Secondary distribution line overvoltage
In summary: older transformers it may be easier to just connect the primaries directly to the system neutral rather than use a transformer.
Rechel88
What is the probable cause of overvoltage in three phase secondary distribution line? Is it Possible to have an unbalance voltage in secondary distribution line? How do we solve this?
Situation: 1-disconnecting switch of a three phase transformer bank has been open in Primary distribution line due to dust and foreign matters and no fault occurs in the line. Wye-delta connection.
Any big motors on secondary side?
check all your primary side neutral connections.
good day sir, i believe there are no motor loads in the area or any significant big loads to possibly creates a unbalance loads. it happens when 1-disconnecting switch opened.
Do i interpret correctly that you are opening just one phase of the feed to a three phase wye transformer primary ?
So long as the neutral connection is solid, the voltage across and 120 degree phase angle between other two phases will be maintained and the secondary can continue to operate as an open delta.
But if the neutral connection is not solid, what happens to the phase angles?
Have you taken measurements? How much overvoltage are you seeing? Are secondary phase to phase voltages balanced?
yes sir, we open 1-phase only of the feeder and we didn't take any measurement because we have to re-energize the line asap so we only assume that the line were unbalanced but we are conducting investigation for our report the possible cause of the over voltage because there some damages. Neutral are connected properly though.
yet opening one phase of primary causes secondary overvoltage...
just a thought experiment here-
get a pencil and sketch some phasors to see if the following is right:
Primary side voltages with neutral connected, phase B open
let me assume phase to phase primary voltage is one unit...
Van = 1/√3 unit
Vbn = 1/√3 unit because it's backfed from secondary
Vcn = 1/√3 unit
so secondary phase to phase voltages are balanced, each is 1/√3 unit X turns ratio,
and the 120 degree phase relationship is intact.
Now remove the neutral connection between transformer and its source...
Phases An and Cn no longer are 120 degrees out because
On primary side , voltages across windings A and C are now in phase not out by 120 degrees, because the neutral is missing so can't pull their midpoint over to center of phasor triangle.
They are just in series .
So each sees half Vac, or 0.5 unit. No problem yet, for 0.5 is less than 1/√3
BUT
On secondary side, phase B is connected between A and C.
So phase B secondary winding sees (Vac/2 +Vac/2) X turns ratio,
or (0.5unit + 0.5 unit ) = 1 unit X turns ratio
and that is more than 1/√3unit X turns ratio.
So phase B secondary winding sees 1 whole unit X turns ratio, not 1/√3 unit X turns ratio.
That's a 15% overvoltage.
That increased phase B secondary winding voltage will backfeed to the primary winding.
And it might saturate the transformer you just disconnected ... Did it hum ?
What damage did you observe? Overvoltage arrestors actuating? Phase B transformer overheating? Phase AC secondary voltage too high?
I'd look for an open in the neutral wire that connects those transformer primaries back to the next transformer or bus upstream.
I guess i'd summarize this so:
Draw two unit vectors emanating from a common point at 120 degrees to each other.
What is distance between their outboard ends?
Now rotate them so they align.
Their ends moved further apart by ratio 2/√3. That's 15% more distance.
So --- will your phase AC voltage, if you disconnect phase B with an open present( but not noticed because things were balanced ) in the neutral wire somewhere back on the line, not increase by 15% ?
If neutral current is returning via earth, you'll get overvoltage less than 15%.
But - this is just a thought experiment from probably a long distance away.
Probably it's something else . It's very late here and i probably made a mistake - catch you in the morning..
old jim
ok sir, thank you we will take your advice in consideration...
Good luck guys !
That was my best guess as to "probable cause".
I saw something similar once when we [STRIKE]opened[/STRIKE] disconnected the neutral wire to a voltage regulator and didn't know a phase fuseholder was open.
This is the sort of thing one really learns from.
Let us know here what you find ?
one last thought:
Are primary side transformer neutrals perhaps intentionally not connected to the high side(primary)distribution system neutral?
Sometimes with a small wye-delta transformer bank it is necessary to NOT make that connection, in order to prevent third harmonics from circulating around the delta secondary .
[A small transformer bank driven by a much bigger one in four wire wye-wye-delta can try to absorb all the third harmonic current and overheat. By not tying the small transformer's neutral to the large one's neutral , you block third harmonic current. So, somebody might have wired them that way on purpose.]
I just assumed that "properly" means 'neutrals are connected to one another AND to primary side neutral' .
But you could have meant "connected to each other but not to primary neutral, as designed."
That would explain your symptom.
Won't pester you further. Hope you share your solution.
FAQ: Secondary distribution line overvoltage
What is Secondary Distribution Line Overvoltage?
Secondary distribution line overvoltage is a phenomenon in which the voltage on a secondary distribution line exceeds its normal level. This can occur due to various reasons, such as lightning strikes, switching operations, or equipment failures.
What are the effects of Secondary Distribution Line Overvoltage?
Overvoltages on secondary distribution lines can cause damage to electrical equipment, such as appliances and electronics. It can also lead to power outages and disruptions in the distribution system.
What causes Secondary Distribution Line Overvoltage?
The most common cause of secondary distribution line overvoltage is lightning strikes. However, it can also be caused by switching operations, faults in the distribution system, or equipment failures.
How can Secondary Distribution Line Overvoltage be prevented?
To prevent secondary distribution line overvoltage, proper insulation and grounding of the distribution system is essential. Surge protection devices can also be installed to divert excess voltage away from the system.
What are the safety measures for Secondary Distribution Line Overvoltage?
If you encounter secondary distribution line overvoltage, it is important to stay away from electrical equipment and avoid touching any exposed wires or conductors. Contact your local utility company for assistance and follow any safety instructions they provide.