practically do not respond to an increase in voltage from 220V to 380V, since they have a nonlinear characteristic of the dependence of resistance on voltage.
Likes DaveE and berkeman
Yes, this. Devices that can clamp voltages that accurately tend to be small, like TVS diodes, which can't absorb much energy. You could monitor the voltages and trip upstream circuit breakers, but this is complex and expensive for an unusual failure mode. It may also not be fast enough to save the downstream equipment anyway. Electrical distribution, done right, is usually pretty reliable, mechanically. If a neutral is broken, someone probably did it sort of on purpose. You can't protect against everything.
Likes Ivan Nikiforov, Averagesupernova and berkeman
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...