In summary, to achieve a 90% lagging power factor for a 50 kW load operating from a 60 Hz 10 kV rms line with a power factor of 60% lagging, a capacitance of 1.126μF must be placed in parallel with the load. This is calculated by finding the difference between the desired reactive power and the initial reactive power, and then using the formula C = 1 / (2πfXc) with Xc being the impedance of the parallel capacitance.
  • #1
Jason-Li
119
14

Homework Statement


A 50 kW load operates from a 60 Hz 10 kV rms line with a power factor of 60% lagging. Determine the capacitance that must be placed in parallel with the load to achieve a 90% lagging power factor.

The Attempt at a Solution



For Z at 0.6pf
S=P/pf = 50000/0.6 = 83333.33VA
I = P/Vs = 83333.33/10000 = 8.333A
R=p/I^2 = 50000 / 8.333^2 = 720Ω
Z=R/pf = 720/0.6 = 1200Ω
Xc=√(1200^2-720^2) = 960Ω
CosΦ=0.6 Φ=53.13°
Z1=720+j960Ω or 1200∠53.13°Ω

so for Z at 0.9
CosΦ=0.9 Φ=25.842°
Z2=r/pf = 720/0.9 = 800Ω
Xc=√(800^2-720^2) = 348.711Ω
Z2 = 720+j348.711Ω or 800∠25.842°Ω

Hence Z required = Z1 - Z2 = 720+j960 - 720+j348.711Ω = 0+j611.289Ω
so Xc = 611.289Ω
then C = 1/(2πfXc) = 1 / (2π*60*611.289) = 4.339μF

My main problem with this answer is I have seen several other answers equalling 1.126 μF using other methods such as https://www.physicsforums.com/threads/capacitance-power-factor-question.591792/ however I don't understand why either method don't give the same answer? Any help would be much appreciated.
 
Physics news on Phys.org
  • #2
I think you started out OK with the 0.6 PF portion except that what you call Xc is actual inductive or Xl. Nonetheless, your Z1 reflects this result.

I like to keep a circuit diagram in mind, like the following

upload_2018-12-23_0-43-14.png


I also like to work with the power quantities rather than impedances.

So you start off with 50 kW and that doesn't change for the resistive portion.

Initial apparent power is 50/0.6 or 83.3 kVA and the reactive power is 50/0.6 * 0.8 or 66.7 kvar.When you get to the 0.9 pf situation, the resistive or 50 kW portion doesn't change so the new reactive power is 50/0.9 * 0.436 or 42.5 kvar inductive.

To achieve the reduction in kvar from 66.7 to 42.5 kvar, we add parallel capacitance. So the capacitance required must make up the difference of 22.2 kvar. With your 10 kV voltage source, what capacitance is required to give you 22.2 kvar? I'm not sure it is the same answer that you showed but I haven't checked that yet.
 

Attachments

  • upload_2018-12-23_0-43-14.png
    upload_2018-12-23_0-43-14.png
    1.3 KB · Views: 754
  • #3
Hi Magoo thanks for the fast response!

So Xc = V / Qc = 10000^2 / 222222 = 4500Ω

C = 1/ (2πfXc) = 1 / 2*π*60*4500 = 0.589μF

Still doesn't seem correct? Still not sure why my original answer doesn't work either if I'm honest
 
  • #4
Look at @magoo's schematic.

That shows capacitance in parallel with the load resistance. You calculated the entire current as flowing through the resistor as if the load's capacitance was in series with the resistor.
Jason-Li said:
S=P/pf = 50000/0.6 = 83333.33VA
I = P/Vs = 83333.33/10000 = 8.333A
R=p/I^2 = 50000 / 8.333^2 = 720Ω
 
  • Like
Likes scottdave
  • #5
@anorlunda ah that makes sense as I wouldn't be able to calculate the I properly thanks!

So would my initial response be correct?

So Xc = V / Qc = 10000^2 / 22222 = 4500Ω C = 1/ (2πfXc) = 1 / 2*π*60*4500 = 0.589μF

Just referring to other sources and they have used the value of 42.5kVAr rather than 22.2kVAr for calculating Xc?
 
  • #6
Jason-Li said:
Just referring to other sources and they have used the value of 42.5kVAr rather than 22.2kVAr for calculating Xc?
I think that some values are getting mixed up. Can we agree that for the original circuit that the apparent power is correctly calculated to be ##S = 83.33\;kVA##, and that the reactive power is ##Q = 66.67\;kVAr##?

Then, taking the pf = 0.9 case we look to find the desired reactive power ##Q_d##.

##S_d = \frac{P}{0.9} = 55.56\;kVA## {The apparent power for the pf 0.9 case}

##Q_d = \sqrt{S_d^2 - P^2} = 24.23\;kVAr##

In the following diagram is the situation laid out in the form of power triangles:
upload_2018-12-23_15-34-57.png

The ##\Delta Q## is what the what the added capacitance will need to "consume".

##\Delta Q = Q - Q_d = 42.45\;kVAr##

So your "other sources" have it right.
 

Attachments

  • upload_2018-12-23_15-34-57.png
    upload_2018-12-23_15-34-57.png
    3.1 KB · Views: 693
  • Like
Likes jim hardy
  • #7
@gneill Thanks for that very thorough explanation, definitely one of those moments when it just clicks now.

So 'rerunning' the calc.

Xc = V / Qc = 10000^2 / 42450 = 2355.712Ω C = 1/ (2πfXc) = 1 / 2*π*60*2355.712 = 1.126μF

The help is much appreciated! Also thank you @magoo & @anorlunda .
 
Last edited:
  • Like
Likes jim hardy and gneill

Related to Parallel Capacitance - Power Factor Question

1. What is parallel capacitance?

Parallel capacitance is a measure of the ability of a circuit to store electrical charge. It is represented by the symbol C and is measured in Farads (F).

2. How is parallel capacitance calculated?

The formula for parallel capacitance is C = C1 + C2 + C3 + ..., where C1, C2, C3, etc. are the individual capacitance values of capacitors connected in parallel in a circuit.

3. What is power factor in relation to parallel capacitance?

Power factor is a measure of how efficiently a circuit uses electricity. In parallel capacitance, a low power factor indicates that the circuit is not using electricity efficiently and may be causing power losses.

4. How does parallel capacitance affect power factor?

In parallel capacitance, capacitors can improve power factor by storing and releasing electrical energy to balance out reactive power and reduce power losses. However, if there is too much parallel capacitance, it can cause overcompensation and lead to a higher power factor, which can also be problematic.

5. What are some applications of parallel capacitance?

Parallel capacitance has many practical applications, such as improving power factor and energy efficiency in industrial and commercial buildings, reducing power losses in transmission lines, and helping to stabilize the voltage and frequency of electrical grids.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
9
Views
17K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Introductory Physics Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
5K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
3K
Replies
55
Views
7K
  • Introductory Physics Homework Help
Replies
10
Views
5K
Replies
10
Views
2K
  • Introductory Physics Homework Help
Replies
2
Views
2K
Back
Top