- #1
CosmicDriftwood
- 2
- 0
Chasing a ghost perhaps but in the process of pressure testing a simple propane furnace installation I installed a water Column pressure gauge. Over a period of 11 hours the pressure gauge reading will go from 10" WC to 0" WC. In the course of trying to understand this I installed a manometer in conjunction with the pressure gauge. I should add that this furnace is new and has never be used beyond an initial checkout.
Extensive testing shows that with an initial test pressure of 11" WC the rate of pressure loss is approximate 0.5" WC/hour. Exhaustive soap bubble testing of the short run of pipe and six fittings between the manual shut off valve and the furnace electric gas valve shows no leaks. So that suggest the the gas valve is leaking either through and/or from the valve body. I will say that there has never been a hint of propane odor.
The phenomenon that I need help with understanding it that after 15 hours or so with the test in progress and having been pressured to 10" - 12" WC the manometer will show a negative pressure of -3" WC -. This is a U-Tube manometer and is open on one side to atmosphere. So If indeed there is a leak through the electric gas valve - since all piping connections are tight, then the -3" WC is the difference between atmospheric pressure and the pressure inside of the piping and electric gas valve. I should add that the outlet side of the electric gas valve is always at atmosphere. It really looks like that there is a 3" vacuum relative to atmosphere right? But how can this be since the system will go to zero pressure, because of this "ghost" leak and then start to show negative (vacuum)? Nature abhors a vacuum so if there is a leak then the manometer should go to zero and stay there right?
The ANSI standard for electric gas valves allows for 235 cc/hour leakage passing through the valve and 200 cc/hour out of the valve for a total of 435 cc/hours. Relatively speaking I can't get a handle on what that means in terms of pressure loss. With a base pressure of 11" WC at an ambient temperature of 60 F; I'm trying to figure out of this valve is within spec.
Any help and/or advice will be appreciated. Thanks...
Extensive testing shows that with an initial test pressure of 11" WC the rate of pressure loss is approximate 0.5" WC/hour. Exhaustive soap bubble testing of the short run of pipe and six fittings between the manual shut off valve and the furnace electric gas valve shows no leaks. So that suggest the the gas valve is leaking either through and/or from the valve body. I will say that there has never been a hint of propane odor.
The phenomenon that I need help with understanding it that after 15 hours or so with the test in progress and having been pressured to 10" - 12" WC the manometer will show a negative pressure of -3" WC -. This is a U-Tube manometer and is open on one side to atmosphere. So If indeed there is a leak through the electric gas valve - since all piping connections are tight, then the -3" WC is the difference between atmospheric pressure and the pressure inside of the piping and electric gas valve. I should add that the outlet side of the electric gas valve is always at atmosphere. It really looks like that there is a 3" vacuum relative to atmosphere right? But how can this be since the system will go to zero pressure, because of this "ghost" leak and then start to show negative (vacuum)? Nature abhors a vacuum so if there is a leak then the manometer should go to zero and stay there right?
The ANSI standard for electric gas valves allows for 235 cc/hour leakage passing through the valve and 200 cc/hour out of the valve for a total of 435 cc/hours. Relatively speaking I can't get a handle on what that means in terms of pressure loss. With a base pressure of 11" WC at an ambient temperature of 60 F; I'm trying to figure out of this valve is within spec.
Any help and/or advice will be appreciated. Thanks...