Hello,
I have a light AC fan, that I wish to correct its power factor.
According to my measurements, it has around 0.7 LAG power factor.
Here are my digital measurements:
Vsupply = 204VAC
I(load) = 0.237Amps
phi = 43 , pf = 0.7 LAG
My target power factor (pf) is to be 0.85 , and to neutralize (reasonably) the lagging power factor, I inject it with leading VAR supplied by the capacitor bank.
The supply here, have a maximum value of 230VAC , so I got capacitor with Vrated = 450VAC > Sqrt(2)*230
For the capacitance this is the formulas/algorithm I've used to get C:
Q1 = Vrms * Irms * pf1 * tan(43)
Q2 = Vrms * Irms * pf1 * tan(32) //since cos^-1(32) = ~0.85
Qcap = Q1 - Q2 = Vrms ^ 2 / Xc
Xc = Vrms ^2 / Qcap = 1 / 2 * pi * f * C //hence C is calculated
Results:
*Note*: I connected two 100K 2W in series across capacitor terminals, as bleeding resistor for electrical safety
1) I branched a 6uF 450VAC in parallel with the load, I noticed that the load drew more current of 0.4Amps where originally it draw 0.2Amps // This is referred to over-compensation
2) I decreased the 6uF to 4uF , still were an over-compensation, but lighter than before, and the motor drew 0.3Amps
3) I kept on decreasing the capacitance until 1.6uF there I noticed that the motor got back drawing its original amount of current
4) Still decreasing, until 0.5uF what I noticed is that the current is as was at original ~0.237Amps and no improvement in reducing this current, not reducing the phase angle and pf improvement
My questions are the followings:
A) Is power factor correction applicable for such a small 60W load?
B) What is the value of capacitance C to improve its power factor?
C) After revising formulas, why I am not having an answer that intersect with real hardware working?
Thanks
I have a light AC fan, that I wish to correct its power factor.
According to my measurements, it has around 0.7 LAG power factor.
Here are my digital measurements:
Vsupply = 204VAC
I(load) = 0.237Amps
phi = 43 , pf = 0.7 LAG
My target power factor (pf) is to be 0.85 , and to neutralize (reasonably) the lagging power factor, I inject it with leading VAR supplied by the capacitor bank.
The supply here, have a maximum value of 230VAC , so I got capacitor with Vrated = 450VAC > Sqrt(2)*230
For the capacitance this is the formulas/algorithm I've used to get C:
Q1 = Vrms * Irms * pf1 * tan(43)
Q2 = Vrms * Irms * pf1 * tan(32) //since cos^-1(32) = ~0.85
Qcap = Q1 - Q2 = Vrms ^ 2 / Xc
Xc = Vrms ^2 / Qcap = 1 / 2 * pi * f * C //hence C is calculated
Results:
*Note*: I connected two 100K 2W in series across capacitor terminals, as bleeding resistor for electrical safety
1) I branched a 6uF 450VAC in parallel with the load, I noticed that the load drew more current of 0.4Amps where originally it draw 0.2Amps // This is referred to over-compensation
2) I decreased the 6uF to 4uF , still were an over-compensation, but lighter than before, and the motor drew 0.3Amps
3) I kept on decreasing the capacitance until 1.6uF there I noticed that the motor got back drawing its original amount of current
4) Still decreasing, until 0.5uF what I noticed is that the current is as was at original ~0.237Amps and no improvement in reducing this current, not reducing the phase angle and pf improvement
My questions are the followings:
A) Is power factor correction applicable for such a small 60W load?
B) What is the value of capacitance C to improve its power factor?
C) After revising formulas, why I am not having an answer that intersect with real hardware working?
Thanks