Pumping power calculation of a vertical closed-loop system

In summary, the pumping power required for fluid circulation depends only on the fluid flow and the pressure differential between the inlet and outlet of the pump.
  • #1
argeus
2
0
TL;DR Summary
pumping power calculation of a vertical closed-loop system assuming the hydrostatic term
Hi there,
I hope that somebody can help me with this.. Any response is much appreciated!

Let's have a vertical closed-loop system where the fluid circulates using the pump. The temperature in both sections gradually changes (the upcomer section is heated up) so that the densities, velocities, and pressure drop change as well. Hence, it would be beneficial to split the geometry into horizontal sections; each section (downcomer and upcomer) is divided into a certain number of elements, each of the same height. The point is to calculate the pumping power needed for fluid circulation. The total power is calculated per partes, i.e. for each ith row separately and then simply summed together.

1677502151535.png


For any single ith row, the pumping power equation (w/o hydrostatic term) yields:
1677502566704.png

Note that subscript a refers to a downcomer and subscript b to an upcomer, respectively. Symbol m refers to the mass flow rate, ρ is density and Δp is the pressure drop across the element in the ith row as per Darcy friction eq.
Now assuming a hydrostatic pressure due to the changing density, one gets:
1677502594418.png

Simply, g denotes gravitational acceleration, and the term dl refers to the height of the element in the ith row.
Rearranging a bit:
?hash=1292ae7e36b7eaa26def673fa23d82f0.png

Since the mass flow is the same in both channels, we finally get:
1677502657295.png

Does this mean that the pumping power is independent of the hydrostatic pressure in the closed loop even when the fluid densities in both vertical channels differ? This does not seems correct to me, however, simply cannot find where I'm going wrong..
 

Attachments

  • 1677502617665.png
    1677502617665.png
    1.6 KB · Views: 97
Last edited:
Engineering news on Phys.org
  • #2
Welcome @argeus !
Pumping required power depends only on fluid flow and pressure differential between inlet and outlet of the pump.
 
  • #3
argeus said:
Does this mean that the pumping power is independent of the hydrostatic pressure in the closed loop even when the fluid densities in both vertical channels differ?
Rewriting your equation:
$$P = \rho_a \dot{V}_a\frac{\Delta P_a}{\rho_a} + \rho_b \dot{V}_b\frac{\Delta P_b}{\rho_b}$$
Where ##\rho_a \dot{V}_a = \rho_b \dot{V}_b =\dot{m}##. Simplifying:
$$P = \dot{V}_a\Delta P_a + \dot{V}_b\Delta P_b$$
 
  • #4
Dear Lnewqban,

Thank you for your reply. This is completely true and it matches the first eq. However, the question of how the pressure differential should be calculated remains open. I would guess that it consists of two terms, i.e. frictional forces and hydrostatic forces. If the temperature in the upcomer section is higher (because this section is heated), the density decreases and the hydrostatic balance should promote fluid flow. This is how thermosiphons (aka heat pipes) work. In a specific case, the hydrostatic force difference could balance the frictional forces so that a natural circulation in the closed-loop system is established and no pump is needed. For instance, the geometrical integrity of the Trans-Alaska Pipeline System in a permafrost environment is maintained using such heat pipes. So neglecting the hydrostatic term indicates to me that I've just overlooked something..
 
  • #5
That difference of temperatures, if substantial and continuous due to good heat transfer on both halves of the loop, may help your pump.
If most thermal energy does not remain in the fluid, something else is needed to stablish and keep a flow, overcoming friction and turbulence.
There is phase change in a heat pipe, you don’t have that in your system.

Nevertheless, at start up, that T differential may not be there, and your pump will need to have increased power to overcome friction of the system at an intermediate temperature.

If you have valves, expansion tanks, aireators, thermometers, coils, etc. in your loop, you will need to calculate pump power for worst conditions (full flow and restricted flow with all closed valves, restricted coils, air pockets traped in horizontal pipes, etc.).
Therefore, a safety factor should be included in your calculations as well.
 

FAQ: Pumping power calculation of a vertical closed-loop system

What is pumping power in a vertical closed-loop system?

Pumping power in a vertical closed-loop system refers to the amount of energy required to circulate the working fluid through the system. This includes overcoming frictional losses in pipes, fittings, and any other components within the loop.

How do you calculate the pumping power required for a vertical closed-loop system?

The pumping power (P) can be calculated using the formula: P = Q * ΔP / η, where Q is the flow rate of the fluid, ΔP is the pressure drop across the system, and η is the pump efficiency. The units of Q are typically cubic meters per second (m³/s), ΔP is in Pascals (Pa), and η is a dimensionless number between 0 and 1.

What factors influence the pumping power in a vertical closed-loop system?

Several factors influence the pumping power, including the flow rate of the fluid, the pressure drop due to frictional losses, the height difference in the system, the viscosity of the fluid, and the efficiency of the pump. Pipe diameter, length, and roughness also play significant roles in determining the pressure drop.

How can you minimize the pumping power in a vertical closed-loop system?

To minimize the pumping power, you can optimize the pipe diameter to reduce frictional losses, use smooth pipes to lower resistance, and ensure that the pump operates at its highest efficiency point. Additionally, minimizing the height difference and using low-viscosity fluids can further reduce the required pumping power.

What are the common units used in pumping power calculations?

Common units used in pumping power calculations include cubic meters per second (m³/s) for flow rate, Pascals (Pa) for pressure drop, and Watts (W) for power. Efficiency is typically expressed as a dimensionless ratio, ranging from 0 to 1. In some cases, other units like liters per second (L/s) or gallons per minute (GPM) for flow rate and feet of head for pressure drop might also be used.